Ground

05/09/2011 10:18 AM

Can the GROUND wire in a house for A/C 120 volt wiring be used for the ground of a D/C 12 volt system. with a seperate wire for the positive for both systems. In other words can they share the COMMON GROUND wire? If so what would I need to use for blocking shorts for either system, keep them seperate so to speak.

__________________
"No where to go but up, LPCS". "One things for sure theres always two"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#1

Re: Ground

05/09/2011 10:38 AM

If you utilize the same ground it must somehow be referenced in the 12 volt circuit. DC especially needs that complete circuit. For example, if you connect the negative cable in your car to a ground rod and the positive cable in your car to the battery you will not get power to the car. Not in any appreciable form anyway. The ground rod would have to have a reference to the car's frame.

If you were running DC power supplies throughout your house (for whatever reason) you could reference your existing ground in your house, which would require the negative terminal of each DC supply to be connected to the house ground somewhere. Your house ground may or may not be isolated within the DC supply from the negative side of the DC supply, that's dependent on the design of the supply. Normally, it is isolated. Most DC supplies I have do not have a ground lug (third prong) anyway, just hot and neutral.

Keep in mind that this would put an additional load on your DC power supply as the circuit is now much larger than it would be if a normal small closed loop circuit were used.

They can share the common ground. There is no problem there unless you are carrying high current levels on your ground return path and that makes it through your DC supply somehow.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #1

Re: Ground

05/09/2011 11:09 AM

It is better to run a separate 0V conductor and ground/earth the 12VDC supply at its source only. That way, a simultaneous overcurrent in both the 12VDC system and in the mains system will not overload the ground/earth conductor at any place. Reference British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#4
In reply to #3

Re: Ground

05/09/2011 11:19 AM

Yes, excellent point. I am not sure where the op was going with this, but standards are definitely in place for a reason. Since there is a published reference for this situation, I would go with that.

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#2

Re: Ground

05/09/2011 11:08 AM

Have you ever noticed 24VDC battery bank of generator with a negative end connected to generator case?

Where does the case, in its turn, connect to? The common grounding bar.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Associate
Hobbies - Automotive Performance - New Member

Join Date: Mar 2011
Location: Washington
Posts: 41
#8
In reply to #2

Re: Ground

05/09/2011 10:45 PM

So if I leave the mains ground alone and use the common grounding bar it would be fine right, would the positive D/C need to be as a 12 gauge or 14 gauge wire then?

__________________
"No where to go but up, LPCS". "One things for sure theres always two"
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18
In reply to #8

Re: Ground

05/10/2011 3:49 AM

Well, that depends upon the current the system is expected to supply, the permissible voltage drop and the electrical code applicable at the location of the installation.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#5

Re: Ground

05/09/2011 3:19 PM

Physically it can be done but it will not conform to code in Washington. Also this would likely cause GFCI breakers to trip and the wiring will be undersized with larger DC loads.

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Dec 2009
Location: New Zealand
Posts: 121
Good Answers: 4
#6

Re: Ground

05/09/2011 10:44 PM

This is the first time I have heard of anyone grounding a 12V system through the earth. Is this normal?

I thought that DC was not normally grounded because of the potential for corrosion of the electrode.

Register to Reply
Power-User

Join Date: Apr 2007
Posts: 414
Good Answers: 19
#17
In reply to #6

Re: Ground

05/10/2011 2:40 AM

That is why US telephone systems, which run on a 48V battery supply, use a positive ground.

Register to Reply
3
Power-User

Join Date: Mar 2011
Posts: 117
Good Answers: 15
#7

Re: Ground

05/09/2011 10:45 PM

So will you be really mad if somehow you get the impression from this group of responses that you could do what you are asking: and then one day some one is replacing a 120 AC device, interrupts this common used ground and then the AC side wants to find a new path to ground through one of your DC devices it blows the DC connected device to charcoal heaven?

