ACDB/ DCDB

02/20/2011 10:33 PM

Is there any difference in the testing methodology for ACDB & DCDB?

(Means testing for ACDB is different from that of DCDB?)

__________________
Anand Kathale
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: ACDB/ DCDB

02/20/2011 10:48 PM

How about applying AC to the former, and DC to the latter? Elephino.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: ACDB/ DCDB

02/20/2011 10:52 PM

Can you please explain what an ACDB and DCDB are first.

__________________
jack of all trades
Register to Reply
Active Contributor

Join Date: Dec 2010
Posts: 15
#3
In reply to #2

Re: ACDB/ DCDB

02/20/2011 10:55 PM

Its distribution boards for Ac & DC system....

(Including Bus bars, meters, relays etc.)

__________________
Anand Kathale
Register to Reply
Member

Join Date: Feb 2011
Posts: 6
#4

Re: ACDB/ DCDB

02/21/2011 8:13 AM

ACDB - AC Distribution Board; DCDB - DC Distribution board.

They are LT basically panels meant to supply the required supply(AC or DC) for the local accessories and auxiliaries. The testing procedure of the two is the same. The only difference may be in the testing of its individual components (like ammeter, voltmeter, MFM, etc.) since the types of meters used might be different for AC and DC.

The basic insulation test, which is done on any panel (3KV test for 10 mins) is common to both of them.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: ACDB/ DCDB

02/21/2011 9:28 AM

Don't they need to be tested as per IEC 60439 in IEC countries and as per NEMA in US ? A conditional short-circuit test is involved i think?

As the OP seems to be from India, i must point out that there may be difficulty in testing a DC board. Only limited facilities available.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#6

Re: ACDB/ DCDB

02/21/2011 11:18 PM

I guess, you are working in some reputed test laboratory in India? Am I right?