I have transformer of 2000Kva, 2 nos and DG of 1500Kva . How to calculate the short circuit individually
Re: short circuit calculation
07/19/2011 10:44 AM
Why not look it up in the original equipment manufacturer's Operation and Maintenance Manual?
07/19/2011 11:49 AM
1. Get Transformer and Genset impedances.
2. Take any Base Kv & Kva
3. convert them into per unit impedances
4. Draw the single line diagram
5. Apply fault at any node on the single line diagram
6. Apply Theveniz theorem to get fault current in per Unit value in unit less.
7. Actual fault current in Amps is obtained by dividing base current by fault per unit current.
8. If you find difficulty then display the single line diagrams with their impedances on this forum.I will calculate the fault currents and indicate on the forum.
CR4 Admin - phone number removed
From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.
B.E, M.I.E, M.S
07/19/2011 12:09 PM
07/20/2011 12:12 AM
best is to follow hussainin's step's...and for easier approach..use a therr-phase short circuit calculation...these yields an acceptable values for you to size up your OCPD's...g'luck
take care of your seconds and the minute will take care of itself..
Good Answers: 170
Re: Short Circuit Calculation
07/26/2011 11:21 AM
Transformer:
Fault Current = FLC of transformer / % Impedance of the transformer
Generator:
Fault Current = FLC of generator / % sub-transient reactance of the generator