You need to think beyond how or if it can work and think about the ways that it can fail and what the results will be. DC current verses AC current? You can see what DC can do when any welder is nearby.

__________________
For every action, there is an equal and opposite criticism.
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#9
In reply to #7

Re: Ground

05/09/2011 11:18 PM

Why are you are hellbent on inviting trouble? That is my only question.

Register to Reply
Active Contributor

Join Date: Mar 2010
Location: Detroit, MI
Posts: 11
#45
In reply to #7

Re: Ground

05/13/2011 8:45 AM

You must adhere to code. However, the answer provided by "Beenaround" is the most logical approach. He provided an excellent engineering answer. The safer thing to do is to not use a common ground.

__________________
The only way to know is to apply what you learn!
Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#10

Re: Ground

05/09/2011 11:47 PM

There will be always risk. Better have separate earth or draw separate wire wire from earth source.

__________________
Subramanyam
Register to Reply
Associate
Hobbies - Automotive Performance - New Member

Join Date: Mar 2011
Location: Washington
Posts: 41
#12
In reply to #10

Re: Ground

05/09/2011 11:53 PM

Got it and great answer.

__________________
"No where to go but up, LPCS". "One things for sure theres always two"
Register to Reply
Associate
Hobbies - Automotive Performance - New Member

Join Date: Mar 2011
Location: Washington
Posts: 41
#11

Re: Ground

05/09/2011 11:52 PM

OK so I do understand the worry and concern and inputs, thank you again. I do understand better. I will use seperate Sytems for sure.

Valuble stuff here

What I did not know before I do now..

LPCS /Gary

__________________
"No where to go but up, LPCS". "One things for sure theres always two"
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Feb 2011
Location: Perth, Western Australia.
Posts: 72
Good Answers: 1
#13

Re: Ground

05/10/2011 12:00 AM

I agree with leveles. Others have pointed out if you have a problem on the 'high' voltage side it could get complicated even lethal. Keep the two separated. Some transformers have an earthing connect point but it has nothing to do with low voltage side, its there to ground the system if something goes wrong 'high' voltage side.

__________________
'Nunc est bibendum'
Register to Reply
Power-User

Join Date: Nov 2009
Location: In the Ozark woods in missouri.
Posts: 106
Good Answers: 3
#14

Re: Ground

05/10/2011 12:42 AM

Everyone here had pretty good answers, but for me I would not want the 12 volt hum in my 110 appliances. Also, like one gentlemen said, if house current wants a new path to ground, there goes your DC stuff. Could end up being very costly, especially if you are renting.Always keep DC ground seperate from AC grounds. In my ham shack, I never mix the two. ALL my stuff is costly, and some irreplaceable. Have a good day guys.

__________________
Life is tough, but it`s tougher if your stupid, John Wayne.
Register to Reply
Anonymous Poster #1
#15

Re: Ground

05/10/2011 1:37 AM

Yes you may use the common ground. You just consider about simple rectifire circuit,a common ground is used for both AC and DC

Register to Reply Off Topic (Score 5)
Associate
Hobbies - Automotive Performance - New Member

Join Date: Mar 2011
Location: Washington
Posts: 41
#16
In reply to #15

Re: Ground

05/10/2011 1:55 AM

Pleae give me a reference for this finding,,,as I thought so,,,I beleived it could be used but with protection and you say a rectifier?

__________________
"No where to go but up, LPCS". "One things for sure theres always two"
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#19

Re: Ground

05/10/2011 4:30 AM

Common Ground Systems are used all the time, just take a look at switch-mode power supplies the usal case is that netural is connected to ground, the only time that this is not the case is with sensitive systems that cannot afford voltage or current fluctions.

