Indicator Lamp in Series With a Switch

02/24/2011 12:07 PM

I have a problem with a 24 volt circuit two wire remote switch circuit for an air handler. The operator keeps leaving the blower on because he cannot see, hear, or feel it working.

So I would like to install a indicator lamp to illuminate when the switch is closed, indicating that the blower is ON.

There are only two wires at the remote location - no common - so the indicator lamp has to be in series with the switch and not create such a voltage drop that the contactor energizing the blower fails to pull in.

What is the best kind of lamp to use: Neon, LED, ?? ?

Thanks

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Register to Reply
Pathfinder Tags: Indicator lamps
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Indicator Lamp in Series With a Switch

02/24/2011 12:23 PM

You can buy toggle switches with a neon indicator built-in to the handle. It glows just based on being excited by the potential across the switch, no common necessary. But it glows when the switch is OFF (open), not when it is On, because the switch essentially shorts across the lamp. You would need your operator to know "If you don't see the light, the fan is on".

You could try "You cannot leave this area until the light comes on telling you it's OK", he/she will figure it out pretty quick.

If you need it to glow when the switch is on, you must have the common for the lamp, LED, Neon or otherwise.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#2

Re: Indicator Lamp in Series With a Switch

02/24/2011 1:31 PM

If you are controlling an air handler, you have a ground.

Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#3

Re: Indicator Lamp in Series With a Switch

02/24/2011 2:23 PM

Trucks run on 24V electrics - and there are plenty with warning lights built into their switches.

__________________
Madness is all in the mind
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #3

Re: Indicator Lamp in Series With a Switch

02/24/2011 3:30 PM

"Trucks run on 24V electrics - and there are plenty with warning lights built into their switches."

That's because they can use the chassis as a common. I forgot this was 24VDC though, so I'm not sure if that's a possibility on a building. I'm not fluent in Low Voltage HVAC control wiring codes. In general though, using ground as a current carrying common conductor is frowned upon.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#9
In reply to #6

Re: Indicator Lamp in Series With a Switch

02/24/2011 3:47 PM

Almost every power supply I use, and this includes AC and DC supplies, ties the chassis of the power supply to the chassis of the cabinet it is mounted in. If you don't, you have a floating ground for the supply. There are instances of this, but I doubt an air handler circuit is such an example. Of those, my indicators are grounded through the bulb housing, or have a ground wire going back to the neg side of the supply (essentially chassis ground). Some are in-line single wire AC or DC bulbs (i.e., neon, led, filament, etc), and those are grounded to the equipment chassis. No ripple and minimally measurable DC current is returned through the chassis of the air handler. I don't see the issue.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#17
In reply to #9

Re: Indicator Lamp in Series With a Switch

02/25/2011 1:46 PM

This would not be a code compliant installation in Canada. No matter what the voltage is, the use of a bonding conductor or bonded chassis for the return of current back to its source, is not permitted. I am quite surprised to hear it is there. This practice is compliant with NFPA 70?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#4

Re: Indicator Lamp in Series With a Switch

02/24/2011 2:46 PM

Sounds like your also going to need a common at the switch area as well in order to run a lamp. They are only breaking the hot lead to the coil. Thus they only use the two wires. One in one out of switch. Neon may show an indication of power flow, but amp draw is so low it may not. Other wise run the common and use LED.

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#5

Re: Indicator Lamp in Series With a Switch

02/24/2011 3:20 PM

Please be aware that the contactor essentially has at least one normal open and one common close auxiliary contacts readily built in by the manufacturer. You just have to use these auxiliary contacts, selection of lamp and voltage source is up to your convenience.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Member

Join Date: Feb 2011
Posts: 5
#7
In reply to #5

Re: Indicator Lamp in Series With a Switch

02/24/2011 3:30 PM

I think he should explore the option of the auxiliary contacts like you suggested. That way the lamp will come on when the coil pulls in and not when the switch changes it's state, and please correct me if I'm wrong but it also removes the chance of an open circuit if the lamp ever fails/burns out while it's in series with the coil.

__________________
The Electrical Nerd
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#8

Re: Indicator Lamp in Series With a Switch

02/24/2011 3:37 PM

Why simply indicate? What if your operator forgets to look at the lamp?

