Anonymous Poster #1

Voltage Between Neutral & Earth

03/25/2011 9:45 PM

I am getting 230 v between neutral and earth in a cummins 35kva generator. is it ok. if not what could be the reason? and what is the remedy. The generator is earthed with an earth pit but at about 100 mts away near the load.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#1

Re: Voltage between neutral & earth

03/26/2011 1:25 AM

#1; maybe one phase is grounded through your load. perry

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Voltage between neutral & earth

03/26/2011 2:24 AM

What voltages are you getting to earth for each of the phases?

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Voltage Between Neutral & Earth

03/26/2011 5:11 PM

Does your generator have a floating neutral or is it bonded directly to the frame of the equipment? It is important to distinguish between the equipment safety ground (bonding) and the electrical system neutral (possibly current carrying).

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4

Re: Voltage Between Neutral & Earth

03/26/2011 6:53 PM

Describe the genset. Is it single or three phase? What are its normal voltages supposed to be? You have not given us enough data for any meaningful answer.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Off Topic (Score 5)
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#5

Re: Voltage Between Neutral & Earth

03/26/2011 11:11 PM

Where is the 230v, at the generator, or 100meters away at the load.....?...?

Your neutral could be open, and showing a reading because of capacitance...!..?

Cheers

Mark N.

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Voltage Between Neutral & Earth

03/27/2011 11:00 AM

Would that be a super-dooper DVM or a cheap-and-nasty moving coil voltmeter? That sort of reading on a DVM may simply be an indication that the neutral is not earthed at the generator and that there is an earth leak somewhere on one of the three phases near the load. Does a filament lamp light when it is connected between neutral and earth <repeat question; previous applicants need not apply......>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#7

Re: Voltage Between Neutral & Earth

03/27/2011 11:56 AM

I do believe that earth and the neutral should only be bonded at the generator. The frame should/could be physically earthed with an earth pit, which is to my mind a really great idea......

I do feel that 100 meters away, that if its showing such a large voltage difference that probably something is wrong. But I am fully prepared to be wrong as well!!

If the loads are fairly evenly distributed (if 3 phase), you should only see a few volts of difference between neutral and earth even 100 meters away......I reckon that you have a wiring or cable fault......

Warning, it could also be dangerous!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#8

Re: Voltage Between Neutral & Earth

03/27/2011 12:09 PM

First: take a 240V lamp and connect between the neutral and Earth to see if it will glow If the blow is visible (or you can check the amps), then you have a fault downstream (i.e. on the load side), between a phase and earth.

The normal methoad is to have the neutral from the generator, grounded to a separate ground, as near as possible to the generator. The grounding of the generator metal body is a separate earthing from the neutral. there should be a protective system that will shut down the alternator if there is a leak from the output phases to the chassis of the genset.

If your case is well understood, you have a missing connection between the neutral point at the genset and the ground, AND you have a possible fault on one of the phases, leaking to a ground link somewhere on the load circuit. The fault could be resistive, or through some device like a transformer or lights circuitry, with one end grounded either by mistake or because of an insulation fault...

Reply
Member

Join Date: Jul 2010
Posts: 5
#9

Re: Voltage Between Neutral & Earth

03/27/2011 12:26 PM

Its dangerous. Have it checkedby an qualifid electrician. Thwere may be leakage.

Reply
Power-User

Join Date: Dec 2010
Posts: 166
Good Answers: 4
#10

Re: Voltage Between Neutral & Earth

03/27/2011 1:22 PM

The generator should be grounded at the generator. This establishes the voltage reference point for the system. The distribution panel(s) should also be grounded at their location. This ensures that the entire system is operating with the same zero-reference. Is the Neutral bonded to the frame of the generator? If not, it should be as this constitutes a "seperately derived system". See article 250.35 of NFPA 70.

Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#11
In reply to #10

Re: Voltage Between Neutral & Earth

03/27/2011 1:43 PM

The Neutral point at the Generator should be grounded and preferably at a separate groung from the generator body's ground. This will allow you to install a tripping device in case of a generator internal fault and prevent a fire or much bigger damage.

Reply
Commentator

Join Date: Jan 2011
Location: Rockhampton Queensland
Posts: 67
Good Answers: 1
#12
In reply to #11

Re: Voltage Between Neutral & Earth

03/27/2011 10:32 PM

As usual, Anonymous is showing their ignorance, or is it arrogance.

This is the last time anyone should try to help an "Anon".

They will/do not even try to help themselves with a simple reply.

Sincerely.

Mark N.

__________________
I dislike "Anonymous" intensely. It is like they have something to hide? Their Cowardice.! I also dislike those Who will not help themselves, by not replying, to a civil Question.
Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#13
In reply to #12

Re: Voltage Between Neutral & Earth

03/28/2011 6:41 AM

Yes

At least he should respond to one of the comments that are trying to help him!

Well, from the start, his entry shows that he is ignorant of the minimum required to be doing anything near a genset, or trouble shooting it.

The best response is either to ignore such OPs, or just send them to get professional help. This particular one seems not interested in the answers he got or unable to understand them...

Reply Score 1 for Good Answer
Participant

Join Date: Dec 2008
Posts: 3
#14
In reply to #13

Re: Voltage Between Neutral & Earth

03/28/2011 10:09 AM

I am sorry gentlemen. I was away and not able to read the great suggestions. I am checking the system for possible ground falult. The system neutral is earthed separately. But I am not sure the condition near the genset. I will get it checked up as well. Thank you for all the help. I will come back and post the identified problem. Regards.

Reply Score 1 for Good Answer
Commentator
United States - Member - Preserve and protect...

Join Date: Nov 2005
Location: First, DO NO HARM!
Posts: 78
Good Answers: 4
#15
In reply to #14

Re: Voltage Between Neutral & Earth

03/28/2011 9:50 PM

GA because you responded.

Our "colleagues" - although knowledgeable and caring - are apparently somewhat short of patience.

Regards,

Gene

__________________
Pessimists are rarely disappointed; optimists are rarely celebrated; pragmatists are neither pessimists nor optimists, and are therefore never wholly right or wrong. -- Anon
Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#16
In reply to #12

Re: Voltage Between Neutral & Earth

04/07/2011 4:18 AM

Mark N, I know that you do not want anyone to help, but there is a reason to help.

He has asked for assistance, in some cultures, it is very embarrassing to respond, that may be the reason for no responce, mind you I have not come across it several times, only ocasionaly, and not on this forum. The preson may be embarrased about the real reason for the fault, dont be to hard on the guy.

Anyway for my uninformed guess as to why you get 230 volts between N + E is because the generator should have its own earth stake and be bonded with the netural, as this is a supply not a sub circuit

Regards

Joe

Reply
Reply to Forum Thread 16 comments

"Almost" Good Answers: