Vent At Higher Point In Piping

04/03/2011 7:57 AM

We did hydrostatic test in CS piping and as per design vent is not required due to service and design at high point. But client wants to install vent at higher point for hydrostatic test purpose and asks for re-hydrostatic test after installing vent.

Is vent required at higher point? If not installed, what will be the issue?

Details: CS. Code : B31.3

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Vent At Higher Point In Piping

04/03/2011 10:53 AM

Without a vent at the top, how do you ensure that the piping is completely full of the hydro test fluid?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#2
In reply to #1

Re: Vent At Higher Point In Piping

04/03/2011 11:47 AM

Maybe this is an attempt to kill two birds with one stone; i.e., pneumatic and hydrostatic tests thrown together as one. ξ

Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#3
In reply to #2

Re: Vent At Higher Point In Piping

04/03/2011 3:28 PM

And, wouldn't that be a pretty good test? Can air leak out easier than water?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Vent At Higher Point In Piping

04/04/2011 1:08 AM

These tests are looking for somewhat different things, and are not really interchangeable.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Nov 2009
Posts: 46
#5

Re: Vent At Higher Point In Piping

04/04/2011 8:30 AM

Good design should always include high point vents, to eliminate any air in the system, remember that air is compressible and if system is under high pressure liquid you could have a serious issue of air building up during the initial filling of the system.

High point vent is to open during filling, when liquid is present you know the system is full and the air is eliminated, but besure it is truly the high point.

Air in the system can cause havoc with instruments, pumps and many other devices.

Get the air out !!!!!!!!!!!!

Register to Reply
Active Contributor

Join Date: Mar 2009
Location: Vancouver, WA USA
Posts: 14
#6
In reply to #5

Re: Vent At Higher Point In Piping

04/04/2011 8:56 AM

And note that there may be more than one high point. Piping configuration may dictate several local high points

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#7

Re: Vent At Higher Point In Piping

04/04/2011 12:17 PM

While all of the previously mentioned "values" of one or more high-point vents are valid- the results of the hydrostatic test is/was not compromised by potential air presence.

Any air would have been compressed to the same pressure as the fluid in the test. Any leak would have caused a loss of pressure. IF you saw no pressure drop- absolutely NONE- then you have a "tight" piping system.

If you saw ANY pressure drop- whether you saw water or not- then your pipes are not sound.

Net effect- Yes, air vents are useful (only if they are capable of holding the test pressure) AND- if they are automatic, you must run a drain pipe from them to a "safe" place because they will ultimately fail and start dumping water. BUT- they are not needed to do a valid hydrostatic test so long as the observation time is adequate and the gauges used are precise enough to verify that there is NO pressure drop.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Posts: 121
Good Answers: 4
#8
In reply to #7

Re: Vent At Higher Point In Piping

04/05/2011 1:40 AM

Air being compressible, it will take more time to raise the pressure. Also, during pressurization, air may find its way through gaskets. Vent is essential to avoid it.

Register to Reply
Associate

Join Date: Mar 2011
Posts: 29
Good Answers: 1
#9

Re: Vent At Higher Point In Piping

04/05/2011 6:28 AM

Please specify application whether this is recirculation of water(like HVAC system) or supply to building onlywith open outlet(like house plumbing)

Register to Reply Score 1 for Off Topic
Associate

Join Date: Nov 2009
Posts: 46
#10
In reply to #9

Re: Vent At Higher Point In Piping

04/05/2011 6:37 AM

your missing the whole thing, house plumbing is normally a closed loop system, air in any liquid system is a problem. If you have done any design/build in industrial or commerical systems you would have not asked such a question.

Register to Reply
3
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#11

Re: Vent At Higher Point In Piping

04/06/2011 8:12 AM

In certain cases as per ASME code, a pneumatic test can be conducted in lieu of hydrostatic, e.g. to avoid freezing of liquid inside your piping system, or hydrostatic test would damage linings or internal insulation, or the little traces of moisture can have a bad affect on process itself, .... etc.

Please refer to Para. 345 "Testing" of ASME B31.3 as clearly indicated at CR4 Thread Hydrostatic Tests, Post #17.

__________________
It is better to be defeated on principles, than to win on lies!
Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#12

Re: Vent At Higher Point In Piping

04/12/2011 4:34 AM

Hydrostatic test is basically a strength test for piping and if it is already conducted successfully as per the provisions of code B31.3, may be with little air pockets, I think retest may not be required. Sometimes retest may be damaging, particularly for gas pipes by enhancing rate of corrosion. Also you may loose water, power and efforts in addition to delay in project without any appreciable gain.

Register to Reply
Associate

Join Date: Nov 2009
Posts: 46
#13

Re: Vent At Higher Point In Piping

04/12/2011 7:10 AM

I can"t believe all the misguided information being stated, If your client wants an high point vent put it in. First mistake was not ensuring all the air is out of a liquid system, when hydo testing lets say you are looking for leaks in the system, how do you find an air leak in any major piping system? you cannot see it but only look at the system pressure dropping, and where do you start looking?

Water will leak and you will be able to see it very easy and find all the leaks specially in a threaded pipe system vs welded.

As I stated before air in a liquid system will only cause problems with instruments, get the air out so you can be certain that when hydro testing you have no high point air pockets that may leak but cant find the leak . case in point, would you like to fill the system with a very strong caustic or acid and then find a leak.

in closing if you do not understand why high point vents are needed why are you involved with the installation and testing?????????? it sound like your unqualified.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#14

Re: Vent At Higher Point In Piping

07/16/2013 10:58 AM

Dear Mr.Shavessels,

The Client is RIGHT.

For any Hydro Static Test, AIR VENT is a MUST, and NO AIR should be allowed to remain inside the Pressure parts to be tested. This is possible only when AIR IS VENTED OUT from the top most point.

If 3 crests are there in the vessel to be tested, the vent also should be 3. In other words, each CREST should have one vent and water should flow out which confirms Air is removed from the vessel to be tested.

If by chance air is remaining inside, it will also under go COMPRESSION which will take more time to reach the Test Pressure. Generally Water is used for Hydro Static Testing which is IN-COMPRESSIBLE, and the VOLUME Reduction is very small, during compression. Air is is HIGHLY COMPRESSIBLE to such an extent of 1/85 of its original volume at Atmospheric Pressure and Temp.

DHAYANANDHAN.S

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: