Do I Add High Point Vent

01/31/2011 10:10 AM

What I was wondering what were the rules or needs for placing a vent on a 150# steam and condensate piping system if the location would be a high point, in a vertical loop. If the normal high point vent is used there (just a tap off of the line with a valve).

Thanks alot,

Designer

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Do I Add High Point Vent

01/31/2011 10:29 AM

If the valve is easily reached, then someone can operate it during start-up to let the air out of the main. If it is not reachable or if start-ups are frequent, then adding an automatic air vent might prove worthwhile; it can always be screwed onto the valve and then the valve left open.

If the steam user points are properly trapped, then the air, the "incondensibles", will come out of the auto vent valve downstream of the user point, in which case adding auto vents to the main steam line might not be necessary.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 3)
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#2
In reply to #1

Re: Do I Add High Point Vent

02/01/2011 7:27 PM

GA, nothing to add.

Register to Reply
Member

Join Date: Jan 2011
Posts: 5
#3
In reply to #2

Re: Do I Add High Point Vent

02/02/2011 6:53 AM

Hi,

We don't even need these to hydro the system?

Is it that any air in the system would not be harmful in a steam system, so there is not need for vents, or that the air is expected to be removed at the vent connection on the trap? The system is routed to drain correctly, to traps.

Is there something that you use to judge whether or not to add vents to a steam system, or always just to not do it, maybe a temperature? Some guide that you may use.

Thanks so much for your help (great looking dog you have there),

Designer

Register to Reply Off Topic (Score 5)
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#4
In reply to #3

Re: Do I Add High Point Vent

02/02/2011 10:30 AM

Thanks for the comment about the puppy.

Any air in a steam or a hot water system is plain bad news. Air has oxygen and that is very bad, not to mention vapour locks and other odd things.

I would always install manual vents at any high point and condensate traps at the low point or with long runs.

Water and air are killers of a good steam system.

It never hurts to cover all the bases

Register to Reply Off Topic (Score 5)
Member

Join Date: Jan 2011
Posts: 5
#5
In reply to #4

Re: Do I Add High Point Vent

02/02/2011 12:28 PM

Icarus,

Thanks so much. Really didn't know for sure.

What does GA stand for, not a text person.

Thanks again,

Designer

Register to Reply Off Topic (Score 5)
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#7
In reply to #5

Re: Do I Add High Point Vent

02/08/2011 6:12 PM

It means a good answer

Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#6

Re: Do I Add High Point Vent

02/07/2011 11:32 PM

All end of steam mains to be installed with an automatic air vent which is a bi-metallic/thermostatic version (AV 20 or similar, size 15mm of Spirax) . All Hot/Condensate mains to be installed with automatic air eliminator which is ball float type( AE 14, size 1/2" or similar). Please refer web site of Spirax Sarco.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Member

Join Date: Jan 2011
Posts: 5
#9
In reply to #6

Re: Do I Add High Point Vent

02/09/2011 7:03 AM

DUCON,

Thanks for the great advice and help.

Designer

Register to Reply
Guru
Engineering Fields - Piping Design Engineering - Retired Piper

Join Date: Feb 2007
Location: Bayonet Point, Florida
Posts: 635
Good Answers: 61
#8

Re: Do I Add High Point Vent

02/08/2011 7:22 PM

From another but related question.

High Point Vents and Low Point Drains

The question:

"High point vents and low point drains, what they are? Why do we have them?

My answer:

These are both very good questions. So let's us take a look at some answers to these questions.

First you might ask if there are there other types of vents. Yes, there are other types of vents. And by association there are also other types of drains besides the Low Point Drain. There are the Process vents and there are the Process drains. The process vent and process drain is provided for multiple usages during the proper active operation for which the plant was designed.

Every plant that is built with piping systems must insure that the piping systems are properly fabricated, installed and safe. Some of these systems may have very hot or very cold or hazardous or toxic chemicals in them. These types of commodities can kill, maim or seriously injure the operators working in one of these plants or the people living around these plants.

In order to insure that a piping system is secure, the system must be tested and properly prepared prior to start-up. The method used for this testing is to fill the system with water and then apply pressure. This is called "Hydro-testing." Hydro-testing can be done with other types of fluids but water is the normal choice. The water, under pressure will seek and find weak points in the piping system and then squirt out. Water under pressure is not as dangerous as a normal commodity such as high pressure steam or sulfuric acid. Some systems only need to be tested for tightness. Others must be tested then because the water is not compatible with the process, it must be flushed with a solvent or other cleaning agent to remove the water. For this Hydro-test to be done and be affective the system must be absolutely and completely full of water (or other fluid).

In order to completely fill a piping system you must be able to get all the air out of the pipes. The air will naturally accumulate in the high points of the system. Thus we install "high point vents" to be able to get rid of the air. Once the test is completed we must be able to get rid of or drain out all the water. The water naturally gravitates down to the low points of the system. So we install "low point drains."

Hydro-test vents and drains are normally ¾" or 1" in size. Most of these vents and drains are only used when the plant is first built or when a system is modified and must be retested. These vents and drains do not always require valves. Some plants only install temporary valves for use during the testing process. After the test the valve is removed and a plug is installed. These Plugs are then "Seal-Welded" to prevent leaks. Other plants may use some selected hydro-test vents or drains as process start-up vents or drains so the valves installed in these and are retained. Still other plants require that all hydro-test valves be permanently installed and plugged (with no "Seal-welding").

In conclusion, high point vents and low point drains are a small but important and necessary detail of the piping system in a process plant.

__________________
Do it once and do it right
Register to Reply
Member

Join Date: Jan 2011
Posts: 5
#10
In reply to #8

Re: Do I Add High Point Vent

02/09/2011 7:06 AM

PennPiper,

Thanks so very much for the great reply. A really detailed and thoughtful answer to the reasoning for vents & drains.

Thanks,

Designer

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Designer (4); ducon (1); Icarus (3); PennPiper (1); PWSlack (1)