This is a real world example of how strange low voltage signals and noise sources can be at times.
To start, this is packaged machinery and falls under NFPA 79, so no criticisms of the wiring based on NEC 300 please, as we usually don't have room to run conduits everywhere on our machinery.
Situation:
1. 50 HP motor with VFD drive fed by 4 #2 AWG conductors in ss conduit with a 2' flex connection to the jb.
2. Vibration sensor mounted on the equipment driven by the motor and it is a 4-20ma device. This is connected with a shielded cable to a signal jb with a shielded cable. My connections are made to this terminals strip in this jb. It is mounted very close to the motor by necessity due to space availibility.
3. VFD cabinet and PLC cabinet on the framing with the motor. The run from the sensor to the PLC cabinet has to pass under the VFD cabinet.
4. Sensor wiring is foil shielded 2#18 cable with drain wire by major cable manufacturer. Run to sensor is partially in ss conduit (protect where someone might step on the cable to access the equipment) with three discrete (24VDC) signal cables. Exposed for 2' before the jb where the sensor is wired to, and for the distance under the VFD and PLC cabinet to entry under the far end of the PLC cabinet. (there is some 120VAC in the PLC cabinet, but it is segregated from the 24VDC signals)
When we tried to run the VFD, the sensor signal would go over 20ma. Noise for sure. To expedite check out of the other devices we temporarily ran a replacement cable from the same spool outside the frame to the PLC cabinet from the sensor jb. This worked. Noise stopped, so we knew we had to add more shielding protection to the signal cable.
To stop the noise we ran an ss conduit most of the way from the jb to the PLC cabinet with only 1.5' of exposed cable at each end. At this point we re-connected the original cable through this conduit. The noise returned. I said let's try something. I put the cable we had run temporarily into the conduit and replaced the original run with this second cable - no noise. Same location - same connection points - same conduit - same type of cable from the same spool. Everything identical except the cables, which as stated had come from the same spool of wire.
My best guess is that the foil shielding is not continuous inside the first cable. Any other thoughts?
"Almost" Good Answers: