Exact Derating Factor

04/19/2011 5:08 AM

What is the exact derating factor to be considered for selecting the rating of a breaker for a capacitor in an APFC Panel?

__________________
Prem
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Exact Derating Factor

04/19/2011 6:47 AM

Why to de-rate in the first place?

The only thing to check is the inrush current of the last capacitor in a bank with all other capacitors already ON and check whether the making capacity of the breaker is more than this worst case scenario inrush current.

Also, to be checked is the setting (both current as well as time) in the Instantaneous and/or Short Time Releases of the breaker. And, ensuer that the release wouldn't trip for a switching inrush.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Exact Derating Factor

04/19/2011 8:00 AM

The word "exact" is fishy.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: Exact Derating Factor

04/19/2011 8:51 AM

In addition to the good points by ee65, may i add:

1. Thermal derating factor of 1.43 as explained by AEG here..

2. Circuit breakers should be used for protection only. Capacitor switching should be done by contactors specially designed for this purpose. If CB is used for switching on and off, its life will be over very soon. Contactors have a life of millions of operations while CBs have a life in thousands only.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Exact Derating Factor

04/19/2011 1:53 PM

NEC requires the breaker to be 135% of the capacitor amperage.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Exact Derating Factor

04/19/2011 3:17 PM

What about looking in British Standard 7671?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply