Power Piping (Velocity?)

07/13/2011 12:26 AM

Hi,

Please let me know that the required design velocity for the following pipe lines for Combined Cycle Power Plant?

- HP Steam Line

- MP Steam Line

- LP Steam Line

- Turbine Bypass Line

- HP/LP Bypass Line

- Boiler Feedwater Line (BFP Suction & Discharge)

- Condensate Water Line

Register to Reply
Pathfinder Tags: Power piping velocity
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: Power Piping (Velocity?)

07/13/2011 12:45 AM

Greater than zero. Less than mach 1.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Power Piping (Velocity?)

07/13/2011 3:57 AM

Economic considerations of pressure drop versus pipe size would suggest that, as a rule of thumb, if a gas flow exceeds 10m/s then the piping is too small. For a liquid, the figure is around 3m/s.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#3

Re: Power Piping (Velocity?)

07/13/2011 4:48 AM

I can suggest following:

- HP Steam Line- (PN64) : 45 m/s

- MP Steam Line- (PN25) : 35 m/s

- LP Steam Line- (PN25) : 30 m/s

- Boiler Feedwater Line - 3 m/s

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#4

Re: Power Piping (Velocity?)

07/13/2011 10:29 AM

JBK....

Recommended velocities for the systems you mentioned are contained in the Piping Handbook, by Nayaar.

Please be aware that, in real Engineering Companies (like, say Bechtel), a detailed study is done comparing Main Steam, HRH & CRH piping diameters vs. best steam velocities in order to get the best financial ROR over the plant life.

These systems are so important and can affect the overall plant economics, that a detailed study is warrented.

Is this the first time that you have ever sized piping systems ?

-MJC

__________________
We have met the enemy....and he is us. POGO
Register to Reply Score 1 for Good Answer
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ace Boeringa (1); MJCronin (1); pritam (1); PWSlack (1)

Previous in Forum: How to Figure Gearing, Motor Size (hp and Torque)   Next in Forum: Unit Conversion

Advertisement