Minimum Distance Between MCC and Wall

07/12/2011 11:42 PM

Can anyone please let me know what is the minimum clearance required from wall (as per statutory rules) to place a MCC panel in a room (single front type MCC with bottom cable entry)

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Minimum distance between MCC and wall

07/13/2011 12:31 AM

Zero, I think. (Else most MCCs I've seen are installed incorrectly.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Minimum distance between MCC and wall

07/13/2011 12:46 AM

The minimum clearance is 1 radian/fortnight x the square root of the inverse if the voltage is 249V/11, or greater.

Otherwise, zero.

These rules do not apply if the walls are red.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Minimum distance between MCC and wall

07/13/2011 1:28 AM

What he said...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Minimum distance between MCC and wall

07/13/2011 1:29 AM

But seriously, unless it is a "back-to-back" MCC design, they are made to be totally front access and zero clearance.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Minimum distance between MCC and wall

07/13/2011 1:44 AM

Maybe we should distinguish between the back clearance (zero) and the front clearance of walls or other obstructions. In the NEC (U.S. National Electrical Code), the required clearance is 3 feet up to a certain voltage, and 4 feet for higher voltages. I forget the dividing line--something like 250 or 300 volts.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#9
In reply to #5

Re: Minimum distance between MCC and wall

07/13/2011 1:20 PM

From 0-150 volts (condition 1,2 and 3) 3 feet.

From 151-600 volts:

condition 1--3 feet

condition 2--3 feet 6 inches

condition 3--4 feet

There are also extensive current rating derived clearances for working space arc-flash safety. NEC 620.5 references article 110 heavily. All panel doors must also open to a minimum 90 degrees.

Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #9

Re: Minimum distance between MCC and wall

07/13/2011 1:38 PM

My mistake in ASS-U-Me-ing the OP was referring to clearance to the BACK wall, it actually wasn't clear. Good on you all for catching the distinction.

LOL on your signature line cuba pete.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#11
In reply to #10

Re: Minimum distance between MCC and wall

07/13/2011 1:41 PM

If (s)he is referring to back wall clearance, (s)he needs to choose a new profession.

Unless, of course, it is a double-sided cabinet. There is a lot to assume, isn't there?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Minimum distance between MCC and wall

07/13/2011 5:23 AM

With some of the genius designers I've come across it's maximum panel door width minus six inches so it's impossible to fully open the door!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Minimum distance between MCC and wall

07/13/2011 5:52 AM

Exactly. One does need to be able to get the door open!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#8

Re: Minimum Distance Between MCC and Wall

07/13/2011 7:56 AM

You need to look at your local fire codes. As the clearance is set by those. Here I believe it's 5 feet. That is not just from the walls but any obstruction.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
4
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#12

Re: Minimum Distance Between MCC and Wall

07/13/2011 8:17 PM

It depends on the working space required for the MCC. If the back side of the MCC is required to open for the working (back accessible MCC), the sufficient working space is required between the wall and the MCC. If not (front-accessible only MCC), it can be attached to the wall. The distance required also depends on the MCC voltage and the type of wall. NEC 110.26 (up to 600V) and 110.34 (over 600V) has the detail space requirement.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 4)
Commentator

Join Date: Nov 2006
Location: Roscoe IL
Posts: 69
#13
In reply to #12

Re: Minimum Distance Between MCC and Wall

07/13/2011 10:31 PM

msamad; that link ROCKS!!!! if you back up a little in that directory there is a proverbial a$$load of info on there!!! as for the MCC issue; unless prevented by composition of the wall (rice paper, balsa etc) a front only unit is designed to be mounted against the wall..unless "local jurisdiction" requires otherwise.

__________________
God's greatest gift is the ability to learn.... and the worst curse is the ability to rationalize our behaviour
Register to Reply
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#15
In reply to #12

Re: Minimum Distance Between MCC and Wall

07/14/2011 3:12 AM

Hi msamad,

I agree 100% with duffdr when he writes that the site you gave is MAGIC. Thanks!

A little further back on that same site is a list of very interesting E-Books as well.

Regarding the OP's question I think your answer goes right to the crux of the question by stating 'sufficient working space being required'. Apart from the legal requirements (which often tend to give the minimum requirements) a practical approach which allows easy access should always be employed.

Reading some of the other posters comments I was reminded of times when I would have to actually take the door off in order to get clear access.

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#16
In reply to #15

Re: Minimum Distance Between MCC and Wall

07/14/2011 11:37 AM

Great link! Thanks for the magic.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#14

Re: Minimum Distance Between MCC and Wall

07/14/2011 12:27 AM

From a ventilation point of view it is better to have little clearance.

__________________
pnaban
Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#17

Re: Minimum Distance Between MCC and Wall

07/14/2011 11:39 AM

In real no standards as such, but the minimum clearance is whatever you need to open the MCC for maintenance access and to take items in or out of the MCC.

If the MCC is specified as front entry than you can place it right against a wall if you want, generally leave a space for ventilation.

Register to Reply
Active Contributor

Join Date: Sep 2009
Location: A.P., India
Posts: 20
#18

Re: Minimum Distance Between MCC and Wall

07/15/2011 9:31 PM

Mr. Vithal,

you can download "Indian Electricity Rules" from "www.india.gov.in" for your reading.

Following are the required clearances around a MCC.

Front: minimum 3ft (from any projected point)

Sides: Less than 200mm or more than 750mm

Rear: It can be flushed to wall if it is single front, otherwise less than 200mm or morethan 3ft.

sitaram.

__________________
-- sitaram
Register to Reply
Member

Join Date: Jul 2011
Posts: 7
#19
In reply to #18

Re: Minimum Distance Between MCC and Wall

07/18/2011 1:57 AM

Dear Sitaram,

Thank u for your reply can you please give me exact link wherin i can get this info

Register to Reply
Active Contributor

Join Date: Sep 2009
Location: A.P., India
Posts: 20
#20
In reply to #19

Re: Minimum Distance Between MCC and Wall

07/19/2011 1:41 AM

Mr. Vithal,

i gave you the url of Govt. of India where you will get many of acts & rules. Any how, here is the direct link to Indian Electricity Rules-1956.

http://www.india.gov.in/allimpfrms/allrules/484.pdf

sitaram.

__________________
-- sitaram
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#21

Re: Minimum Distance Between MCC and Wall

02/24/2012 1:20 PM

Dear Mr. VITHAL,

I believe you are in India. As per I.E.R it is 900 MM min.

DHAYANANDHAN.S

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#22

Re: Minimum Distance Between MCC and Wall

02/22/2024 10:43 AM

<...minimum clearance required from wall...as per statutory rules...>

Are there such things?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

cuba_pete (2); dhayanandhan (1); duffdr (1); JRaef (3); Keith Grewar (1); lyn (1); msamad (1); NotUrOrdinaryJoe (1); ozzb (1); pnaban (1); PWSlack (2); sitaram (2); TonyS (1); Tornado (2); vargaalex (1); vithal3921 (1)

Previous in Forum: fundamental of settings of protective relays.   Next in Forum: Overvoltage Relay in Transformer Protection

Advertisement