Transformer Problem

03/11/2011 8:47 AM

Hi to all. I was presented with a problem by a customer who would like to have a balance line to ground voltage. The problem is they source their requirements from a delta-delta connected transformers with the following specifications;

13,2kV-460V/230v

37.5 kVA

The mid point of one transformer is connected to ground and from there you can measure 2 equal secondary and one sqrt 3 higher in line ground voltage and balance 460 in phase to phase.

I was thinking of connecting into the secondary a 3 phase wye-delta, 460v-230v, with the primary neutral grounded to provide for this requirement of a balance 3 phase line to ground and to also source their 230 requirement.

My question is if there are other ways to supply this requirement at the least possible cost to the customer?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Transformer Problem

03/11/2011 9:22 AM

Have you any idea of what you're talking about?

You want a neutral out of a star-delta transformer?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Mar 2011
Posts: 11
#8
In reply to #1

Re: Transformer Problem

03/12/2011 4:46 PM

I cant blame you for your comment but my intention really is to seek experts opinion on the requirement of a customer. On why they require a balance 460/sqrt of 3 line to ground is one thing that had not been cleared sufficiently to me in our discussion.

From what I have gathered it is a requirement of the relays of their water purification facilities to monitor this balance line to ground condition and for that purpose only.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Transformer Problem

03/11/2011 9:31 AM

Why do some customers talk complete boll codswallop <rhetorical question>?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Transformer Problem

03/11/2011 10:03 AM

So you have a "wild-leg delta" configuration on the secondary now (giving you two 230V single-phase connections and the unusable 400V from the opposite phase to ground)? And you would like to take the 460V, 3-phase and feed it into a 460V wye - 230V delta transformer to get a true 230V, 3-phase system for those loads? You should be able to do it. If you are taking all the 230V load off the wild legs and moving it to the new transformer's 230V secondary, you could eliminate that ground connection and then you will be just fine. It probably would still work if you left the ground, but unless you have any single-phase loads there that you can't transfer, you shouldn't need it.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#5
In reply to #3

Re: Transformer Problem

03/11/2011 4:03 PM

I guess I understood his intent differently (although he didn't quite say it this way)--I thought he intended to lift the existing ground at the midpoint of the one leg of the delta and create a new ground for the 460 volt level at the neutral of the wye primary of the new 460V wye - 230V. In concept, I think that can work.

There are probably other factors to consider, including the rating of that new transformer, such that it can carry an appropriate level of ground current (and / or appropriate protective relaying).

If what I described his his intent, another alternative would be a zig-zag transformer, but that could not be used to supply their 230 volt loads.

Register to Reply
Active Contributor

Join Date: Mar 2011
Posts: 11
#7
In reply to #5

Re: Transformer Problem

03/12/2011 4:32 PM

Yes you are correct that it was the way im thinking.

Register to Reply
Active Contributor

Join Date: Mar 2011
Posts: 11
#11
In reply to #3

Re: Transformer Problem

03/12/2011 5:02 PM

thank you

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Transformer Problem

03/11/2011 12:25 PM

You (or somebody) need to list all the loads by both voltage and number of phases, in order to determine what will be cost-effective.

If there needs to be another transformer, it would be delta-star, not star-delta.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Mar 2011
Posts: 11
#9
In reply to #4

Re: Transformer Problem

03/12/2011 4:52 PM

thank you

Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#6

Re: Transformer Problem

03/12/2011 1:56 AM

As the other guys said, by creating a neutral for the low voltage winding won't do any good. Instead a delta-z connection is a connection that self balances, not much but enough when using slightly umbalanced loads (20-30%). Second option, try to balance the loads by using balancing schemes if necessary. the kind of schemes used for arc furnaces maybe, the situation being similar.

__________________
The time is ......now
Register to Reply
Active Contributor

Join Date: Mar 2011
Posts: 11
#10
In reply to #6

Re: Transformer Problem

03/12/2011 4:55 PM

thank you