How Can I Choose the Wires for Surge Arrester

05/24/2011 11:21 PM

Dear Friends.

I am assembling a low voltage distribution cabinet (indoor) for my workshop. But, i don't see any document that guide to choose the section of wire for low voltage surge arrester.

Any body has any idea about this business please help me.

Thank you so much

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: How can i choose the wise for surge arrester

05/25/2011 1:18 AM

....wire for low voltage surge arrester....

Do you mean fuse-wire? For arresting current surge ? This is not a normal usage of the terms, perhaps English is not your native language ?

If you mean a voltage surge, you would need to use a Varistor, or an RC network or something.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Dec 2008
Location: Ha Noi - Viet Nam
Posts: 20
#2
In reply to #1

Re: How can i choose the wise for surge arrester

05/25/2011 3:16 AM

Firstly, I thank you so much for your responce and sorry for my bad English. You are true, vietnamese is the my native language.

In this case, i want to mention in section of the wire that connects between the busbar phase and terminal of surge arrester.

Thank you so much.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: How can i choose the wise for surge arrester

05/25/2011 4:48 AM

Well, English isn't my native tongue either, so please do not misunderstand whatever i may say.

This surge arrestor that you mention .. who is the manufacturer, is there a model number, any details that you can give would be helpful. i assume you are having a surge arrestor to absorb voltage surges, yes?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#5
In reply to #3

Re: How can i choose the wise for surge arrester

05/25/2011 7:18 AM

There are various manufactures of Low voltage Surge Arrestors and also variety of model numbers. I am mentioning one manufacturer and Model no - Baleastro, PBT-175G, PBT-280G, PBT-500G, PBT-750G and PBT-1000G.

Vinu_Answers Sure Answers

__________________
Sure Answers Always
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: How can i choose the wise for surge arrester

05/25/2011 8:23 AM

There are literally millions - Elpro, Epcos, ..... (incidentally, Google doesn't recognise "Baleastro" .. is the spelling right?)

That is not the OP's question. He/she hasn't even confirmed that it is a voltage-surge-arrestor.....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: How can i choose the wise for surge arrester

05/25/2011 6:55 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#7

Re: How Can I Choose the Wires for Surge Arrester

05/25/2011 9:14 AM

The surge arrester is connected between your voltage conductors (bus) and ground, to direct surges such as lightning strikes to ground rather than through your electrical loads. The cables that connect the surge arrester to your system have to be sized to handle that short-time surge current without melting or other thermal damage.

If you know what the possible current will be, then IEEE Std 80-2000 can help you in choosing a conductor size. The tables in section 11.3.2.2 give current ratings of various size conductors at a range of levels of current and duration of time. Since it can be difficult to know the expected value of surge current, many people choose either to size the cable very conservatively (such as #4/0AWG or 100 mm^2), or else will size it per the maximum fault current rating of the system, by which point your overcurrent devices should have tripped. This will probably results in a much larger cable then is really needed.

However, I would expect the surge arrester manufacturer to recommend a cable size to coordinate with the capability of the arrester. Have you checked that? I found the following on a quick Google search on "surge arrester cables" which tells what Schneider Electric uses in their switchgear:

http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=content&country=US&lang=EN&id=FA130961&redirect=true

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#8

Re: How Can I Choose the Wires for Surge Arrester

05/26/2011 1:09 AM

Consider the surge current, for the arrester you are installing in the cabinet, as a guide to choosing the wire section.

For human safety reasons the voltage drop between the cabinet and ground must be lower than 50V as far as I remember so you can also consider this factor in choosing wire section.

__________________
The time is ......now
Register to Reply
Participant

Join Date: May 2011
Posts: 2
#9

Re: How Can I Choose the Wires for Surge Arrester

05/26/2011 3:38 AM

The surge arrester should protect the panel & all cables / circuits coming into the panel from the outside and all circuits leaving the panel to an external source outside of the building.

The Furse & Dehn lightning protection products have a section that will assist with selecting a SPD that suits your requirements.

Regards

Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#10

Re: How Can I Choose the Wires for Surge Arrester

05/26/2011 9:01 AM

I couldn't pick a post to reply to, so I'm posting to the OP.

I'm a little confused even if no one else is ;-)

The surge arrestor we're talking about here is not generally intended to handle a full lightning stroke. Lightning arrestors somewhere outside the building, are intended to handle those.

This device is aimed at smaller surges that might be the result of a lightning stroke already "arrested" outside the building (but that doesn't level the surge completely), or noise, spikes, surges generated by devices in the workshop.

As such, surely it doesn't need anything like a 4/0 cable. Consider the surge arrestor for something like a PC. It just uses the ground cable in the cable to the device to bleed off the surge. Typically, if you have a cord of #16 wire, the ground wire is also #16.

I'd get the information from the manufacturer, but I'd expect to use a fairly small conductor from the protected bus to the surge device, and from the surge device to ground. Something on the order of the size of the cables feeding the loads from that panel, maybe even smaller.

(What I'm trying to say here is that, for example, 10 loads are each being fed by a #14 feeder (15 amps each), I wouldn't expect to have to use a cable to the surge device and then to ground capable of handling 150 amps. But, I could be wrong.)

But, like I say, see what the manufacturer recommends / requires.

Register to Reply
Participant

Join Date: May 2011
Posts: 2
#11
In reply to #10

Re: How Can I Choose the Wires for Surge Arrester

05/26/2011 10:45 AM

I would refer to the comments from PeterT.

Regards

Register to Reply