Cheers Joe

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#20
In reply to #19

Re: Ground

05/10/2011 4:43 AM

And common ground system here is the main grounding system of the house not the 12VDC equipments.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#31
In reply to #20

Re: Ground

05/10/2011 3:56 PM

Opp's i said that the netural was connected to the ground, which it is but I meant to say that the negative is connected to the ground

Cheers

Joe

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#44
In reply to #20

Re: Ground

05/12/2011 2:50 AM

Hi Hein

As long as the Ground is only used as a Ground system, I don't have a problem with that. If the Ground is used as the main return path, I would have some problems.

Cheers

Joe

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#21

Re: Ground

05/10/2011 10:23 AM

Holy crapadocius! I am not sure where this thread went overnight...If you look at a standard DC power supply in just about every computer in the world (for example), the case of the power supply is connected to the case of the computer. Both are effectively grounded to the ground terminal of the power cord.

They share ground...period!

The very basics of power supply construction shows a clear connection in the rectifier circuit to what? Ground! Where is that ground from? The case! Where is the case connected to?

Do I need to keep on?

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2011
Posts: 117
Good Answers: 15
#22
In reply to #21

Re: Ground

05/10/2011 10:31 AM

Hey Cuba Pete,

Does your computer case/frame carry current? No,it is really a safety ground...not a DC current carrying "ground". DC ground is closer to but still very different to AC neutral.

__________________
For every action, there is an equal and opposite criticism.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#23
In reply to #22

Re: Ground

05/10/2011 10:46 AM

No, not normally...I don't suspect anybody's does (!). The OP and, I believe, intent of this thread was to ground a DC power supply, not use the frame as a current carrying device for negative DC power. Those are very different things.

I have attached, as a matter of course for all interested, a schematic of a simple AT switching power supply. Please note the connections to frame ground, which references the ground supplied by a standard three prong plug. All effectively the same...continuous...bonded...ground.

If the image is too small, it may be found here: http://www.cmheong.com/work/schematics/at_psu_3.gif

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#24
In reply to #23

Re: Ground

05/10/2011 10:53 AM

Nevermind...I read back through the OP and subsequent responses and I don't think I really understood what the original intent was.

I think I must recuse myself from this discussion.

Register to Reply
Associate
Hobbies - Automotive Performance - New Member

Join Date: Mar 2011
Location: Washington
Posts: 41
#26
In reply to #24

Re: Ground

05/10/2011 12:34 PM

My question was. I want to use the commons ground of the mains for the common ground of my D/C system, will there be any problems with doing this or do I need to run a complete seperate D/C wiring system?

That was the start of this discussion.

__________________
"No where to go but up, LPCS". "One things for sure theres always two"
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#29
In reply to #26

Re: Ground

05/10/2011 3:12 PM

The answer is.

It could work - but don't do it, unless you want to risk killing someone!

Register to Reply
Associate
Hobbies - Automotive Performance - New Member

Join Date: Mar 2011
Location: Washington
Posts: 41
#25
In reply to #22

Re: Ground

05/10/2011 11:48 AM

OK! SO I now have in scenario A< mains wiring and D/C wiring, Seperate systems and now how far aprt should they be in the travel from light source to some given distance from the light source. Can there be interference between the fields of each power supply. In other words, could their be a potentilial probblem with them in close proximity or overlapping in conduit or should that be seperate?

__________________
"No where to go but up, LPCS". "One things for sure theres always two"
Register to Reply
Power-User

Join Date: Mar 2011
Posts: 117
Good Answers: 15
#33
In reply to #25

Re: Ground

05/10/2011 9:05 PM

Hi again,

You are certainly asking some interesting questions here. I want to respond from my experiences of 46 years with everything from shipboard radio, radar, sonar; with house wiring, computer room wiring ( 1968 to present) where the computers were large enough to walk inside and the whole system could fill rooms 40' x50' for one system. We had motor alternators to buffer surges from the power company (pre- outlet strip protection) I am familiar with transient spike coming across or through a grounding system, radiated from electrostatic air cleaner, electronic ignition for factory overhead furnaces.Static electricity from moving belts or material. I am familiar with radio and radar using waveguides and antenna theory. Enough of the bragging.

Please provide some very specific information of what devices you will be powering with the 12VDC. What type of signal you are concerned may be interrupted. You mention distance from "light source", what is this light source? Fluorescent, led, incandescent? Are you using the 12VDC as a control signal, to carry data or information, or radio signals? There are ways of shielding for radiated electrical interference even to the extent that the military used in the 70's to prevent spying during the cold war. Also provide and unique 120 VAC devices connected.

__________________
For every action, there is an equal and opposite criticism.
Register to Reply
Associate
Hobbies - Automotive Performance - New Member

Join Date: Mar 2011
Location: Washington
Posts: 41
#34
In reply to #33

Re: Ground

05/10/2011 9:54 PM

Well with out mixing things up I need to tell you that I have another submission called LPCS here on the discussion board. With that be said then i wanted to know about cost saving by utilizing wiring already in place and only adding one more for the positive wire and utilizing ground as is in the mains and have D/C to go to some location, component or storage system somewhere with in the environment producing the light in the first place. The LPCS will move the D/C, and I do say I have my own opinions on the amount of voltages but for now that is what my task is. To get D/C power from point a to point b and do it as cheaply as possible. I was concerned that if the total combined D/C voltages around 14.4 volts and over 200 amps collectively of course, would that be a concern when in the close proximity of the 120 v A/C mains supplying power to the lights. I know it seems complicated but it turns out rather simple. The part about electomagnetic interference and the such is my concern, or for that matter any type of interference. I know their is an answer just not sure i am askng it correctly.

Thanks for your help.

LPCS /Gary

__________________
"No where to go but up, LPCS". "One things for sure theres always two"
Register to Reply
Anonymous Poster #2
#38
In reply to #34

Re: Ground

05/11/2011 12:17 PM

200 Amps!? 12 gauge will simply melt.

You are going to need something like 3/0 copper or better depending on the length and allowable voltage drop.

Register to Reply
Power-User

Join Date: Mar 2011
Posts: 117
Good Answers: 15
#39
In reply to #38

Re: Ground

05/11/2011 12:28 PM

I was pondering this too. A car battery is rated between 500-700 cold cranking amps, so what are "cold cranking amps" verses normal amps. Yes, 4 or larger and the distance/lenght can play in so it should be the fine strands or face the drop. Now the OP does say "cummalative" . Is that code for "many circuits"?

__________________
For every action, there is an equal and opposite criticism.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#40
In reply to #39

Re: Ground

05/11/2011 1:05 PM

Cold cranking amps is the rating of the battery. That is a capability of the battery, not what it is actually delivering.

The current draw is determined by the load, not by the capability of the source.

I have a lighting panel in my facility. The panel is rated at 125A. The lights only actually pull around 30A total, all circuits.

Starting my car on Christmas morning in Bismarck, ND would require much more current than starting it in Honolulu, HI (on just about any day!), rhetorically speaking.

Register to Reply
Associate
Hobbies - Automotive Performance - New Member

Join Date: Mar 2011
Location: Washington
Posts: 41
#41
In reply to #39

Re: Ground

05/11/2011 1:14 PM

In this case it means number of individual LPCS in series to produce the current to the system. For instance store a has 4000 of these overhead artificial lights and they basically are on 24hrs day. If done correctly at any given time the result will be well over 200 amps but I am sure we could work out the logistics of the system and make it very efficient with some inverting along the way to mains or basically wherever it would be needed.

__________________
"No where to go but up, LPCS". "One things for sure theres always two"
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#27

Re: Ground

05/10/2011 12:45 PM

Are you trying to run a single wire for the DC + side and use the AC ground for the DC - side?

__________________
Mr.Ron from South Ms.
Register to Reply
Associate
Hobbies - Automotive Performance - New Member

Join Date: Mar 2011
Location: Washington
Posts: 41
#28
In reply to #27

Re: Ground

05/10/2011 12:58 PM

100% yes!

exactly !

__________________
"No where to go but up, LPCS". "One things for sure theres always two"
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#32
In reply to #28

Re: Ground

05/10/2011 4:23 PM

Then the answer is NO.

The ground conductor is there for a specific reason, to provide a safe path for ground fault currents.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#42
In reply to #28

Re: Ground

05/11/2011 11:42 PM

LPCS:

Why you want to do that? For safety or operation ground?

For safety, having half a loaf is better than no bread.

For operation, apple is apple. Banana is banana.

Hope that helps.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Active Contributor

Join Date: Jan 2009
Posts: 18
#30

Re: Ground

05/10/2011 3:49 PM

You could use the ground for both if the house was connected to a TT systems which it probably is not. The factory I work in is TT and all neutrals and earths of AC & DC are connected to the same earth. Some motors are on a IT system whis different again.

Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 16
Good Answers: 2
#35

Re: Ground

05/11/2011 12:00 AM

Sorry for being late to the party but there needs to be a distinction made between common and ground. They are NOT the same thing. For instance, a DC electrical system may have a common negative (not ground) or a common positive (again, not ground). Normally you do not want to directly tie your DC common to ground (take a look at a Siemens DC power supply for 24VDC out and 110VAC input - it has 5 terminals, 3 on the AC side (L1, N, PE) and two on the DC side (+, -). THAT PE on the AC side absolutely must be tied to ground for safety. Connecting the + or - on the DC side to ground is asking for trouble. So the upshot is NO, don't connect your DC common to ground, but do connect your metal chassis to ground.

Register to Reply
3
Guru
Engineering Fields - Electrical Engineering - Hmmm...

Join Date: Jul 2010
Location: Maryland
Posts: 567
Good Answers: 29
#36

Re: Ground

05/11/2011 8:06 AM

LPCS, please keep in mind the difference between the safety ground and the neutral in AC systems. Some of the posts here appear to mix the two. The safety ground (the bare wire in AC systems) is not intended to carry current under normal circumstances. It exists to carry fault current only. The neutral wire (the white wire in AC systems) is normally used to carry current and is bonded to ground at the breaker panel only.

As noted above, if you use the AC neutral for your DC return, you risk running AC current through your DC devices if there is a fault.

Keep in mind that AC wiring at 120 or 230 volts will allow smaller gauge wire for a given power throughput. DC wiring, especially at the currents you are discussing (200 amps?) will require much larger wire.

Under no circumstances should you ever use the AC safety ground to carry any current (AC or DC) in non-fault conditions. As most grounded equipment, including cabinets, cases, and the like, is connected to the AC safety ground, you risk elevating your equipment to voltage potentials other than ground. This can quickly become dangerous.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#37
In reply to #36

Re: Ground

05/11/2011 9:29 AM

You nailed an important point there. You raise the reference. GA.

Register to Reply
Associate
Hobbies - Automotive Performance - New Member

Join Date: Mar 2011
Location: Washington
Posts: 41
#43

Re: Ground

05/12/2011 12:03 AM

Trying to do a job sometimes cannot be done cheaply. I see that. I also see a great way to have a conversation and get to the right answer with out all the bull is phenominal. All the post rated or not have been outstanding and I really thank you all.
LPCS /Gary

__________________
"No where to go but up, LPCS". "One things for sure theres always two"
Register to Reply Off Topic (Score 5)
Register to Reply 45 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ace Boeringa (2); Anonymous Poster (1); Beenaround (4); bubbapebi (1); crashcol (1); cuba_pete (7); hien.nguyenquoc (3); Joe Sparky (3); JSCadman (1); kvsubramanyam (1); leveles (1); Lo_Volt (1); LPCS (10); PWSlack (2); rcrain (1); rls1230 (1); ronseto (1); Smeaton (1); TonyS (1); woobster1 (1)

Previous in Forum: ETAP 7 Launch Problem   Next in Forum: Generator Exhaust Through Steel Ceiling Bushing Material

Advertisement