VCB Tripping

05/15/2011 2:35 PM

The VCB in my firm is tripping at full load due to earth fault. This happens at full load after 5 minutes or so.Could any one throw some light on this issue

Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: VCB tripping

05/15/2011 4:38 PM

I can lend you a torch!

You need to give more information.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: May 2011
Posts: 5
#2

Re: VCB Tripping

05/15/2011 11:54 PM

Can you give me the info related to make of VCB.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: VCB Tripping

05/16/2011 12:21 AM

Since it happens after 5 minutes of full-load running, some thermal phenomenon is indicated....to wit, some conductor's insulation is developing a leakage to earth, after getting heated a bit. You can perhaps trace that weak point by meggering.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4

Re: VCB Tripping

05/16/2011 4:27 AM

Please furnish the following information to help you. Relay make and type. CT ratio. Relay settings. Load current. What was the current when VCB tripped

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#5

Re: VCB Tripping

05/16/2011 6:48 AM

What's the rating of the VCB? The Earth fault relay is residually connected? If so, in full load condition, if there is substantially amount of unbalance current, zero sequence component of unbalance current may flow thru the earth fault relay and may cause tripping.

__________________
Manindra
Register to Reply Score 1 for Good Answer
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #5

Re: VCB Tripping

05/16/2011 9:13 AM

Dear manindra,

i have a small doubt here. In all systems i have seen in LV, all four cables (3P+N) pass through the core-balance CT (CBCT) which vectorially sums up all the currents, including any unbalance currents. The relay will not trip for any unbalance, only for any current flowing outside the CBCT, which can only be an earth leakage/fault. What you are saying here is different...maybe things are different in MV/HV ? Not that i think so....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#8
In reply to #7

Re: VCB Tripping

05/16/2011 9:34 AM

Dear kvsridhar,

What you have told in case of CBCT is absolutely true. I have indicated that in case of Earth fault relay is residually connected in the CT secondary circuits, in case of high line unbalance currents, zero sequence component of unbalance current may flow thru E/F element and if that amount exceeds threshold value(pick-up value) E/F relay may operate.

__________________
Manindra
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: VCB Tripping

05/16/2011 9:43 AM

Ah, ok. i think i get it. Thanks.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member

Join Date: Sep 2009
Location: BH, Vietnam
Posts: 435
Good Answers: 1
#10
In reply to #5

Re: VCB Tripping

05/16/2011 9:50 PM

Additional to manindra:

1. What is the parameter shown at the point where the trip occurs?

2. What is the setting range?

3. What is the type of earthing protection scheme?

4. What is full load current?

__________________
Anything that can go wrong, will go wrong
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: VCB Tripping

05/16/2011 8:51 AM

What's so difficult about eliminating the earth fault that is causing the trip?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

hien.nguyenquoc (1); kvsridhar (3); manindra (2); NUKALA (1); PWSlack (1); ramvinod (1); TonyS (1)