power cable

02/03/2011 9:42 AM

10 motor of 10kw 7 motor of 15kw distance of 320meter now tell me what the size of cable plz send me formula of this

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: power cable

02/03/2011 1:38 PM

There is no one real formula of this. See the gazillions of CR4 threads on cable sizing.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: power cable

02/04/2011 12:36 PM

British Standard 7671 again.

Contact the British Standards Institution. There's so many copies of BS7671 there that there's a sales drive on just to get rid of them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#3

Re: power cable

02/17/2011 9:49 AM

It seems complicated, however, I might just put it together for you :)

Load of 10 motors of 10KW each = 100KW

Load of 7 motors of 15KW each = 105KW

---------------------------------------

Total Load (not including any safety factor) = 205KW

Total Length = 320 meters

Assuming voltage drop allowed = 2.5%

Max. acceptable voltage drop (Vd) = 2.5% (415) = 10.375v

I = (205 X 1000)/(1.73 X 415 X 0.8) = 356.7A

Using the following formula:

Formula Vd = mV x I x L or mV = Vd x 1000

1000 I x L

where Vd = maximum acceptable volt drop (in volts)

I = current per phase (in amps)

mV = appropriate volt drop (in mV/amp/metre)

L = route length (in metres)

Once you come up with mV figure, then look up for the manufacturer list of four core

xlpe cable.

After studying the table to find a voltage drop value equal to, or less than the calculated one above. Then you could select the cable size in the same row in the table....

Your breaker size would be of 630A MCCB, depending on the sizing. Hoping that would help ya :)