HT vs LT Motors

01/27/2011 12:37 AM

How is energy being saved in HT (High Tension/Voltage) motors? As we know power consumed by a motor is 1.732 x V x I x power factor. If we reduce the current by employing HT motor then on the same time we are increasing the voltage factor. Thus the product of voltage and current will remain same. Then how energy is being saved in HT motors? Please reply by giving some example or comparison.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: HT vs LT motors

01/27/2011 3:19 AM

The losses in the feeder cables are lower, the lower the current that flows in them, which may be significant for larger loads.

That is why power is transmitted long distances at high voltage and reduced to more manageable voltages at the points of use.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#2

Re: HT vs LT motors

01/27/2011 4:12 AM

Dear Guest, calculate load current for two motors for two terminal voltage (415V and 6.6KV) you will get answer yourself.

1. 10 KW

2. 1000 KW

__________________
When was last time you did something for first time.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: HT vs LT motors

01/27/2011 7:24 AM

Eeerr…. A 1000KW motor is a 1000KW motor, whatever the voltage

415V = 1391A

6.6KV = 87.4A

OK there's the losses to take in to account and additional insulation.

__________________
The reports of my death are greatly exaggerated.
Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#4
In reply to #3

Re: HT vs LT motors

01/27/2011 7:57 AM

Half efforts gives quarter result,....:)

Do the calculation for 10 KW for two voltage.

This remaining half effort would give 3/4 of result.

__________________
When was last time you did something for first time.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #4

Re: HT vs LT motors

01/27/2011 8:09 AM

You've confused me.

10KW @ 6.6KV = .87A

10KW @ 415V = 14A

Same amount of effort going in ? ? ? ? ?

__________________
The reports of my death are greatly exaggerated.
Reply
3
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6

Re: HT vs LT Motors

01/27/2011 10:12 AM

Imagine a motor of 220V with winding resistance R. Use the same amount of copper to make a motor at 440V (with double the turns). The wire cross-section is halved and the length is doubled. So the resistance is 4R. But the current is half, so the voltage drop is only twice and the watts lost at half the current is the same as the 220V motor.

So it is the reduced loss in the feed cables which saves energy. Compare a 115V circuit at 1 amp with a cable giving 2.3 Volts drop, with a 230V circuit carrying 1 amp you get twice the power transferred by the same cable for the same loss in the cable - and you get 99% of the source voltage at the load rather than 98%!

There is another effect when you want a high power motor. If the cable diameter is doubled, there is 4 times the cross section. On might expect 4 times the current, but the surface area was only doubled with copper losses 4 times as much - so the cable gets much hotter. This is bad for losses, because resistance increases with temperature - but a higher insulation temperature is intolerable. Even for open wires on overhead lines, the useful maximum diameter corresponds to about 1000 amp, any higher current and multiple conductors, usually 2 or 4 are used. 1000 amps at 415 volts 3 phase is 719 kW, it is not a surprise that higher voltages are used for motors of that power.

If you think of inside a motor, it is necessary to parallel conductors to use high currents, but this soon leads to an intolerable lead-out wire & terminal problem. It is much more practical to put the copper into more turns using a higher voltage and bring out just one cable - it works out more efficient too because there is less wasted space.

Reply Good Answer (Score 3)
Active Contributor

Join Date: Mar 2009
Location: Vancouver, WA USA
Posts: 14
#8
In reply to #6

Re: HT vs LT Motors

01/28/2011 2:43 PM

In addition, you also have at least one less transformer to go through for HT motors. Each one of these has it's own I^2 R losses.

Reply Score 1 for Good Answer
Anonymous Poster
#7

Re: HT vs LT Motors

01/27/2011 10:28 PM

THIS IS THE ENERGY SAVED IN

.REDUCED I(SQUARE)t loss for the motor and the cables as well,and better efficiency as noload losses are less than 1%in HT motors and in LT motor this is around 4%.

Reply
Active Contributor

Join Date: Dec 2010
Location: Brasil
Posts: 21
#9

Re: HT vs LT Motors

01/29/2011 9:06 AM

Power is power anywhere. The energy loss reduction is % small, but installation and maintanace cost will be significantly different. It is possible that for certain particular instalation the cost will be the same for both sollutions.

For HT equipment and cables are of low corrent capacity but need special cares on insulation and safety.

For LT instalation is simplified, but you will need equipment and cables for high current levels, wich afects safety to.

You have to consider the overall facility needs. Consider energy availability, room space for transformers, cables, safety, manuover possibilitys, and so on.

Reply
Guru

Join Date: Jun 2006
Posts: 501
Good Answers: 8
#10

Re: HT vs LT Motors

01/29/2011 8:52 PM

While higher voltage permits you to use smaller conductors for the same output power, there are other losses that come into play. Higher voltages in AC circuits in crease losses though induction and capacitance.

So you may actually (will?)pay for more kW!

Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#11

Re: HT vs LT Motors

01/30/2011 7:14 AM

Dear Guest,

For the given Power if the Voltage is high means the Current will be low, as it is inversely proportional. Therefore the I^2xR Lossess will come down, hence the heating effect on the winding will come down.

For Example for 1000 kVA set, for 420 Volts, the Current will be 1099 Amps, and if the Voltage is 11000, the current will be 41.96 Amps. You can calculate the I^2xR Loss.

Further, the Cross Section of the winding of Alternator will come down, hence the size of the Alternator will come down. But the Insulation has to be taken care for 11000 Volts.

DHAYANANDHAN.S., INDIA.

Reply
Participant

Join Date: May 2015
Posts: 1
#12

Re: HT vs LT Motors

05/05/2015 5:40 AM

Yes , I agree with KalbBR, there will be more initial investment is required for High Voltage installation. Let me know still there will be saving by using higher voltage Motor/ DG set( 11kV) compare to 415V.

Reply
Reply to Forum Thread 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Anonymous Poster (1); dhayanandhan (1); Happy singh (2); jmart23 (1); KalbBR (1); MLHemmer (1); P-rama (1); PWSlack (1); TonyS (2)

Previous in Forum: Difference Between Tong Tester & Clamp On Meter?   Next in Forum: 415V DG & 11kV DG Differences
You might be interested in: DC Motors, Stepper Motors, AC Motors

Advertisement