We have a potential problem with a voltage diff between neutral and ground--
the system consists of a 45kva isolation transformer, 600V to 400/230 three phase 5 wire config. Equipment FLA is 30amps.
Voltage measurements as below with equipment running..
V L1-230.8 L2-233.1 L3 232.3 N-Grnd 2.31
V L1-L2 405.8 L2-L3 408.7 L1-L3 404.6
The equipment manufacturer is suggesting that the voltage between neutral and ground is 'severe' and may be causing electronic issues. This is a large format digital printer printing banners.
All connections -line,neutral,ground have been removed and retightend to confirm integrity.
All wirng is to 'spec' and sized correctly.
The transformer is a mere 50' total wire length to the machine.(# 8awg wire is used rated at 40A)
The ground is bonded to the neutral and to the building.(also #8awg)
Is this ~2volt nuetral to ground a potential problem.
Thanks for any assistance.