Continuity testing

05/24/2011 4:20 PM

What is the recommended test voltage to be applied when carrying out a continuity test of protective conductors of a wiring installation.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#1

Re: Continuity testing

05/24/2011 10:00 PM

According to IS:732(Part III)-1982

The DC(a battery) test voltage is unknown but the procedure is to measure the earth terminal and farthest installation terminal so that the ohm-meter should not read more than 1 ohm.

If the installation is large each sub-circuit should be measured separately.

Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#2

Re: Continuity testing

05/25/2011 6:58 AM

I am Agree with Our Friend Hithuanand, For conticuity testing not required to know the value DC voltage of Ohm-meter.

There is no any recommended test voltage for carrying out a continuity test of protective conductors of a wiring installation.

As per IS 732-1989, Clause 12.3.3, Every protective conductor shall be seperately tested to verify that it is electrically sound.

For insulation resistance measurement of protective conductor, the test voltage shall be:

For extra Low voltage Circuits - Up to 250-500V

For 250-500 V Circuits - 1000V

For Circuits above 500V - 2.5KV

Vinu_Answers Sure Answers

__________________
Sure Answers Always
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Continuity testing

05/25/2011 7:57 AM

By definition, continuity testing requires the passing of a current to prove the continuity of the conductors.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856