How Often do VSD's Save Money

07/20/2011 3:12 AM

How often do VSD's actually save energy and money, and is this possible without installing extra filters to reduce the harmonics?

Register to Reply
Pathfinder Tags: harmonics vsd
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Plugg

07/20/2011 3:48 AM

All CE-marked VSDs are suitable for installation without additional harmonic filters.

One good way of saving money is installing VSDs on motors where there is a Peak Demand Tariff. Shaving off those starting current charges makes a good deal of economic sense.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Hobbies - Musician - New Member United Kingdom - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Transportation Engineering - New Member

Join Date: Mar 2007
Location: England
Posts: 951
Good Answers: 48
#2

Re: How Often do VSD's Save Money

07/20/2011 10:05 AM
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7
In reply to #2

Re: How Often do VSD's Save Money

07/20/2011 11:57 PM

good link..thanks!

__________________
The square root of nothing is what you make it!
Register to Reply Off Topic (Score 5)
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: How Often do VSD's Save Money

07/20/2011 2:36 PM

VFDs will ONLY save money under the following circumstances:

  1. The process they are applied to can benefit from reduced speed and reduced output of the machine, i.e. less flow from a pump or fan, not just reduced speed.
  2. There is some other mechanical method of reducing the output that is being replaced or avoided that would have had wasted energy associated with it.

That's IT. Despite all the other blather about taking advantage of the affinity laws on variable torque loads, the truth that is almost ALWAYS overlooked is that the Affinity Laws apply whether the flow is reduced via a VFD or a mechanical means. In other words when they use the "power reduces by the cube of the flow" line in their advertising, that statement is true regardless of how you reduce it. But in a mechanical means, such as fan guide vanes or fluid valves in pumps, there are extra losses associated with those means that are avoided when using a VFD. Those losses are more significant than most people realize, so in most cases a VFD will indeed save energy by comparison, even when harmonics mitigation is considered. But this issue is often grossly over stated.

If the load requires Constant Torque regardless of speed, as in a conveyor or machine tool, there is NO energy savings associated with using a VFD. Another common mis-statement is "With a VFD, the motor will only use as much power as it needs." Again, this statement is true, but it is ALWAYS true regardless of whether or not the VFD is present. In fact the VFD is not 100% efficient, so there are losses associated with a VFD that will actually cost you energy. Of course this is irrelevant if the speed reduction is necessary, but it means there is no energy savings available when Constant Torque is necessary.

The only time energy savings on a CT load MIGHT save energy is when truly VARIABLE speeds are required and the alternative is something like a mechanical vari-drive (variable pulley) because those are notoriously inefficient by comparison to a VFD. But unfortunately, those also come with mechanical advantage with regards to torque, which VFDs do not provide, so that must always be considered as well.

So the answer to your question is, YES, there are many many applications where reduced flow requirements are necessary and VFDs will save energy when used to displace other methods of flow restriction. Not as many as the VFD suppliers want you to think there are, but still a great many. 67% of all electric energy used in the USA is for motors, and of that, 40% are on pumps and fans! That's a lot of potential savings out there.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#4
In reply to #3

Re: How Often do VSD's Save Money

07/20/2011 11:31 PM

Super answer..can I use it please?

To add a little something, having used VSD/VFD's for many years on ESP's in the oil industry there added factor is the ramp up facility of the VFD which almost eliminates the shock load starting on bearings, couplings, shafts and twisting of the whole downhole completion.

The ramp up time does increase the run lift of ESP's and the cable a there is little or no inrush current.

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: How Often do VSD's Save Money

07/20/2011 11:51 PM

Yes, ramp up (and down) are added benefits of using VFDs, they are also however available with soft starters in many cases so that alone is not enough of a reason to spend the extra money (although in small motor applications, VFDs are now at par with SS cost).

