Anonymous Poster

Calculating Pipeline Sizes

03/30/2007 1:56 AM

hi

Can you all help for a simple formula to calculate the size of pipe lines for chilled water lines and boiler lines

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Mar 2007
Location: Turkiye
Posts: 2
#1

Re: pipline calculation

03/30/2007 4:45 AM

Boilers and boiler pipeline selection, calculation ! Nice Coice..

Reply
Participant

Join Date: Mar 2007
Posts: 1
#2

Re: pipline calculation

03/30/2007 5:54 AM

The pressure requirement is 4kg/cm2 the distribution is around 500 mts

Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#3

Re: Calculating Pipeline Sizes

03/31/2007 10:26 AM

Please STATE your 2 problems precisely and separately.

You will then expect meaningful replies.

Only then!

Reply
Anonymous Poster
#4

Re: Calculating Pipeline Sizes

03/31/2007 4:11 PM

YOU CAN GET A FREE PIPE SIZER PROGRAM DOWNLOAD ON LINE, OR CONTACT SARCO FOR A COMPLETE SET OF DETAILS CHARTS AND DIAGRAMS. USUALLY I WILL SIZE FOR A 5.2 TO 5.4 FEET PER SECOND FLOW RATE. AT POINT OF ZPD YOU SHOULD BE BELOW 2.25 FPS TO ALOW FOR AIR SEPARATION AND IN THE REST OF THE SYSTEM YOU NEED TO STAY ABOVE 4.75 FPS TO MOVE THE AIR OR GASSES BACK TO THE SEPARATOR. CONTROL AND MIXING VALVES SHOULD BE SIZED FOR A 2-3 PSI PD, YOU CANE GO TO THE KELE WEB SIGHT AND USE THE VALVE WIZARD TO CALCULATE CV AND SIZE THE VALVES. THIS SHOULD PROVIDE THE MOST SATISFACTORY PERFORMANCE WITH THE LEAST PUMP POWER CONSUMPTION AND ELINATE NOISE. I USUALLY START WITH THE FLOW RATES AND PD ON THE CHILLED WATR ON 2 PIPE SYSTEMS. 4 PIPE WILL REQUIRE SEPARATE CALCULATIONS ON BOTH. I LIKE TO RUN A SEPARATE PUMP AND MIXING VALVE ON CHILLED WATER COILS. WITH SIMPLE PID CALCULATIONS BASED ON DEW POINT, YOU CAN GET THE MOST DEHUMIFICATION AT THE LOWEST COST BY MOVING THE WATER THROUGHT THE COIL FAST ENOUGH TO STAY BELOW DEW POINT ALLTHE WAY THROUGH THE COIL RATHER THAN LOWERING THEWATER TEMPERATURE LEAVING YOUR CHILLER WHICH WOULD SERVE TO LOWER YOUR CAPACITY AND RAISE YOU POWER CONSUMPTION. ( LOWER RH- HIGHER COMFORTABLE TEMPERATURE SETPOINT.

Reply
Anonymous Poster
#5
In reply to #4

Re: Calculating Pipeline Sizes

04/02/2007 3:08 AM

can I have the site address were i can down load the program

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Calculating Pipeline Sizes

04/02/2007 5:39 AM

It's a simple calculation.

As a rule-of-thumb, keep the velocity between 1 and 3m/s for liquids.

One can go a bit higher for gases.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#7

Re: Calculating Pipeline Sizes

04/18/2007 8:31 AM

Pipe sizing: water/air/gas

Q = 3.142/4 x A2 x V x 3600/1000000

Q = m3/h

A = mm pipe dia

V = velocity : water 1- 10 kg/cm2 : 1.5 - 3 m/s

air 1- 2 kg/cm2 : 8 - 15 m/s

200-300 kg/cm2 : 5 - 7 m/s

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Reply
Anonymous Poster
#10
In reply to #7

Re: Calculating Pipeline Sizes

03/15/2009 6:47 AM

Please elaborate the formula?

Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#11
In reply to #10

Re: Calculating Pipeline Sizes

03/15/2009 3:27 PM

For water capacity m3/hr pipeline sizing at various velocities 1.5 m/s thru 3.0 m/s based on formula:

water flow m3/hr for pipe size 15mm:

velocity m/s: say 1.5. 15mm = 225 area =

3.142 x 225 x 1.5 x 3600

------------------------ = 0.95 m3/hr

4 x 1000000

velocity m/s: say 3.0 15mm = 225 area =

3.142 x 225 x 3 x 3600

------------------------ = 1.9 m3/hr

4 x 1000000

water flow pipe size 100mm:

velocity m/s: say 1.5. 100mm = 10000 area =

3.142 x 10000 x 1.5 x 3600

------------------------ = 42.4 m3/hr

4 x 1000000

velocity m/s: say 3.0 100mm = 10000 area =

3.142 x 10000 x 3 x 3600

------------------------ = 84.8 m3/hr

4 x 1000000

you can now workout for any pipe size depending what velocity you want to keep.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#13
In reply to #11

Re: Calculating Pipeline Sizes

03/15/2009 3:39 PM

Keeping everything constant change velocity stated for air and gas and the same formula indicates the m3/hr compressed air flow and natural gas flow via pipe selected.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Reply
Anonymous Poster
#8

Re: Calculating Pipeline Sizes

06/01/2007 10:17 AM

please let me know what will be max flow in m3/hr for thermic fluid for a pipe line size of 250 mm dia

Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#9
In reply to #8

Re: Calculating Pipeline Sizes

06/01/2007 11:47 AM

You can circulate up to 5,000 cubic metres in one hour.

mm

Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#12
In reply to #8

Re: Calculating Pipeline Sizes

03/15/2009 3:35 PM

Please intimate MKcal output of thermic oil fluid.

Is it from one boiler? or a set of boilers like: 5.0 Mkcal x 3 nos

a 250mm pipe is good enough for 15 MKcal at reasonable pressure drop within limits.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson