Anonymous Poster

Exhaust Fan

02/15/2011 9:10 PM

hi, I have received a task,for calculating of an exhaust fan for a hall 122*52*26ft volume. It is just for sucking dust/particles.can you help me in this regard pl. Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Exhaust Fan

02/15/2011 9:41 PM

Do you have a clue of what your doing?

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster
#17
In reply to #1

Re: Exhaust Fan

02/22/2011 11:19 AM

You, good man, are an A$$HOLE.

Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Exhaust Fan

02/15/2011 10:29 PM

Exhaust fan calculations may be based on:
Room volume (ft3)
Room area (ft2)
Room occupancy (number of people)
Various heat loads in the room
Local code eccentricities
Contract specifications, whether rational or not
and maybe some other stuff.

More info needed.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Exhaust Fan

02/15/2011 10:48 PM

You need a BFEF.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Exhaust Fan

02/15/2011 10:55 PM

Acronym alert!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#5

Re: Exhaust Fan

02/15/2011 11:37 PM

These are the questions you need to answer first,

1) What is the typical application of that exhaust fan. Is it for clean room, (ICU)hospital or other industrial application?

2) What is the concentration of dust in the room, is it ventilated (if so what is the concentration of dust from the source air (ambient,perhaps), by how much is ambient air is being brought inside(cross section of diffuser x air velocity). Know the sources of dust. (OSHA has methods for knowing the concentration, TND or TD) you can use the data

3) Typically for just dust removal, you have to consider only a recirculating system.

This will be your working equation:

Rate of removal => Rate of dust infiltration

then you can design a Filter system using HEPA Filter, its not an air exhaust system, take note. It is because the exhausted air from these filters are already cleaned from dust particles. (See Hepa Filter specification, google it)

or you can just buy something like these (HEPA FILTER)

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#6

Re: Exhaust Fan

02/16/2011 10:43 PM

How long is a piece of string.

How many times do you need the room volume in air removed , say, per hour.

Are you restricted in the placement of fans.

Is there any forced inwards airflow.

Is the room sealed.

Do you have a piece of string.

Do you have noise restrictions, internal and external.

Get a piece of string measure it, and give us some "Criteria". All of it...!

Thick string or thin string.

Then someone maybe someone will help you.

Me personally...I don't think you have a clue, do you.

Tyre kickers, sort of interested, but not really.

Sorry to be blunt, but.........!

Cheers Mark N.

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Reply Score 1 for Off Topic
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#7
In reply to #6

Re: Exhaust Fan

02/16/2011 10:46 PM

Try this.!

http://www.engineeringtoolbox.com/fan-types-d_142.html

Mark N.

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#8

Re: Exhaust Fan

02/17/2011 4:19 AM

Minimum data required is Number of air changes and sources of heat . Multiple the volume of the room by number of air changes per hour will give you the quantity of air to be exhausted. From the standards fan literature you can select the exhaust fan.

Reply
Anonymous Poster
#9
In reply to #8

Re: Exhaust Fan

02/17/2011 8:24 AM

This answer should suffice.I would say that we are all professionals and should not discourage/ confuse the professional.

As he said, it is for sucking dust particles, the right approach will be to tell us everything you know about these particles. are they heavy or if you can quantify them.

This will help you in finding optimum number of air changes required to remove them. And if possible any process which produces these particulates.

Even if you know the process taking place there. rules of thumbs can then be told to calculate CFM to be exhausted.

Call me/ E-mail with more details to help you further.--Esskay11@live.com

Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#10

Re: Exhaust Fan

02/17/2011 9:55 AM

The typical resident genius (in their minds only) heckling should be ignored. It would help if you gave a bit more info on what type "dust" you're talking about. I'd hold back on any Hepa system. That was a really stupid reply unless the dust you're exhausting has to be treated to meet some code or emission requirement. You need to know that. Hepa filters are quite costly for "dust". The suggestions you got for "air changes per hour" are valid. So how many time an hour or day do you expect to completely change the volume of air in the room? You have to have an idea before you can size a fan. Theres an old rule in HVAC that gets forgotten all the time. It goes like this, "you can't take it out if you don't put it in first". Which means you have to make sure you have a source of "new air" to replace the air you're removing. So it's really important to know if this hall is a conditioned space? It's wasteful to condition air and then exhaust it. If the hall isn't critical you might want to take in outside air or a combination of outside and conditioned. You're probably able to set up a fan but you really might want to consult with an HVAC person to not only get the airflow you want but to do it without setting up a system thats pumping dollars through the roof. Good luck.

Reply Score 1 for Off Topic
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #10

Re: Exhaust Fan

02/17/2011 10:04 AM

Fredski,

Given your track record, I think it's really overbearing of you to refer to anyone's replies as stupid. "That was a really stupid reply unless the dust you're exhausting has to be treated to meet some code or emission requirement."

I'll take any response from Noudge79 over yours any day.

I think you should sit on your hands and observe for a while longer, cause you aren't getting off to a good start here.

Cheers, good buddy.

Reply Good Answer (Score 2)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#12
In reply to #11

Re: Exhaust Fan

02/17/2011 10:27 AM

Still with the condescending remarks. Does that actually work for you? Seriously do you expect bloggers to be subordinate to you? You're a slow learner if you think I'll listen to anything you say. And it IS a stupid remark. I'm a long time HVAC contractor is So Calif. I know exactly what I'm talking about on this topic. If the guy is located in certain air districts he might be required to treat his exhaust, but again it depends on what type of "dust" he plans to exhaust. If it's inert it would be extremely costly to install a Hepa system that doesn't even require filtration in the first place. Which is more than stupid, but if you need to install an exhaust system please feel free to install a few powered Hepa's to vent your bathroom or kitchen.

Reply Score 1 for Off Topic
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#14
In reply to #10

Re: Exhaust Fan

02/17/2011 11:28 PM

It is amazing..............!

Our mate "Guest" who has asked the question, as not entered further into the debate.

I doubt he is really interested in the correct answer, as he really hasn't defined his question, after 2 days, hasn't bothered to help himself, with more information.

We are left guessing whether his string is of Natural Fibre or Synthetic. If someone presumes to give an answer, to the ill defined question, chances are it will be in Error.

No answer in this situation is "Dumb".

If we are to converse amongst ourselves, with no more input from "Guest", then we are all dumb, for trying to second guess this bloke.

I reckon, by now, he has swapped his battered bucket, for some kids bright new bucket, picked up his spade, and is now playing in the rich kids sandpit at the end of the street.

I mean, should we have bothered in the first place.??????

Those who help themselves, WILL get help from others.

Cheers and Good Health.

Mark N

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#15
In reply to #14

Re: Exhaust Fan

02/18/2011 3:38 AM

"It is amazing..............!

Our mate "Guest" who has asked the question, as not entered further into the debate."

This is actually rather common; and annoying.

Reply
Anonymous Poster
#13

Re: Exhaust Fan

02/17/2011 9:45 PM

You should first ask your Instructor to be more specific about your →Home Work Assignments

Reply
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#16
In reply to #13

Re: Exhaust Fan

02/18/2011 3:45 AM

Yes. Possibly Right.

Couldn't see the student for the teachers.

Mark N.

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Reply
Reply to Forum Thread 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); Fredski (2); lyn (3); Markone (4); mrswamy (1); Noudge79 (1); TonyS (1); Tornado (2)

Previous in Forum: Bearing Lubrication   Next in Forum: Beraing temperatures.

Advertisement