Cable Voltage Drop Calculation

06/15/2011 11:19 AM

As experts and designers knows that, in cable voltage drop calculation we consider only real part of complete equation i.e. ( I.R.cos (fi) +I.X.sin (fi) ). we are assuming imaginary part of this equation as negligible hence not to consider. Pl. note due to addition of this imaginary part cable size for standard run lengths say 250 mtr. increases. In my openion, in comparison with conventional formula and it's application as standard practice in industry, this new complete equation un-necessarily increases cable size in turn cable cost...moreover wastage of national resources, probably. Whether, it is feasible and techno- commercially right practice to consider complete equation with its imaginary part also? When to use and when not to use this imaginary part?

__________________
Engineering is an APPLICATION..
Register to Reply
Pathfinder Tags: Cable voltage drop
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Cable Voltage Drop Calculation

06/15/2011 11:23 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Cable Voltage Drop Calculation

06/15/2011 10:56 PM

The angle in question is usually denoted by the Greek letter phi (φ). Depending on your browser, the composing window for CR4 posts includes a special symbol menu, shown by Ω in the tool bar. Selecting this menu allows you to insert such symbols as ©, ≥, ÷, √, →, ¿, and other useful items. Similarly, the x2 and x2 features allow you to insert subscripts (e.g., H2O), and superscripts (e.g., πr2).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Feb 2011
Location: Pune, Maharashtra, India
Posts: 32
Good Answers: 2
#3
In reply to #2

Re: Cable Voltage Drop Calculation

06/15/2011 11:13 PM

My friend! Thanks for your reply but unfortunately this is not answer to my main question. Requested to involve if someone knows correct answer. Pl. note I stated this discussion only for knowledegous elect. Engineers for their expert sharings and not for MS world format editors or English teachers who will just increase their number of posts in forum!!

__________________
Engineering is an APPLICATION..
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Cable Voltage Drop Calculation

06/15/2011 11:50 PM

Welcome aboard. Surely you will enjoy yourself here.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 3)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #4

Re: Cable Voltage Drop Calculation

06/16/2011 12:04 AM

Geese Tornado... I guess you were told. Some people's kids!

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Off Topic (Score 3)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: Cable Voltage Drop Calculation

06/16/2011 12:48 AM

Somehow I thought the OP's formula was supposed to have an imaginary part. Too bad I am not a "knowledegous" EE, but as a mere "English teacher" I hazard this guess:

IR cosφ + iIX sinφ.

I haven't yet seen a Code that uses this formula for computing voltage drop, however.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 3)
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#7

Re: Cable Voltage Drop Calculation

06/16/2011 2:16 AM

As long as the comsumer gets the voltage within the 10% range you can calculate the voltage drop as you wish. Try both ways and see which one gets the lowest value. Use that one for dimensioning the cable.

__________________
The time is ......now
Register to Reply Score 2 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: Cable Voltage Drop Calculation

06/16/2011 4:28 AM

Salunkhem, if you can't take the banter that goes on between engineers I would suggest you close the door behind you when you leave.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Off Topic (Score 3)
Anonymous Poster #1
#9

Re: Cable Voltage Drop Calculation

06/16/2011 8:43 AM

I am not a cable designer, only humble EE. But I don't think the formulae that you gave is correct.

V = IRCosφ + IX Sinφ

The voltage drop is

V = IZ = (ICosφ1+jISinφ1) (R+jX)

(Though Finally if you simplify it to the modulus (non phasor values) and it may simplify to something like

V = IZ(Cos(φ12) + jSin(φ12)) = |IZ|

This is what must be taken for the drop calculation. As far as I know the cable ratings and calculations are dependent on load current (and thus it does take care of the powerfactor of I) and then there are some standard multipliers (must be for the cable reactance).

But again it is IMHO since I do not indulge in cables.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#10

Re: Cable Voltage Drop Calculation

07/14/2011 9:32 PM

This thread (especially the comment #12 and #14) may be related to the discussion: http://cr4.globalspec.com/thread/65251/Voltage-Drop-Calculation-for-Single-Phase

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)