What factors iconsider in generator sizing
Re: Generator sizing
05/16/2011 5:56 AM
For what load?
Like this?
Like this?
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member
05/16/2011 9:56 PM
Voltage? Phase?
Anything that can go wrong, will go wrong
05/17/2011 7:43 AM
starting current 400Ampere/phase
operating current 250Ampere/phase
Good Answers: 5
05/17/2011 11:22 AM
Generator capacity has two components,kW and kVA or pf. During starting pf will be low
but current high. During running current and pf are known.If you measure the voltage and pf during running as well as during starting you can calculate kW of engine as well as kVA of alternator.
pnaban
Good Answers: 5
Re: Generator Sizing
05/17/2011 5:37 AM
You should take into account the total connected load,diversity,load characteristic etc
pnaban