WEG GTA250MI33 Genset Over Voltage

03/09/2011 10:01 AM

We have a problem with the voltage from a WEG GTA250MI33 / John Deere genset. The load on this machine is made up of a few large electric motors with a combined total power of 138kW. These motors are controlled by a PLC. When the power demand from these motors is below 90kW the genset supplies 230V between any of the three phases and Neutral. This voltage remains tha same even with no load on the machine.

The problem is that when the load is increased, the voltage also rises. The maximum voltage rise was measured at 262.5V. We measured the power factor on this genset and it was 0.52. The fequency from the genset is quite stable at 50Hz and the engine sounds very smooth as it is loaded and unloaded.

We suspect that the problem might be on the AVR, but we have no information about the AVR fitted to this genset. Can anyone maybe tell us where to start looking?

__________________
It is not the crook in modern business that we fear, but the honest man who does not know what he is doing.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: WEG GTA250MI33 genset over voltage

03/09/2011 10:12 AM

Unless someone on CR4 happens to have an operator's manual for this genset, the best place to ask would be WEG and/or John Deere. Provide name, rank and serial number.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: WEG GTA250MI33 genset over voltage

03/09/2011 1:19 PM

Did it work properly in the past? Or is this a new set-up?? Because if you made a wrong polarity CT connection to AVR, you would get the opposite of voltage droop with increasing lagging load (and if you used a CT from the wrong phase, you would get strange behaviour). If the set is isolated from mains and other sets, droop is not essential - you could try shorting out the secondary (AVR side) of the phase CT that biases the voltage signal to the AVR.

Register to Reply
Participant

Join Date: Dec 2010
Location: South Africa
Posts: 4
Good Answers: 1
#3
In reply to #2

Re: WEG GTA250MI33 genset over voltage

03/10/2011 1:09 AM

Unfortunately I do not know if this problem existed in the past. This genset was installed by the owner as a standby unit. When he bought the pelleting plant form us we had to use the generator to power some of our machines because the utility power is limeted to only 250kVa. The problem showed up during the commisionning of our pelleting equipment when we measured the voltage increase and low power factor.

I have been trying to get the WEG agent in that ariea to visit the site and check/repair the problem, but it has been 3 weeks now and NOTHING. He did ask that we bring the complete genset to his workshop where he can run it on a load bank, but the time involved makes that impossable right now, mid season. It is not as if my client is not willing to pay for services and parts.

As the plant is currently running I am at great risk tah the PLC's and other sensative switchgear may burn out. We are allredy experiencing trips on the soft starters and on some GB's.

__________________
It is not the crook in modern business that we fear, but the honest man who does not know what he is doing.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: WEG GTA250MI33 genset over voltage

03/10/2011 1:16 AM

Load banks are much more easily transported than are gensets. The problem might be simpler than that, anyway. I'm surprised at their lack of cooperation, to say nothing of common sense. If they want to play like that, we know a company to avoid; too bad you might be stuck for a while.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.