Flare Gas Meter Reading High

05/13/2011 7:24 AM

I'm using gf868 ultrasonic flowmeter of panametrics for flare gas flow measurement and recently observed that the flow in the morning remains 8000 kg/hr where as in the afternoon it increasing and went upto 120000 kg/hr where as from the process point of view there is no any flaring took place!

Observation is that temperature is increasing from 30 DegC to 46 DegC in this period and parallel Molecular weight also increased from 29 g/mol to 33 g/mol. Also whenever molecular weight fluctuates that time flow also fluctuates. Sound speed at high flow is showing 312 m/S .

So i would like to know that is these a cause of temperature? or molecular weight or effect of temperature on molecular weight and hence flow?

Register to Reply
Pathfinder Tags: gf868 trouble shooting
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: flare gas meter reading high

05/13/2011 7:41 AM

The speed of sound varies with both pressure and temperature, though a rise of 16degC is unlikely to be the whole cause of the apparent 50% increase in flow.

What does "time flow" mean?

Check the instrument's set-up and that the current parameters are the same as the as-commissioned parameters, in case someone has "fiddled" with it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: May 2011
Posts: 3
#2

Re: Flare Gas Meter Reading High

05/13/2011 2:42 PM

dear i mean to say that

Also whenever molecular weight fluctuates that same time "flow" also fluctuates.

Register to Reply
Associate

Join Date: Mar 2011
Location: Toronto, Ont.,Canada
Posts: 39
Good Answers: 1
#3

Re: Flare Gas Meter Reading High

05/14/2011 10:29 AM

I don't know what gas you are talking about, but it is unlikely that the molecular weight to vary with temperature, if the chemical composition of gas remains the same

Register to Reply
Anonymous Poster #1
#4

Re: Flare Gas Meter Reading High

05/16/2011 4:36 AM

It seems that the problem is in the electronics of Flare Flow meter. Probably the flow meters must be installed in the field and due to heat of sun some component must be mall-functioning, this could be one of the reason of problem. With longer separation is possible (Sick - 1000m and Gf868 400+), nowadays people are installing electronics of flow meters at remote locations like control room or SRR. Other reason could be the Low flow, being intrusive (bias 90) sensors, they may not be able to see any flow during very low flow conditions. The cross duce measurement could be a great solutions for such applications. The Cross Duct sensors are also intrusive type but they inserted upto the pipe surface only and does measure the whole flow profile. Solutions are available from two company one indeed Panameterics and other is Sick Maihak Gmbh. Try out...

Register to Reply