Condensate Drain Piping Of Fan Coil Units

05/22/2011 11:39 AM

The condensate drain piping collects the condensate of about 5 fan coil units mounted above the false ceiling. It is not always possible to give the desired 1 % slope to the pipes due to many obstructions in the pipe path. Since the fan coil unit's drain pan is at a higher level and the water will definitely flow, can the absence of desired slope or at some place the opposite slope be ignored?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: condensate drain piping of fan coil units

05/22/2011 11:45 AM

Yes, if you can tolerate standing water in the tube.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#2

Re: Condensate Drain Piping Of Fan Coil Units

05/22/2011 6:16 PM

This would be a good example of faulty engineering. On a ship, it could be tolerated because the ship moves, but not in a building.

__________________
Mr.Ron from South Ms.
Register to Reply
Associate

Join Date: May 2011
Posts: 30
#3
In reply to #2

Re: Condensate Drain Piping Of Fan Coil Units

05/22/2011 10:56 PM

The function would be achieved in both the ship and the building, viz. that gravity will make the water flow as long as the FCU drain pan is higher than the rest of the pipes. Unlike soil pipes, the concern here is not to have a slope to result in scouring velocity in pipes.

Register to Reply
2
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#4

Re: Condensate Drain Piping Of Fan Coil Units

05/22/2011 11:09 PM

You would have to provide much more information to determine the answer. In almost all cases similar to what you are describing the solution is to install a condensate pump on the drain pan drain to pump the condensate up and/or across to a location where it can be transferred to an appropriate drain. This can range from a 5 gal/hour $50 small pump up to extremely large and expensive units.

The pump is basically similar to a sump pump within a small and appropriate sized container which collects the water. The discharge from the pump is connected to a hose/pipe/tubing which discharges into a drain. A float switch or some other type of switch then controls the pump.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Good Answer (Score 2)
Associate

Join Date: May 2011
Posts: 30
#7
In reply to #4

Re: Condensate Drain Piping Of Fan Coil Units

05/24/2011 3:14 PM

The only additional information I have is that the specs call for the condensate pipes running inside the masonry walls of the toilets en route their eventual connection to the floor gulleys to be also insulated. I wonder what is the point of insulating this portion of the pipe that might just cool the wall a bit but the condensate on the ceramics if any would not be a major concern nor an eye sore?

Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#5

Re: Condensate Drain Piping Of Fan Coil Units

05/23/2011 3:35 AM

The 1° slope is to prevent water from accumulating in the pipe, and freezing in cold weather thus bursting the pipe. If the pipe sections involved are indoors and will never freeze, you don't have a problem. If not, live with the potential leaks, or trace heat the pipe.

Register to Reply Score 1 for Good Answer
Associate

Join Date: May 2011
Posts: 30
#6
In reply to #5

Re: Condensate Drain Piping Of Fan Coil Units

05/23/2011 4:08 AM

I hope your verdict enjoys majority consensus namely that the slope can be omitted due to pressing circumstances as long as the pipe is not exposed to the elements.

Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

786verycool (3); jhhassociates (1); lyn (1); old salt (1); ronseto (1)

Previous in Forum: Fire Dampers   Next in Forum: Efficiency of a Chiller

Advertisement