Motor Star & Delta Connection

07/10/2011 2:09 AM

HI all........

I have a motor with all 6 terminals come out.how to identify the terminals if I have to connect it in delta or star type connection,if each coils has been identified?I read a lot of links in CR4 itself but no answer I got to my satisfaction.

Pls guide.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Motor star & delta connection

07/10/2011 2:29 AM

In one of the common "terminal board with jumpers" types:

Star:

O-O-O

OOO
| | |
L L L

Delta:

OOO
| | |
OOO
| | |
L L L

(Sorry about the weak formatting system here. O = motor terminal: L = line: - or | = jumper strip.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Jul 2011
Posts: 4
#2
In reply to #1

Re: Motor star & delta connection

07/10/2011 4:22 AM

Sorry I forgot to mention that there is no terminal wiring diagram on the motor.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Motor star & delta connection

07/10/2011 4:42 AM

What I gave was just one example I've seen. There may wire leads rather than a terminal block. If so, look for markings on the wires such as U1, U2, V1, V2, W1, and W2. Sometimes such markings are hard to see, but they may be there.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Jul 2011
Posts: 4
#4
In reply to #3

Re: Motor star & delta connection

07/10/2011 4:46 AM

No any other data available dear..........Isn't there any methods for identifying the starting & ending terminals?

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Motor Star & Delta Connection

07/10/2011 11:25 PM

The motor nameplate should give important data like connection(star or delta),voltage (single or dual),speed etc. If nameplate is not available ,consult a motor rewinding shop

to check the winding and give you guidance.

__________________
pnaban
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: Motor Star & Delta Connection

07/10/2011 11:49 PM

An ohmmeter can get you partly there; at least it will tell which wire or terminal pairs are connected to the same winding. But it won't tell you the direction or polarity. There was a CR4 thread about this, but I don't remember the title. This isn't much help, but maybe a start....

I suppose the voltage is a total guess, too?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
5
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7

Re: Motor Star & Delta Connection

07/11/2011 12:30 AM

Why does this question KEEP appearing?

So again here is the answer.. you did NOT search that well in CR4, as this is a reply I gave to the same question about a month ago.

You first find the winding ends using a continuity meter marking each winding end as "A" "AA", "B", "BB", "C" , "CC". use a 6 volt battery and a center zero galvanometer, connect the galvo to one pair and noting which ends are connected to the + and - of the meter, mark the winding ends as you have connected them to the meter.

Connect one of the other winding ends to one terminal of the battery and just touch the other end to the other terminal of the battery and note which way the needle of the meter moves, either to the left of the right, repeat until all the windings are done and with each test the meter needle moves in the same direction. This is called a "flick test" and if you leave the battery connected to the winding the meter will not move hence you only quickly touch the battery terminal with the winding end.

You now have found the correct polarity of all three windings, so you should have three ends with a +, and three with -. Make your star point from the three + ends and connect the other three ends to your supply.

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #7

Re: Motor Star & Delta Connection

07/11/2011 12:43 AM

That's the one I was thinking of; what was the thread's title?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#9
In reply to #8

Re: Motor Star & Delta Connection

07/11/2011 3:08 AM

Hi Tornado,

The thread you are referring to was 'Motor Wdg. Start and End Lead Identification' and the OP was 'cmaguna'. This was about a month or so ago and the replies should have answered virtually anybody's questions regarding this problem but there again, perhaps the old adage about 'history repeating itself' rings true again.

My advice to Hardworker2011 is (as suggested by another poster) to take the motor into a competant winding shop and then spend some time improving his search and reading skills. I am not trying to be insulting, dear, but just practical.

But perhaps this is just another homework question from a student who believes they have found an easy way to have someone else do their work?

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#11
In reply to #7

Re: Motor Star & Delta Connection

07/11/2011 3:54 AM

This the correct procedures for checking of continuity of coils, polarities, and colis connection in STAR or DELTA formation.

__________________
Manindra
Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#10

Re: Motor Star & Delta Connection

07/11/2011 3:14 AM

HI HARDWORKER

Do some Hard thinking too.

Do you know how to check continuity

If you do -you can tag 3 different pole coils with 2 ends each.

Rest is simple if you know a little about Y AND .

Best of luck

mm

Register to Reply
Participant

Join Date: Jul 2011
Posts: 4
#12
In reply to #10

Re: Motor Star & Delta Connection

07/11/2011 9:54 AM

Thanks everybody........special thanks to Brich for the convincing answer.

Dear Tornado"I had already mentioned in the starting that I have identified the winding ends,obviously thru continuity test.

Dear Keith grewar:If you dont want to help,at least don't discourage others for posting questions which many engineers found difficult to answer.

Mukulmahant:I simply didn't get you.(read my question carefully.Already I had told that windings end were identified).

Thanks to all.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#13

Re: Motor Star & Delta Connection

07/27/2011 10:33 AM

1. Question: How to find out Motor Terminal?

Answer:

i) With a multimeter or continuity tester, you can segregate three sets of windings. Can't you?

ii) Now, assume one set of windings to be, say, winding "U" and also, designate its terminals as assumed "U1 & U2".

iii) Take a 9V Cell; Connect + ve of Battery to the assumed "U1" preferably thro a push-switch and - ve to the assumed "U2".

iv) Connect a zero centred galvanometer, to another set of winding, say winding "V" such that the assumed "V1" is connected to the + ve terminal of the galvanometer and the assumed "V2" to the - ve terminal of the meter.

v) Now, when the switch is pressed, the zero centred galvanometer would deflect in the positive direction, if the assumed "U1, U2, V1 & V2" are correct.

vi) Else, if the deflection is on the negative side in the galvanometer, change your assumptions for either one of the winding (That is may be the assumed U1 can be U2 and the assumed U2 is U1 . Or keep the assumptions for U winding as it is and reverse it for the V winding (that is assumed V1 is V2 and assumed V2 is V1).

vii) Repeat this test for applying voltage to other windings and confirm your terminal assumptions.

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14

Re: Motor Star & Delta Connection

07/27/2011 12:19 PM

What I want to know is two things:

1) How is it that so many motors end up with no winding connection information? Are people so ignorant that they think the nameplate is inconsequential in a motor and they remove it?

2) Why would someone persist on using a motor that has no nameplate data and therefore cannot be easily connected? Do they place ZERO value on the amount of time they spend trying to figure it out? To my mind, small motors are too cheap to fuss with, and larger motors are generally associated with high revenue processes, so down time costs should be considered paramount in selecting the proper equipment. Both scenarios preclude the use of junk motors that have obviously already been abused as evidenced by the lack of proper nameplates and connection details.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

brich (1); electricalexpert65 (1); hardworker2011 (3); JRaef (1); Keith Grewar (1); manindra (1); MUKULMAHANT (1); pnaban (1); Tornado (4)