Timer.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#10

Re: Indicator Lamp in Series With a Switch

02/24/2011 3:59 PM

Can you use a timer switch similar to this?

If all else fails, interconnect the air handler switch to a magnetic door lock within the operators' work area, air handler on, no bye bye......problem solved.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Anonymous Poster
#11
In reply to #10

Re: Indicator Lamp in Series With a Switch

02/24/2011 6:56 PM

You will still need to provide a return path for this, as the obvious was pointed out earlier in this thread. Sounds like someone is trying to over-engineer what is a simple solution.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#12

Re: Indicator Lamp in Series With a Switch

02/24/2011 7:05 PM

With just the two wires, you're right - you need a series-connected indicator if you want it ON when the switch is on.

With 24V - forget neons.

Do you know what the load is? Can you give us details? If you could afford to lose a volt or two you could use an LED, but you'd need to put it across a series resistor sized to give the right voltage for the LED with the current drawn by the load.

May be able to find a piezo sounder which can run with a couple of volts (again assuming you can spare it) set up to beep every few seconds. Or a sounder/LED indicator powered by a separate source (battery?) but triggered by current flow. Need to know the current and max. allowable voltage drop, whichever you use.

Then again (he said, thinking "outside the box" God I hate that phrase) - if you used an independent supply for an annunciator, you could rig it to be triggered by the absence of voltage across the switch. No voltage drop when ON, but possibly a teeny bit of current leakage when it's OFF.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#13

Re: Indicator Lamp in Series With a Switch

02/25/2011 1:47 AM

Before putting something in series with the contactor coil, I'd poke around with a voltmeter. I'd be willing to bet that you can find a ground that would be 24V away from the lead going to the switch. An LED and a resistor, and you'd have a light.

Or run a wire back from the contactor?

I just don't like the idea of a series connection: indicator opens, blower doesn't work.

__________________
Think big. Drive small.
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#22
In reply to #13

Re: Indicator Lamp in Series With a Switch

02/25/2011 6:32 PM

"... series connection: indicator opens, blower doesn't work ..." doesn't hold if the majority of the current is being passed by a series resistor, and the indicator is in parallel with the resistor.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#23
In reply to #22

Re: Indicator Lamp in Series With a Switch

02/25/2011 8:13 PM

True.

__________________
Think big. Drive small.
Register to Reply
2
Associate

Join Date: Apr 2008
Posts: 31
Good Answers: 1
#14

Re: Indicator Lamp in Series With a Switch

02/25/2011 8:34 AM

The simplest would be a 1K resistor and and LED across the switch. Switch is open (Air handler off) light is on. Switch is on, (air handler on) light is off. At 1K and 24 volts, current approximately 24 mils. Contactor should pull considerably more. I'd double check the contactor to make sure that 24 ma would not hold it on.

KISS Keep it simple .....

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Apr 2010
Location: Where no man should ever live
Posts: 195
Good Answers: 6
#24
In reply to #14

Re: Indicator Lamp in Series With a Switch

02/26/2011 7:15 AM

Thanks for the numbers, that is what I need - facts I can engineer with.

It would be best to have two lights, one red for not running and one green for running, but it is obvious from the thread that another wire will have to be run for a common.

In this case that is not all that difficult, but it is another job that will take time and materials.

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#15

Re: Indicator Lamp in Series With a Switch

02/25/2011 9:42 AM

Install a 15 minute wind up timer in place of the switch. There is no guarantee if you install 50 lights the operator will still turn it off. With the timer no matter what it will not run more than 15 minutes. Problem solved and no light to ever change.

Register to Reply
Anonymous Poster
#16

Re: Indicator Lamp in Series With a Switch

02/25/2011 12:52 PM

Have you tried just the LED in series with the switch? Voltage drop depends on the type of LED used when forward biased - .6V for Silicon; .2V for Germanium; (?) for whatever the Zener voltage happens to be. I would also need to know how much current needs to go through the switch, which can be measured with an multimeter. The neon bulb has some resistance, and a forward-biased diode should present a short-circuit. I hope this helps.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#20
In reply to #16

Re: Indicator Lamp in Series With a Switch

02/25/2011 4:31 PM

"Voltage drop depends on the type of LED used when forward biased - .6V for Silicon; .2V for Germanium;[1] (?) for whatever the Zener voltage happens to be[2]. I would also need to know how much current needs to go through the switch, which can be measured with an multimeter[3]. The neon bulb has some resistance[4], and a forward-biased diode should present a short-circuit[2]."

