Parking Drainage

05/18/2011 11:59 PM

We are working on a design for drainage from a 3 story enclosed Parking Garage -location NYC. The second and third floor are used only as storage /parking.

There are some maintenance area on the first floor. We are providing oil/water separator w/ capacity as per NYC PC 1 cu ft for ea 100 sq ft only for the drainage from the first floor maintenance. As per NYC PC areas used for storage of automobiles are not required to drain thru separator.

My question is - to what system we should drain the upper two floors ?

The only drainage system we have thru the upper two floors are the storm leaders from the roof (roof is not used for parking). I would prefer to connect the floor drains from the parking areas to the storm system - based on the thought that the parking area drainage system will convey clean water , no different than an open parking structure.

I know that there are different approaches - some connect to the storm, some to the sanitary.

I'll appreciate any advices and any references that can be used to support my approach - draining the parking areas to the storm water system.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: PARKING DRAINAGE

05/19/2011 12:07 AM

If it is an enclosed garage, how would significant amounts of water accumulate on the parking floors? For small amounts of water, there might be oil contamination from vehicle drippage, so why not convey it to the first-floor oil/water separator? (Perhaps upsizing it.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
3
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#2

Re: Parking Drainage

05/19/2011 11:20 AM

I whole-heartedly agree with Tornado, as any motor oil or antifreeze dripping from vehicles should be treated before discharge to the NYC storm drain system. Remember that most of the city's drain system could direct discharge to receiving waters such as the Hudson R. or East R..

I don't know how far the city has progressed in separation of the sanitary/storm combined sewers. There is potential that if they have completed the separations (or a good amount) then there is an equally stronger possibility that NO wastewater treatment plant resides between your building and the receiving waters, therefore allowing direct discharge of contaminated water to th river.

Are you the Contractor, the Engineer of Record or the Architect? Also, have the plans been reviewed by the City? Are any permits been issued by the City for this project thus far, particularly discharge permits? Too many questions and not enough info given....

Finally, you should be asking this question to the NYCDEP, the NYC Building Dept. and/or the NYC City Engineer's Office, not here.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply Good Answer (Score 3)
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#3
In reply to #2

Re: Parking Drainage

05/19/2011 12:10 PM

I gave you a GA for that one.

In my experience, when I have questions like that, and present them in an "I want to do the right thing, but I'm not exactly sure what it is. Please help." way to the regulatory agencies they're generally very helpful in providing guidance.

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Register to Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#4

Re: Parking Drainage

05/19/2011 12:35 PM

Thanks CI!

Believe it or not, even the NYCDEP can be helpful regarding intepetation of the NYC, NYSDEC and USEPA regulations......well, most of the time!

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
Participant

Join Date: May 2011
Posts: 2
#5

Re: Parking Drainage

05/19/2011 11:08 PM

The responde of the autority was a copy of the page of the NYCPC - 1003.4.2.2 Garages and service stations. Where automobiles are serviced, greased, repaired or washed or where gasoline is dispensed, oil separators shall have a minimum capacity of 6 cubic feet (0.17 m3) for the first 100 square feet (9.3 m2) of area to be drained, plus 1 cubic foot (0.028 m3) for each additional 100 square feet (9.3 m2) of area to be drained into the separator. Parking garages in which servicing, repairing or washing is not conducted, and in which gasoline is not dispensed, shall not require a separator. Areas of commercial garages utilized only for storage of automobiles are not required to be drained through a separator.

No any additional requirments above the code.

So based on the last sentence above we desided not to drain the the upper floors thru the OI.

Any thoughts?

Thanks

Register to Reply
Guru
Engineering Fields - Construction Engineering - New Member Engineering Fields - Civil Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member Popular Science - Weaponology - New Member United States - Member - New Member Hobbies - DIY Welding - New Member

Join Date: Apr 2007
Location: Latitude 38.701979 Longitude -90.439540 Coordinates 38.701979, -90.439540 N38°42.11874, W090°26.3724
Posts: 668
Good Answers: 15
#6
In reply to #5

Re: Parking Drainage

05/20/2011 5:13 AM

I'd go ahead and run the other floors thru your separator. You probably won't need to enlarge it any since there really wont be any additional run off. But if you are buying a manufactured separator and really want to play it safe go up to the next larger size & you shouldn't ever have to worry about over capacity.

This is also assuming that it isn't cost prohibitive to run the other floors to the separator.

__________________
scotchdrnkr
Register to Reply
Guru
Engineering Fields - Civil Engineering - Member

Join Date: Mar 2011
Location: ''but, don't we get PAID to ask questions?...''
Posts: 1661
Good Answers: 17
#7

Re: Parking Drainage

05/20/2011 10:53 PM

Hmmmm, 3 stories for parking, maintenance, and storage, hopefully very well enclosed, presumeably all above ground, in New York City (?)... Sounds like a relatively suburban location, as opposed to a high-rise area(?) of what size foot-print?

Ok, in any case, there could still occur a vehicle fire, and probably will eventually occur a storage fire, or an electrical/utility fire, of some kind, from any number of unlikely combinations of circumstances, simply because, given enough time, some kind of fire will eventually start somehow, from natural or unnatural, causes...

Therefore, there will need to be a fire-suppression system installed and/or an eventual need to get a firefighting crew inside to fight the inevitable fire. In any case, fighting such a fire, by whichever means, will also result in some degree of flooding.

So, since fire fighting equipment will probably have difficulty accessing such a fire event on the second or third floor, due to typically low over-head clearances and tight turning radii, in such garages, it would be a good idea to provide for a firehose to be quickly passed up between each of the up/down ramps, or some equivalent alternative, so said fire can relatively quickly (addressed) before too much collateral damage is done to what ever materials are happen to be there at the time...

Thus, it would seem to be logical to suggest that a second oil/water/separator be installed inside or outside of the structure to exclusively handle the flash-type flooding of fighting an upper-story fire. Depending on the details of the circumstances, it could drain entirely separately from the first floor separator...

The main point is to include the relatively elaborate features such as those mentioned above, in the construction drawings/contract/cost-estimate/etc. early-on, and let the plan-checkers, bean-counters, posturing-politicians, etc., remove, in writing or public speechifying, such (extra) safe-guards as suggested above, in anticipation of their finger-pointing in the future...

Thus, they can boast how much money they "saved" the public, only in the short-run, and you will be better insulated from such (blamers), in the long-run, when it comes time for them to find some one other than themselves to blame when the fire finally does happen...

__________________
''illigitimi non carborundum...''(i.e.: don't let the fatherless (self-deluding,sabotaging, long-term-memory-impaired, knee-jerking, cheap-shotting, mono-syllabic, self-annointed, shadow-lurking, back-biting, off-topic-inquisitors) grind you down...)
Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: