Silencer for Steam Safety Relief Valve

07/06/2011 11:42 PM

Hello

I am involved in designing a conditioner steam skid which is integrated by one three way valve using boiler feed water as tempering water. the maximum steam floe rate is 400 ton/hr, downstream of the three way valve is located two safety relief valves sized to handle 50% each of the total flow. The safety relief valve is 6 x 8", orifice Q, our customer is asking for a silencer located inmediatelly afetr the outlet nozle of the relief valve. My question is if the silencer must be sized to handle the full flow rate per each safety relief valve?. I mean 200 ton/h. if it is the case an keeping 85 dba at 3 meters the silencer is very big and expensive. is there any other criteria to define the flow rate to be handled at silencer?.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: silencer for steam safety relief valve

07/06/2011 11:56 PM

A silencer after a relief valve will introduce downstream pressure, which in turn may raise the upstream pressure to unsafe levels--unless the relief valve is a type that is mostly unresponsive to changes in downstream pressure. I urge careful investigation.

(Is "floe rate" measured in icebergs per hour?)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Jun 2011
Posts: 48
Good Answers: 1
#2

Re: silencer for steam safety relief valve

07/07/2011 2:07 AM

i would say practically you have to follow the design of the silencer to the expected flow and that is the 100% capacity.

however, do you expect that it will simultaneously open in case of upset/over pressure in the system, reason why they 50% capacity each? i doubt if it will, relief valves though carefully set and commissioned may not open simultaneous, there might be a difference of 1, 2 or more seconds and when this happens, pressure will eventually decrease and the other one need noot to open.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#3

Re: silencer for steam safety relief valve

07/07/2011 2:53 AM

A compact and very cheap way to ensure that the safety releif valves do not cause noise levels to exceed 85 dba at 3 meters would be to securely attach blind flanges to the discharge ports of the safety valves. If the noise limit is exceeded it will be brief and for reasons other than the safety valves.

If the customer wants the job done fast, cheap and right, tell him he must pick only two.

Register to Reply Score 1 for Off Topic
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#4
In reply to #3

Re: silencer for steam safety relief valve

07/07/2011 4:52 AM

That is so wrong

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #3

Re: silencer for steam safety relief valve

07/07/2011 7:06 AM

One hopes no CR4 reader is within earshot when it happens. It is so distressing when an ear is shot off....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jun 2011
Posts: 48
Good Answers: 1
#7
In reply to #6

Re: silencer for steam safety relief valve

07/08/2011 1:19 AM

i agree...hehehe..

Register to Reply
Power-User

Join Date: Dec 2010
Posts: 377
Good Answers: 20
#5

Re: silencer for steam safety relief valve

07/07/2011 6:43 AM

A silencer at down stream of a relief valve will introduce back pressure, which in turn will raise the upstream pressure to unsafe levels.Once silencer is considered, you should consider to change relief valves also to type suitable for Back pressure.

Register to Reply
Anonymous Poster #1
#11
In reply to #5

Re: silencer for steam safety relief valve

07/08/2011 3:26 AM

There seems to be an echo in the room. This sounds remarkably like an earlier post.

Register to Reply
Commentator

Join Date: Jun 2011
Posts: 77
Good Answers: 8
#8

Re: Silencer for Steam Safety Relief Valve

07/08/2011 2:14 AM

ASME Code does not allow any piping or fittings (or anything else for that matter) to restrict the safety valve flow. I believe Canadian and European codes are similar. I would think any type of silencer attached to a SV would need to be certified (just like a SV must be cert'd) before it could be installed. I suspect the Jurisdiction having Authority would also likely weigh in as well.

Rather then attach something to the SV or piping, I would consider some kind of sound attenuating apparatus (that does not restrict flow of course) that could be fitted around the release point. Alternatively, the relief flow could be piped to a location where dB's are not critical issue.

Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#9
In reply to #8

Re: Silencer for Steam Safety Relief Valve

07/08/2011 2:25 AM

"Alternatively, the relief flow could be piped to a location where dB's are not critical issue."

Suggestion

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #9

Re: Silencer for Steam Safety Relief Valve

07/08/2011 2:40 AM

How much back pressure does a calliope produce? Does it produce better noise?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#12
In reply to #10

Re: Silencer for Steam Safety Relief Valve

07/08/2011 4:07 AM

1 calliope ≈ 0.268974521256 Muses Urania - which may produce, via Apollo (or maybe Oeagrus), one each, Orpheus and Linus - not to be confused with Linus - as we are not talking Peanuts here - rendering the 'better noise' question mute.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Register to Reply 12 comments