04/16/2011 6:00 AM
I closed a old 440V oil breaker on a fault. it felt ok till it got to contacts closeing then the handle bounced back had to use both hands to get it close then it tripped. What made the handle bounce
Re: old breaker
04/16/2011 7:24 AM
Because both hands were not enough--you need three hands.
Reply Score 1 for Off Topic
India - Member - New Member
Good Answers: 164
Re: old breaker
04/16/2011 8:10 AM
You are used to modern breakers which are "Trip free" or "Free handle". In the olden days of the OCB, some were not trip-free. When you closed the breaker on to a fault (a) the contacts would repel, the force being proportional to the square of the current and (b) the overcurrent release would act, trying to trip the breaker. If you had a modern trip-free breaker, it would trip immediately, in spite of you trying to close the breaker. Since your OCB was not trip-free, it couldn't and wouldn't trip. You are lucky that it did not explode and hurt. A friend of mine died doing this same thing, a long time ago.
Good Answers: 804
Re: old breaker
04/16/2011 3:54 PM
"You are lucky that it did not explode and hurt."
Now you've done it! By mentioning this, you have now cursed this poor person because it's a well established fact that ignorance of a danger is often the last remaining protection you have against it occurring. Now that he knows, it's all but guaranteed to happen next time. You have stripped away the magic aura that was keeping that disaster at bay.
To illustrate the genesis of this knowledge: I once had a project to commission a very large soft starter on a compressor in a 100+ year old saw mill in Idaho. It was a grueling task in that the available power source was almost too weak to allow this motor to start. But after an entire day of trial and error, I succeeded and became the hero of the day for this sawmill because nobody had been able to do it since the utility refused to approve the service change, effectively shutting them down, for causing too much of a voltage drop (another long story involving a TV/Movie star as to why).
As I was leaving the mill, we walked by a very old "One Armed Bandit", an oil bath manual compensator motor starter. It's an archaic form of an autotransformer starter that had a manual crank on the side to change the transformer taps as you started the motor. The contacts of this manual transfer switch mechanism were in an oil tank on the bottom. The oil tank had a leak and they had a coffee can under it to catch the oil. As we walked by, the maintenance tech saw that the can was almost full, picked it up and poured it back into the tank, sawdust and all! I was in shock and told him that what he was doing was not only horribly foolish but created a serious risk of fire. He said they had been doing it that way for 25 years, no problem. I wrestled with the idea of calling OSHA (the US industrial safety watchdog agency) but my employer pleaded with me not to because they were a good customer.
2 weeks later the starter did in fact catch on fire and the 100+ year old sawmill went up in a cloud of smoke in under an hour. No deaths but they couldn't re-open that mill. 150 lost jobs and total devastation to the small mountain community that it supported. I got a dunk call from that maintenance technician in which he blamed me.
Good Answers: 164
Re: old breaker
04/16/2011 9:39 PM
Ah yes, the guardian angel of the ignorant. i didn't think of her. Sorry OP, you better get a new ACB or VCB retrofitted as has been suggested by Tony. i hereby wash my hands off your any future misfortunes
Good Answers: 181
Re: Old Breaker
04/16/2011 8:50 AM
As kvsridhar said it's the repulsion of the contacts add to which you have the oil boiling/vaporising between the contacts. Many older breakers would not trip until fully closed. The biggest danger is changing your mind and allowing the contacts to open slowly. Unfortunately kvsridhar's friend found out the hard way.
There are companies out there that can retro fit many types of board with modern ACB's / VCB's. have a look for them. Retro fitting saves re-cabling and is quick. The last retro fit I got involved with took about 2 hours per breaker including time to test/alter the tripping arrangement.
Re: Old Breaker
04/16/2011 11:33 PM
You are a lucky man to be writing this. You could have possibly experienced Arc Flash in a personal way. There are times to reset a breaker, and there are times to leave it to a pro to find out why it faulted and if it is safe to energize again.
Luck was on your side this day.
"Real Bass Players" do not use picks
Re: Old Breaker
07/25/2024 9:57 AM
The answer is in the question: it bounced because <...closed a old 440V oil breaker on a fault....>. The breaker said that it isn't playing.
Eliminate the fault, and have another go. Please make sure all other CR4 subscribers are standing well back before so doing.