Galvanic corrosion

07/03/2011 8:28 PM

This question relates to ships connected to shore power. Could you guys tell me the effect in terms of galvanic corrosion of a 4 wire generator neutral connected to a ground neutral bus would have?

__________________
Thank you for your help - By far the best info site!
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Location: Deepest Darkest Rutherford Oz
Posts: 951
Good Answers: 145
#1

Re: Galvanic corrosion

07/03/2011 9:54 PM

Galvanic corrossion in boats/ships occurs because of the voltages created by the dissimilar metals of props, rudders, shafts soaking in an electrolyte, with the "earth" return of the shore power completing the circuit.

The trick is to break the earth return by using a galvanic earth isolator. These are readily available commercially.

As for your situation using a gen set, it may not be an issue if the genset is not grounded on shore. However best practice is to use a galvanic isolator.

__________________
There are two reasons for a man to do a thing, One that sounds good, and the real one...
Register to Reply
Power-User

Join Date: Sep 2009
Location: Houston, TX
Posts: 118
#2
In reply to #1

Re: Galvanic corrosion

07/03/2011 11:33 PM

Thanks for your input. Galvanic action is certainlycaused by dismilar metals, generator windings being more noble than an aluminum hull. I know about galvanic isolators but the regulations that I deal with require a gen. neutral disconnect for the purpose of meggering. BV is a regulatory body that mentioned that the neutral (grounded), be disconnected when on shore power. My thoughts are that the generator windings may induce galvanic current?

__________________
Thank you for your help - By far the best info site!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Galvanic corrosion

07/04/2011 4:04 AM

It is difficult to see what effect it would have.

Galvanic protection is applied to metal parts immersed in water. Google "sactificial anode" for more information.

Connection of shore-based supplies to a boat is covered in British Standard 7671. Equipment installed wholly within the vessel falls outside the standard.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#4

Re: Galvanic corrosion

07/05/2011 10:50 AM

Most U.S. Navy pierside power connections use 3-p delta to avoid that very problem (imbalanced phases causing current flow on the neutral and potentially through the ships hull to utility ground on shore). Ship's hull is not used as a return path for power and a separate conductor is used for safety ground isolated from the power systems and ideally only connected to the hull at a single point. (Easier said than done, but that's the goal anyways.)

You might want to start with MIL-STD-1310, Standard Practice for Shipboard Bonding, Grounding, and Other Techniques for Electromagnetic Compatability and Safety. Also be sure to look at MIL-STD-1399, Section 300, Electric Power, Alternating Current and MIL-STD-2003, Electric Plant Installation, Standard Methods for Surface Ships and Submarines.

You can access these mil-specs at http://dodssp.daps.dla.mil/

Good luck with your quest.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2011
Posts: 22
Good Answers: 1
#5

Re: Galvanic corrosion

07/05/2011 12:44 PM

If there is any current in the shore power neutral to ground there will be two parallel current paths. One the ground connection between the switchboard ground and the shore ground and the other the path from the hull through the water to the shore.

The path from the hull through the water will cause "stray current corrosion" NOT "galvanic corrosion". Stray current corrosion can cause hull pitting and loss of hull coating.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Sep 2009
Location: Houston, TX
Posts: 118
#6
In reply to #5

Re: Galvanic corrosion

07/05/2011 1:44 PM

Thanks John (even though I didn't know there was any difference) What my ghost is at this point is will a 4 wire generator, while stopped with it's neutral connected to the swbd ground bus and an aluminum vessel create "stray" or galvanic currents?

__________________
Thank you for your help - By far the best info site!
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 22
Good Answers: 1
#8
In reply to #6

Re: Galvanic corrosion

07/05/2011 8:51 PM

Yes, an aluminum vessel can be damaged by stray current or galvanic corrosion. If either condition exists it will be more damaging to an AL hull than a comparable steel hull.

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#7

Re: Galvanic corrosion

07/05/2011 2:11 PM

Who's bright idea was it to build a ship from what is usually a marine sacrificial anode? What are you using for the sacrificial anode and I hope you don't say aluminum.

I agree 100% with comments referring you to standards for shipboard grounding, bonding, etc. I also agree to "ground" the ship neutral at a single point.

Good luck.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Brave Sir Robin (1); James Stewart (1); John Gerke (2); jraubsr (2); PWSlack (1); Tobugrynbak (1)

Previous in Forum: RELAY SETTING SOFTWARE   Next in Forum: AGM Battery voltages

Advertisement