[1] LED forward voltage is higher than either of your examples (which are about right for small-signal diodes). LEDs have a voltage drop of between about 1 and 5 volts, depending on the type (colour).

[2] Zener voltage does not come into it. LEDs are used forward biased (anode to +ve, cathode to -ve). Zener breakdown occurs the other way round.

[3] Enough current to pull in a contactor would destroy most indicator LEDs.

[4] Even so-called low voltage neons need about 70V to strike, and only pass a few milliamps. The control circuit here is 24V.

Sorry, but I felt this had to be said. I have marked this off topic.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 2 for Off Topic
Power-User

Join Date: Apr 2010
Location: Where no man should ever live
Posts: 195
Good Answers: 6
#25
In reply to #20

Re: Indicator Lamp in Series With a Switch

02/26/2011 7:27 AM

Thanks for straightening out the differences between LED's and neon lights by quantifying the differences. I guess I had started to think there was a light bulb that would emit light without consuming energy (have a voltage drop - right?).

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#26
In reply to #25

Re: Indicator Lamp in Series With a Switch

02/26/2011 7:41 AM

"... a light bulb that would emit light without consuming energy (have a voltage drop - right?)" - right.

You don't get owt for nowt, as they say in some parts of Britland where no man should ever live !

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#18

Re: Indicator Lamp in Series With a Switch

02/25/2011 3:29 PM

Hi, not sure what voltage you control circuit is operating on, but I would suggest that you have an indicator wired across the switch the glows when the blower is off, when the blower is on the lamp goes off.

IE instead of having indication that the blower is operating, have indication that the blower is off.

Cheers

Joe

Register to Reply
Anonymous Poster
#19
In reply to #18

Re: Indicator Lamp in Series With a Switch

02/25/2011 4:08 PM

Guest #16 added note: The voltage drop over an actual LED is usually lower depending on the color. You can also try an R/S Latch with the LED to indicate when the system is on or off. I don't work for Radio Shack, but you might want to buy the Electronics Learning Lab they sell for the Truth Table and circuits.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#21

Re: Indicator Lamp in Series With a Switch

02/25/2011 6:21 PM

Coldspot has not told us if the 24 volt is DC or AC. If it is AC, a current transformer could supply a lamp.....

Register to Reply
Anonymous Poster
#27

Re: Indicator Lamp in Series With a Switch

02/26/2011 10:53 AM

OK here is a sugestion that I have used with sucess.

Assuming that your 24V operates a relay that activates the air handler.

The control relay will probably require ~20 mA to activate (close the contact to the air handler) Also, this is probably 24 V AC. So what I have done is put a couple of 10mA LEDs back to back in series with the 24V control switch. The back to back LEDs will conduct on both halves of the AC and prevent the relay from chattering. I also put a low value resistor in parallel with the LEDs. The resistor (if used, will provide just enough current to close the relay in the event of an LED failure. This will cause the LEDs to light when the switch is closed. The circuit will cause ~ 3 Volt drop in voltage but not enough to cause the relay to malfunction. You may have to adjust the resistor value depending on the current for the LEDs that you select. Also, you may want to put a capacitor (.01 uF) across the switch if the control wires are long. Long wires will have enough inductance to cause a voltage spike, when the switch is activated, which could cause damage to the LEDs.

Register to Reply
Register to Reply 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Anonymous Poster (3); Coldspot (2); cuba_pete (2); Doorman (1); fixitorelse (1); Fredski (1); GM1964 (1); Joe Sparky (1); JohnDG (4); JRaef (2); K_Fry (2); KJK/USA (1); mountk2 (1); North of 60 (1); Satcom-Bill (1); The Electrical Nerd (1)