Open Circuited Secondary Current Transformer

05/22/2011 6:48 PM

Onboard our vessel we have six generators. We have had issues with CTs burning up. I found that there was a wiring mistake and one of the CTs on each generator wasn't connected (open circuited). I thought that an open circuit CT would cause saturation and burn itself up? Why didn't all of the CTs that weren't connected burn up? We have had three fail over the past few months, they have all been while underway, quite large load on each generator. I would have thought that the open CT would have failed within a matter of minutes/hours not weeks/months?

Register to Reply
Pathfinder Tags: ct Current Transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#1

Re: Open Circuited Secondary Current Transformer

05/22/2011 11:36 PM

It is simple knowledge that if secondary of CT when not connected with a meter must be shorted other wise it may develop very high voltage and and is dangerous . So check up your wiring throughly to short circuit the non connected CTs. For a better consuptual knowledge about the subject read the link below.

http://www.eng-tips.com/faqs.cfm?fid=1189

Register to Reply Score 1 for Off Topic
Participant

Join Date: May 2011
Posts: 4
#2
In reply to #1

Re: Open Circuited Secondary Current Transformer

05/23/2011 5:34 AM

My question is why didnt all six of the disconected CTs burn up when open circuited, they were in service for roughly 12 months? we have already found the wiring mistake and corrected it.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Open Circuited Secondary Current Transformer

05/23/2011 8:50 AM

Luck.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Participant

Join Date: May 2011
Posts: 4
#4
In reply to #3

Re: Open Circuited Secondary Current Transformer

05/23/2011 4:20 PM

Come on guru that's not much of an answer. There has to be someone out there smart enough to give me some kind of logical answer. These generators have all run for about 12 months now, each generator with one CT open circuited. The gens are all connected to a common 11KV bus, and load share equally. We have had three CTs blow in the past 3 months (prior to finding the incorrect wiring). First failure was on gen #6 while on transit departing the shipyard, we had it replaced under warrantee in Singapore. Few months later, we finaly departed Singapore and while on transit once again gen #6, same CT. Week later, still on transit gen #2.

With the secondary winding open on a CT we know that extremely high voltages will be produced. Would the CT be in constant saturation too? Why didn't all of the opened CTs fail? And why didn't they fail sooner?

It seems that the CTs are only failing while under transit, this is when the generators are loaded the greatest. The thing is they all share the same load.

Register to Reply
3
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#5
In reply to #4

Re: Open Circuited Secondary Current Transformer

05/23/2011 10:56 PM

It's a testimony to the quality of the secondary insulation that they didn't fail immediately. I guess over time the insulatikon deteriorated until it finally failed.

Out of curiosity - if they weren't originally connected how did you know they had failed?

Later edit: I think I see the answer to that - smell and smoke!

__________________
johny451
Register to Reply Good Answer (Score 3)
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#6
In reply to #4

Re: Open Circuited Secondary Current Transformer

05/24/2011 12:14 AM

Though the other CTs haven't visibly failed yet, I guess the insulation must have considerably deteriorated to cause trouble any time.

Hence, better to remove /replace the other three CTs also so as to minimise the problem while generators are running / ship is in transit.

For your question why these haven't failed yet, the answer can only be that - though the insulation is identical in all the CTs, there is bound to be some inherent differences in failure pattern due to many factors that are internal to CT manufacture as well as ambient conditions. Most likely, it is a matter of a few more days that these CTs to showup visible damage.

__________________
Raghunath
Register to Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#11
In reply to #4

Re: Open Circuited Secondary Current Transformer

05/24/2011 6:13 AM

The open circuited CTs would have certainly failed instantaneously in the event of occurence of any current based faults.Perhaps such faults have not occured in your case.

The voltages developed across the open circuited CTs during the normal operation were perhaps not enough to burst them instantaneously.However, the stress due to higher voltages have led to gradual deterioration of the insulation.Hence,the delay in failure of some of the CTs.The other ones,which have survived,must have lost considerable part of their life span.

__________________
Learning is a never-ending process.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Open Circuited Secondary Current Transformer

05/24/2011 2:10 AM

Out of interest have you shorted the other CT's yet? I would have thought it would be a matter of high priority to you to prevent further failures.

I wouldn't like to be on a ship knowing there's a fault lurking about waiting to bite me.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
2
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#8

Re: Open Circuited Secondary Current Transformer

05/24/2011 4:23 AM

Adam,

The newer CT's are very forgiving by design. Originally CT's had plenty of Iron core and lower quality design features, such as closer terminal separation and poorer quality insulation.

Newer CT's have just enough iron core to function accurately at rated amp ranges, above that the cores saturate, reducing the power that can be developed.

As in any transformer (and in most respects these are like any other transformer) leakage through the insulation will eventually build a path that will conduct enough current and thereby heat damage to the insulation.

Think of the effect of an open-circuit CT as a long 'megger' test. There will be some conduction through the insulation if the voltage is significantly above it's rating. Factors that will cause one CT to fail while it's neighbor does not (yet) are mainly ambient temperature, proximity to something hot etc, and insulation impurities or minor construction details of the individual CT's. The gap between the open shunting device may have been different on the different CT's, or moisture tracking was not equal.

Also, the greater the current flow through the primary, the higher the voltage will rise (theoretically to infinity) by ohms law. An un-loaded open CT is not a problem, but a heavily loaded open one is highly unstable.

The more important thing is to shunt them properly now that you know of the issue.

If I had to guess, I would presume these are not for metering but for protective device operation, which leads to the obvious concern that your protective circuitry was not properly functional either, a bit higher concern than an open CT.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply Good Answer (Score 2)
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#9

Re: Open Circuited Secondary Current Transformer

05/24/2011 5:36 AM

I'm a bit confused here: why didn't anyone notice that none of the metres were registering any current?

Or have I got the wrong end of the stick? (again)

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: Open Circuited Secondary Current Transformer

05/24/2011 6:00 AM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: May 2011
Posts: 4
#12

Re: Open Circuited Secondary Current Transformer

05/24/2011 3:46 PM

Good question Johny451, if they weren't connected how did we know that they had failed?

The reason we didn't pick up on the CT not outputting was because it wasn't used for metering purposes. There are three on each generator. One around each phase, one leg of each of the three CTs was tied together to create a star configuration. The remaining three legs are rectified and sent to the AVR as a Booster to help produce the excitation current. With the missing phase the AVR would have still received a DC to help with the excitation but it would have been messy DC.

When the CT burnt up it would also burn up our AVR, I'm not sure exactly how this would happen either? If anyone has ideas on that would love to hear them too.

Sorry about the small picts its the best I could paste them into this text box.

Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#13
In reply to #12

Re: Open Circuited Secondary Current Transformer

05/25/2011 8:34 AM

Adam, well Most of our friends have clarified that what might be the reason, why other CTs were not failed.

As per Mr. Raghun, It would be better to replace all other CTs to reduce interruption and failure in future. It would be possible that they may fail one after another and put your system in nuisance.

__________________
Sure Answers Always
Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#14
In reply to #12

Re: Open Circuited Secondary Current Transformer

05/11/2014 6:04 PM

This is in reply to your secondary question about the AVR damage.

A CT failure doesn't always mean that the secondary becomes involved directly with the primary, simply that it develops an extremely high secondary voltage that damages the CT. If the CT faults in a way that connects the secondary with the primary however, your AVR will see the primary phase directly. Whereas it had been receiving relatively low DC secondary current rectified from a secondary side varying voltage of approximately 0 - 12 volts AC, I'd think that a sudden connection directly to the primary voltage would take out the rectification and hit the AVR with AC line-ground fault-value currents.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: