Four Way Switching

04/14/2011 10:44 PM

Hi I know that for two way switching I would use 2 two way switches and for three way switching I would use 2 two way switches and one intermediate.My question is how many two way and how many intermediate do I have to use for 4 way switching?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Four way switching

04/14/2011 10:59 PM

In your terminology, you need (2) two-way switches and (2) intermediate switches.

Your two-way switches are single pole double throw, with (3) wire connections. Your intermediate switches are double pole double throw, with (6) wire connections.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#8
In reply to #1

Re: Four way switching

04/15/2011 11:45 PM

Hi Tornado

I was under the impression that intermediate switches were only 4 wire connection!

You can put in as many of these as you want, as long as they are between the two way switches. An intermediate switch is just a cross over switch

Changes on any switch will turn off or on the load.

Best regards

Joe

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#13
In reply to #8

Re: Four way switching

04/16/2011 12:09 AM

I have also forgotten to add one other point when wiring intermediate switches, I believe it is illegal to use standard single phase cable for the wiring to and from intermediate switches, this is because you cannot use a neutral as a phase conductor in most countries, best answer is to use 3 phase cable between 2 way switches and intermediate switches.

Cheers

Joe

Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#15
In reply to #13

Re: Four way switching

04/16/2011 12:54 AM

Armour Flex is your friend

you can also pull new wires in if you change you mind about how many wires or what colors to run

I doubt that we are talking about this kind of installation if solder is involved

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#17
In reply to #15

Re: Four way switching

04/16/2011 1:10 AM

Hi Garthh

Who mentioned solder?

I thought this was about intermediate switching? But maybe I have had to much to drink or my by-polar thing is kicking in again.

Cheers

Joe

Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#20
In reply to #17

Re: Four way switching

04/16/2011 1:29 AM

Op on the thread before on the Daily Digest

Register to Reply
Power-User

Join Date: Aug 2008
Location: Chicago, IL USA
Posts: 120
Good Answers: 2
#18
In reply to #15

Re: Four way switching

04/16/2011 1:18 AM

Garthh,

Your pic showing BX cable is prohibited here in Chicago that is greater than 3 feet in length do to a cow that burnt down our city in the late1800's.

Does anybody have a smiley face that looks like a piss off cow?

Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#19
In reply to #18

Re: Four way switching

04/16/2011 1:28 AM

Not if it's inside the walls....

the reg you are talking about refers to exposed BX

Register to Reply
Power-User

Join Date: Aug 2008
Location: Chicago, IL USA
Posts: 120
Good Answers: 2
#21
In reply to #19

Re: Four way switching

04/16/2011 1:33 AM

Not Here in Chicago.

Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#22
In reply to #21

Re: Four way switching

04/16/2011 2:04 AM

3 foot of exposed BX maximum is standard for residential in the rest of the civilized world

for industrial liquidtite is required exposed installation

BX is commonly used in place of conduit inside of walls, in commercial buildings...

I see that Cook county has it's own rules & doesn't allow BX or Romex at all, having less to do with safety than Chicago being a good union town

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#23
In reply to #22

Re: Four way switching

04/16/2011 2:24 AM

What? Not even in cable trays in industrial environments?

Shirley not.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Power-User

Join Date: Aug 2008
Location: Chicago, IL USA
Posts: 120
Good Answers: 2
#24
In reply to #22

Re: Four way switching

04/16/2011 2:48 AM

I live in a rural area a hour west of Chicago were those city folk think we're hillbilly's with cows that cause them grief. We have county that still allow BX and Romex, but not many.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#25
In reply to #18

Re: Four way switching

04/16/2011 3:00 AM

Best i could find...

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Aug 2008
Location: Chicago, IL USA
Posts: 120
Good Answers: 2
#26
In reply to #25

Re: Four way switching

04/16/2011 3:15 AM

You're DA-Man... I mean Cow... I mean!

Thanks for making my day closure will sleep good tonight.

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#14
In reply to #8

Re: Four way switching

04/16/2011 12:46 AM

There may also be 4-terminal crossover switches, but the ones I have used were 6-terminal DPDT switches (two each of A, COM, and B).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#16
In reply to #14

Re: Four way switching

04/16/2011 1:04 AM

Hi Tornado

I would be interested to see how your switches work, obviously this circuit would require more wiring, and I have not seen a domestic switch module like this in my life, Mind you I have not given it to much thought.

Can you please supply a simple drawing of how it works, for my simple mind.

Best Regards

Joe

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#27
In reply to #16

Re: Four way switching

04/16/2011 4:56 AM

Many years ago I was told that 4-way, 5-way, etc., switches were impossible. Using electronic toggle switches (SPDT at the ends, DPDT in the middle), I made up a 5-switch panel, plus a selector switch that would make make active 1, 2, 3, 4, or all 5 toggle switches.

This computer doesn't yet have good drawing facilities on it, so I can only fake it verbally. An SPDT (3-way) switch has common (C), A, and B terminals. A DPDT (four-way) switch has two sets of the same: C1, A1, B1, C2, A2, B2. All of these DPDT switches are wired "crossover" A1-B2 and A2-B1. (This crossover wiring is internal to the 4-terminal intermediate or 4-way switches shown in the thread.)

The first SPDT switch has "hot" to C. A goes to C1 of the second (DPDT) switch, B to C2. From the second to third DPDT, B1 goes to C1, B2 to C2. This continues for as many DPDT switches as there are. From the last DPDT switch to the final SPDT switch, B1 goes to A, B2 to B. Then C goes to the light.

In this case, a picture would be worth about 130 words....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Four way switching

04/14/2011 11:00 PM

4-way Switches

Now lets throw a four way switch into the picture.

The terminals on the four way switch will be labeled to let you know which ones to connect to each leg of the travelers. The third (white) wire in the 14/3 is connected up as to just pass through.

What happens when the four way switch is flipped is the internal connections are reversed. That is, if, internally:
S1's RED was connected to S2's RED and
S1's BLACK went to S2's BLACK (as shown),
switching the four way will cause S1's RED to go to S2's BLACK and S1's BLACK to S2's RED.
That will either make or break the circuit (in the diagram, it will complete the circuit).

4-way Switches

Now lets throw a four way switch into the picture.

The terminals on the four way switch will be labeled to let you know which ones to connect to each leg of the travelers. The third (white) wire in the 14/3 is connected up as to just pass through.

What happens when the four way switch is flipped is the internal connections are reversed. That is, if, internally:
S1's RED was connected to S2's RED and
S1's BLACK went to S2's BLACK (as shown),
switching the four way will cause S1's RED to go to S2's BLACK and S1's BLACK to S2's RED.
That will either make or break the circuit (in the diagram, it will complete the circuit).

Register to Reply Good Answer (Score 2)
2
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#3

Re: Four way switching

04/15/2011 1:58 AM

Too complicated for a Friday

Why not use a signal wire with a push button to supply a pulse at each station and a flip-flop at the light fitting.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#4
In reply to #3

Re: Four way switching

04/15/2011 9:31 AM

I suspect that this will become the most economic solution, if it is not already in many cases.

Smaller wires to install, simpler devices except for the relays / flip-flop.

But, it is not the traditional approach, so will have some resistance due to, well, tradition. ;-)

Register to Reply
Associate

Join Date: Jul 2009
Posts: 49
#5

Re: Four Way Switching

04/15/2011 9:53 AM

hey thanks very much guys ,thanks for the wiring diagram too. I'm gonna pick up those switches today and start my wiring.

Register to Reply
Power-User

Join Date: Aug 2008
Location: Chicago, IL USA
Posts: 120
Good Answers: 2
#6

Re: Four Way Switching

04/15/2011 3:10 PM

To add to post-2.You're not just limited to one 4-way switch, you can put as many of those as you want, as long as you install them between your 3-ways.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#10
In reply to #6

Re: Four Way Switching

04/15/2011 11:57 PM

Hi Dkriley, dont you mean 2 way switches, because with a 3 way switch it would never work.

Best Regards

Joe

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7

Re: Four Way Switching

04/15/2011 11:04 PM
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#9
In reply to #7

Re: Four Way Switching

04/15/2011 11:54 PM

Hi Kvsridhar,

You bet me to it, so you get my GA.

An intermediate switch is just a cross over switch.

Also what programme did you use to give your graphic presentation, I like it.

Best Regards Sub

Joe

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#12
In reply to #9

Re: Four Way Switching

04/16/2011 12:01 AM

Thanks Joe, i am embarrassed to say, this is just an image from some website after Google search

However, i use Solidworks 3D CAD software in my work, and i can do such diagrams easily in that one.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#11

Re: Four Way Switching

04/15/2011 11:58 PM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Power-User

Join Date: Apr 2005
Location: Scotland
Posts: 164
Good Answers: 8
#28

Re: Four Way Switching

04/16/2011 7:27 AM

During training we had an exam question - "You are required to wire up a lighthouse so that the light on the top can be switched On or Off from any of the 10 floors in the tower"

Only one candidate gave the correct answer - use a bathroom ceiling switch with a cord going through holes in each floor to the base of the tower!

(He went on to Officer training!!!)

Simples ...

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#29
In reply to #28

Re: Four Way Switching

04/16/2011 9:05 AM

I like that J

Must be one hell of a pull cord to switch the beacon light on and off, who's pulling it Quasimodo?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#30
In reply to #29

Re: Four Way Switching

04/21/2011 8:07 AM

I would suspect that in this scenario, the weight of the cord would turn all of the switches Off. (Unless they are weird switches in which down = on, which happens occasionally in benighted places.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Aug 2008
Location: Chicago, IL USA
Posts: 120
Good Answers: 2
#31
In reply to #30

Re: Four Way Switching

04/21/2011 10:46 AM

It a toggle switch. You lightly pull it once ON, lightly pull it again OFF. Just done attempt to use it as a fire pole.

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#32
In reply to #30

Re: Four Way Switching

04/21/2011 9:15 PM

"benighted places" Harrumph

(Of course you would need a contactor if the light is over 3600W)

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Register to Reply 32 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (2); dkriley (6); Garthh (4); Hendrik (1); Joe Sparky (6); kvsridhar (3); lyn (1); msamad (1); phillip (1); rhkramer (1); tom (1); TonyS (1); Tornado (4)