Anonymous Poster #1

doubt regarding GD2 of motor

04/05/2011 11:13 AM

Why should GD2 of motor be more than GD2 of PUMP + COUPLING? Is it related to starting time and thermal withstand time or is there any other reason.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: doubt regarding GD2 of motor

04/05/2011 11:36 AM

What in the world does anything involving tumors (GD2) have to do with motors and pumps? Please define your acronym.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: doubt regarding GD2 of motor

04/05/2011 12:01 PM

Google has far too many links which can help you..... remember, 'God helps those who help themselves'....(There was an exception though. A bank cashier followed this, and regrettably, ended up at Sing Sing )

To describe the moment of inertia, J and GD2 is used. J is generally called inertia and has the same value of physical moment of inertia in SI units. Unit is in kg·m2.
GD2 (GD squared) is called "flywheel effect" and generally used in industrial application with gravitational systems of units. Unit is in kgf·m2 or kgf·cm2. A relation between J and GD2 is described as:

J = GD2 / 4

Here is one example : GDsquared

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3
In reply to #2

Re: doubt regarding GD2 of motor

04/05/2011 2:03 PM

Actually, I was afraid that the moment of inertia was what the OP was asking about. If it is not obvious that coupling more mass to the shaft of a motor would increase the moment of inertia, then the original question cannot be easily answered.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: doubt regarding GD2 of motor

04/05/2011 10:15 PM

It is not so. Surprisingly, in many cases, the reverse is true (i.e.) GD2 of the driven equipment will be more than the GD2 of the motor.

Reply
Anonymous Poster #1
#5
In reply to #4

Re: doubt regarding GD2 of motor

04/06/2011 7:57 AM

Actually I am facing the same case in which (PUMP + COUPLING)GD2 is more than MOTOR GD2 but i am unable to understand the exact reason behind it. THe only thing that i Have understood is that we want starting time of induction motor to be less than thermal withstand time and i am assuming this to be the reason behind it.Can u please explain the reason for (PUMP + COUPLING)GD2 to be more than MOTOR GD2???/

Reply
3
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: doubt regarding GD2 of motor

04/06/2011 8:21 AM

The acceleration torque to be developed by the motor should be proportional to the toal of the Motor GD2, the pump GD2 & the coupling GD2. It does not matter if the load GD2 is more or less than the motor GD2. What matters is the total GD2 and the required acceleration torque to overcome the inertia due to the total GD2. As long as your motor develops more acceleration torque than what is demanded, why worry comparing load GD2 & motor GD2?

Reply Good Answer (Score 3)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: doubt regarding GD2 of motor

04/06/2011 8:28 AM

Quite right too. Is this not why the IEC classifies relays into 4 grades (Class 10,20,30 and 40) depending on starting time ? High-inertia, long-start applications. Maybe fully laden conveyor belts for example...

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8
In reply to #7

Re: doubt regarding GD2 of motor

04/06/2011 12:02 PM

KVS ! Pl. clarify! Vide Clause 4.7.3 (2) of IEC 60947-4, the trip classes for overload relays are Class 10A, 10, 20 & 30. Is Class 40 included in any latest revision?

Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10
In reply to #4

Re: doubt regarding GD2 of motor

11/29/2014 3:04 AM

Dear Mr.electricalexpert65,

If the GD^2 of the driven equipment will be more than the GD2 of the motor.-, starting of the equipment will be a serious Issue/problem, one such experience I faced - for an equipment called FIBRISOR in a Cane Sugar Plant, driven by 2000 H.P., 11 KV Motor - which had 4% Slip and t The Fibrisor had swing hammers of 18 Kgs. each and the No.of Hammers were 120, total weight 2160 Kgs, Shaft Weight -2000 Kgs., Coupling Weight 650 Kgs.

The starting was not possible, and motor tripped. The problem was solved in starting the motor by 2 steps.

1. 40 Nos. of Hammers removed as a Temporary Measure, to reduce the GD^2 value.

2. A grid resistor was added to the Rotor circuit to develop more torque and increase the Slip of the Motor was increased to 15%

3. Then it was decided to replace the Grid Resistor with Auto-Slip Resistor to the Motor Rotor circuit, put back the hammers which have been removed.

Now it is working alright with 120 hammers, and Auto-Slip Resistor to the Moto.

DHAYANANDHAN.S

Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#9

Re: doubt regarding GD2 of motor

11/29/2014 2:40 AM

Dear Friend,

The motor GD^2 value MUST be more than the GD^2 of (PUMP + COUPLING). Then only the equipment will start and accelerate to full speed. Then only the starting Torque will be more than the Load Torque. The Higher the GD^2 of the Motor, the faster and quicker the starting and attain full speed and take the load.

If GD^2 value of motor is less then, the Motor will not start, start humming and the starting current will increase and get tripped. If it does not tripp, the motor or starter get damaged.

DHAYANANDHAN.S

Reply
Reply to Forum Thread 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dhayanandhan (2); electricalexpert65 (3); kvsridhar (2); redfred (2)

Previous in Forum: connection details for Start/STop Push button   Next in Forum: POWER ESTIMATION

Advertisement