rating for Inverter

04/21/2011 11:44 AM

Dear Engineers

For 22 kw ,400v, 50hz, 1450 rpm, 3 phase squirell cage induction motor can any one guide me what should be the rating of the Inverter ( 22 kw ,25kw,or 30 kw).

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#1

Re: rating for Inverter

04/21/2011 1:32 PM

Well, according to procedure, there are several steps we need to go through:

1. Definition of continuous operation: Operation pattern such as continuous operation or cyclic operation.

2. Capacity selection:

(2.1) Permissible temperature of the motor should not be exceed during operation.

Because temp. characteristics of a motor differs according to: Motor type, inverter control system, output frequency.

(2.2) Can motor be started: The starting torque of motor operated by an inverter is smaller than that of motor operated by a commercial power supply. (low-speed operation or high-speed operation).

Because starting torque of motor varies according to inverter capacity, inverter control system, and torque boost.

(2.3) Acceleration and deceleration capabilities: Motor current is larger during acceleration so we should select inverter that can supply this current. Need to break or not?

3. what kind of load:

4. As a conclusion, select the inverter that has capacity not less than motor capacity.

__________________
Anything that can go wrong, will go wrong
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#2

Re: rating for Inverter

04/25/2011 9:42 AM

Dear,

Inverter is to be selected on the basis of KVA , i.e. KW @ PF 0.8

Consudering Star Delta Operation of motor starter ,

Starting current of motor - 5 * 35A = 175 Amp.

No. of Start / Stops / Hr. = _______ times.

Normal Starting capacity of Inverter( is 1.5 times In) = 175 / 1.5 = 116 Amp.

So, KVA capacity of Inverer = 116 * 1.732 * 0.415 = 83 KVA i.e. 66KW

Please consult the Inverter manufacturer, to confirm the starting KVA capacity of Inverter.

__________________
Exploring the Science of Electricity
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#3
In reply to #2

Re: rating for Inverter

04/25/2011 11:10 AM

HP, in this modern world where people are trying to save every penny. Is that practical when we have to purchase the double capacity of an inverter for an unknown motor application?

__________________
Anything that can go wrong, will go wrong
Register to Reply