Fire Dampers

05/22/2011 11:36 AM

Some small ducts (6 x 6 inches) going through fire rated walls in our building have been provided with Fire Dampers but without Access Doors. Is it a must to provide access doors for each fire damper regardless of its small size?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Fire Dampers

05/22/2011 12:03 PM

Do you suspect that the building was not built to code, or just curious?

Register to Reply
Associate

Join Date: May 2011
Posts: 30
#2
In reply to #1

Re: Fire Dampers

05/22/2011 3:12 PM

The fact that there are fire dampers indicates that the codes are certainly involved. The argument being advanced against providing access doors in very small ducts is that the small access would not allow the two hands to go inside to manipulate the fusible link of the curtain type damper, so what's the function of providing one.

Thanks

Register to Reply
Participant

Join Date: Feb 2011
Posts: 2
#9
In reply to #2

Re: Fire Dampers

05/27/2011 9:26 PM

It is not practical to have Access doors in such small ducts for the above reasons, though code requires access doors where Fire dampers are required.

__________________
rkumar@dsny.nyc.gov
Register to Reply
Associate

Join Date: May 2011
Posts: 30
#10
In reply to #9

Re: Fire Dampers

05/29/2011 9:04 AM

This would leave one in the lurch as your response is yes and no at the same time. A definite verdict is what is required, whether access doors must be installed even though, functionally speaking, one would not have any physical maneuvarability due to their size other than being able to know visually whether it was open or shut. Another question that stems from the first question is that once the damper was installed in the open position and the fusible link was intact, is there any possibility or event that would release the link besides a fire??

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#3

Re: Fire Dampers

05/22/2011 6:19 PM

You need to check the code for access requirements or contact the fire marshal.

__________________
Mr.Ron from South Ms.
Register to Reply
Associate

Join Date: May 2011
Posts: 30
#4
In reply to #3

Re: Fire Dampers

05/22/2011 10:59 PM

Still waiting for an informed opinion about the requirement of the codes (not just city or local codes) in the matter of Access Doors for very small duct sizes

Register to Reply
Active Contributor

Join Date: Feb 2011
Location: GTA Canada
Posts: 15
Good Answers: 2
#5

Re: Fire Dampers

05/22/2011 11:22 PM

Per the International Mechanical Code, section 607.4 and the International Building Code, section 716.4 all fire dampers installed are required to have access panels installed, clearly labled "FIRE DAMPER" OR "SMOKE DAMPER".

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#6

Re: Fire Dampers

05/23/2011 10:06 AM

If it moves, it needs to be accessible.

Register to Reply
Associate

Join Date: May 2011
Posts: 30
#8
In reply to #6

Re: Fire Dampers

05/24/2011 3:11 PM

I am with you on this one from head to toe, but the arguments being advanced against it are that the teeny weeny access door would not allow the fusible link to be relatched, so what's the point?

My argument has been that the access door would at least allow access to our vision about the open or close status of the damper

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#7

Re: Fire Dampers

05/23/2011 11:57 AM

Absolutely! Lou Bindner

Register to Reply
Register to Reply 10 comments