VFD Drive

05/11/2011 10:13 AM

Hello

I have a VFD drive altivar telemechanique 58 rated 45KW operation.

My question is, what will happen if I connect it to a motor of 30KW rating?

Will it be safe?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: VFD Drive

05/11/2011 12:02 PM

There are other pertinant data to consider. Please expound.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: VFD Drive

05/11/2011 12:33 PM

The correct response is, ask Schneider, they are the only ones who can accurately respond based on the design of their product.

As a general rule, VFDs can be connected to motors as low as 50% of their intended rating. Technically it would not matter at all, but in programming you must tell the VFD what the motor FLA is, and many mfrs have the programming lower limits set to 50% of the rating. This is (generally) because of measurement error that will increase at lower levels of current through the sensors. For example most use Hall Effect transducers to sense current. At the rated current of 65A they are typically looking at 0 to +5VDC from the transducer and the FLC should fall into the +3VDC area to allow working room above and below. But if connected to a motor that is only 10A FLC, that same transducer range makes the measurement now crowded into 0 to 0.77VDC, too narrow to be reasonably accurate.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#3

Re: VFD Drive

05/11/2011 10:53 PM

Simple rule of choosing the inverter, choose one which capacity is not less than the motor capacity. See #4 comment @ http://cr4.globalspec.com/thread/68086#newcomments

For this case, Thing may happen is that the torque produced by the inverter may exceed the torque of motor then the motor may become overtemperature. If the inverter has a torque regulation, then you will adjust so there would not be an issue.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: VFD Drive

05/12/2011 9:07 AM

It isn't the inverter that determines whether or not the system is safe. It is the overload trip setting in the inverter parameter list and the supply fuses upstream of it; if it cannot be set low enough, then the overload trip will not prevent the motor from overload and burn-out.

The overload trip is there to protect the motor. The fuses are there to protect the cable. For guidance on this sort of thing, refer to British Standard 7671.

Welome to CR4, BTW.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5

Re: VFD Drive

03/16/2013 4:59 AM

Dear Mr.warlock,

The answer for your Question is YES - 30 KW RATING Motor WILL WORK IN A 45 KW VFD SYSTEM. It will safely work.

DHAYANANDHAN.S

Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

dhayanandhan (1); hien.nguyenquoc (1); JRaef (1); PWSlack (1); RDGRNR (1)