Previous in Forum: Timer Switch for a Kite Camera   Next in Forum: Bus Bar Size
Mv Motor Cable Size
05/27/2011 11:16 AM
my friends
how can i calculate cable size of 5.5kv, 250kw motor for 200 meter.
please help
take care, have a nice life
necmettin sengun
Pathfinder Tags: mv motor cable size
Re: Mv Motor Cable Size
05/27/2011 11:33 AM
You don't calculate this cable size. You look up the required cable size by your wiring standards for your location.
05/27/2011 11:34 AM
British Standard 7671.
Re: mv motor cable size
05/27/2011 11:37 AM
Dear,
MV Cable is selected on
1. Short circuit current capacity - Calculate the system fault levels , say 3.5 KA
Then, Minimum 25 sq mm cable required.
2. Current Rating - Mfr. data sheet - Ir(25Amp)*derating factors ( App. 0.65) >38Amp
Then, Minimum 6 sq mm Aluminium cable required
3. Volt Drops permitted , say 3% of 5.5 KV - 165 Volts
Volt Drop DV = 1.732*IL * (R*L / 1000)
_________________ =
power factor
= 1.732*25*1.54*200/1000
____________________ = 14.8 V
0.9
Whichever size is higher shall be selected. So, select 25 sq mm minimum for 250 KW motor. @ 5.5 KV
Exploring the Science of Electricity
05/27/2011 1:38 PM
Do you really think that the only criteria for a power distribution cable is the voltage drop at full load? Sigh.
Good Answers: 181
05/27/2011 1:09 PM
We could calculate the required cable size, but then you run in to a problem. Finding a cable manufacturer that produces a 10mm cable rated at 6.6KV.
Look at things practically, look at cable specifications. You have to choose the nearest that suits the situation.
Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Construction Engineering - New Member
05/27/2011 9:49 PM
Look at the book, look at the calculation method they teach. Don't be too stingy.
Anything that can go wrong, will go wrong