Anonymous Poster

DG Maximum Output Power

02/16/2011 12:07 AM

Help : How do I calculate the DG maximum output power interms of KVA /KW .

and how much safe load be put on DG .

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: DG Maximum Output Power

02/16/2011 12:14 AM

One does not generally calculate this; instead, one looks it up on the DG nameplate, or on its data sheet. In many if not most cases, kva and kw are both given. Often kw = 0.80 x kva. If the engine rating is in hp, kw = 0.746 x hp (minus some small drive losses).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: Anil Prakash Sharma

02/16/2011 7:24 AM

I believe the British Standard allows 110% of the continuous rating for 1 hour in each 12 running hours. Note this is for a new engine - also the overload will increase wear at more than 110% - worse on engine already working hard (turbocharged). Also you have to deduct the generator losses from the engine shaft power to get output kW - generator efficiency varies about 70 to 95% from, say, 2 kVA to 500 kVA.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: Anil Prakash Sharma

02/16/2011 11:16 AM

Please explain. If 110% is the new 100% then 100% is still the maximum output.

"Confused" of Dodman's lane.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #4

Re: Anil Prakash Sharma

02/17/2011 6:19 AM

Dear PWS,

The question wrote "maximum" and "safe" not "continuous" (or efficient or economic).

The British Standard can happily allow 10% overload for 1 hour because on a diesel rating it just uses up life (compare the power of a 2 litre petrol car engine with a diesel of 2 litres - same poppet valves etc but much higher exhaust temperature with petrol). N.B. a [direct injection] diesel only typically burns 70% of the oxygen it sucks in - the limitation is incomplete combustion and exhaust smoke - but it is easy to increase the fuel! The AC generator cannot be overloaded much because the engine limits at 110% - in any case they are usually made to class B temperature rise (120 'C max) but have class F insulation (140 'C max). As for BS7671, it is mostly about cables - fuses/CBs have about +/- 10% tolerance on the fusing current for a given time - and the famous BS1363 plug with earth pin, fuse and shutters uses a BS1362 fuse specified to blow in not more than 1 hour at 160% rated continuous current.

Regards,

67model.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Anil Prakash Sharma

02/17/2011 6:20 PM

Which standard, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8
In reply to #7

Re: Anil Prakash Sharma

02/18/2011 8:09 AM

Ancient history BS 649, as far as I remember. Replaced by BS ISO 8528 no doubt!

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #2

Re: Anil Prakash Sharma

02/16/2011 11:46 AM

Shouldn't the circuit protective device(s) operate in the event of an overload, so as to protect both the unit and its internal/external wiring [British Standard 7671]?

Or are these "frigged out" with jumper wires and matchsticks?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: DG Maximum Output Power

02/16/2011 8:19 AM

Just go by the manufactures data, that way you won't invalidate any guarantee. To deliberately over load a machine is shear folly!

__________________
The reports of my death are greatly exaggerated.
Reply
Reply to Forum Thread 8 comments