You also alluded to another benefit, starting current reduction. There are applications where the demands on the power system are so great that the only way to accelerate a motor is with a VFD, because it can provide 100% torque throughout the acceleration cycle without exceeding motor FLC.

And yes, you may use that statement on energy savings.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#6

Re: How Often do VSD's Save Money

07/20/2011 11:55 PM

If you are installing VSD's to save money, they must operate at 40-70% of their rated RPM. If you do not want to add filtering, you can not have any electronic equipment installed in the building housing said drives. I was able to get a $60,000.00 grant from NYSERDA for my company in doing such. If I would have had to add filtering, that would have cost the company $20,000.00 to do so. So we live on and the company collected a check for $60,000.00 I no longer work for them. I have moved on to a better more relaxed atmosphere where I am more than welcome to participate and rewarded for my efforts of saving the company $$$

__________________
"Real Bass Players" do not use picks
Register to Reply
Guru

Join Date: May 2007
Location: Geelong, Australia
Posts: 1084
Good Answers: 54
#8
In reply to #6

Re: How Often do VSD's Save Money

07/21/2011 12:15 AM

"..If you do not want to add filtering, you can not have any electronic equipment installed in the building housing said drives.." Why? What size motors are you driving? How old are the drives?

I've found all industrial equipment I use is insensitive to the small amount of electrical noise produced by VSD's.

__________________
If there's something you don't understand...Then a wizard did it. As heard on "The Simpsons".
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#9
In reply to #8

Re: How Often do VSD's Save Money

07/21/2011 12:25 AM

All new 20HP motors, 80 of them = 80 drives. NYSERDA requirements indictive of 3% harmonic filtering. drives built in 2% harmonic filtering. No other electronic equipment = no needd to provide additional filtering. = %60,000.00 US check to the company. = I moved to a more worh while company that appreciates this incentive.

__________________
"Real Bass Players" do not use picks
Register to Reply
Power-User

Join Date: Jul 2007
Location: Melbourne Florida
Posts: 122
Good Answers: 2
#11
In reply to #6

Re: How Often do VSD's Save Money

07/21/2011 4:31 PM

"..If you do not want to add filtering, you can not have any electronic equipment installed in the building housing said drives.

Could you please elaborate on this. I have not had a problem within the last 8-10 years or so with harmonics caused by a VFD. If there are particular cases where it is a problem I would like to be aware of it.

Thanks, Dave

__________________
repeat problems can not be solved by the same way of thinking ( A. Einstein)
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#13
In reply to #11

Re: How Often do VSD's Save Money

07/21/2011 9:48 PM

Hi Dave, This was specified by the inspector from NYSERDA who was to approve the grant for the $60,000.00 Check. We argued about the Line Reactors and the 2% impedance vs the 3% they require. Due to he fact at that time there was no electronic equipment in either of the 2 buildings he accepted the standard 2% impedance and approved us for the check. I have not had issues with drives since 2002 with the improvements in design. And they get better every year.

__________________
"Real Bass Players" do not use picks
Register to Reply
Power-User

Join Date: Jul 2007
Location: Melbourne Florida
Posts: 122
Good Answers: 2
#14
In reply to #13

Re: How Often do VSD's Save Money

07/21/2011 10:52 PM

Thank you for the clarification.

__________________
repeat problems can not be solved by the same way of thinking ( A. Einstein)
Register to Reply
Commentator

Join Date: Apr 2008
Posts: 59
Good Answers: 2
#10

Re: How Often do VSD's Save Money

07/21/2011 2:37 PM

My experience is with batch pumping (sewage lift stations). A pump will use a lot more energy in the initial few seconds of starting than it will for the next minute or so of running at speed. I heard a statistic something along the lines of "reduce the pump speed by 10% and you will save 40% energy". Sorry, don't have a reference for that at the moment, will try to find it.

In addition to a fixed speed reduction, there are other ways to use VSDs to save energy costs. Take a station which has been sized for peak flow. During off-peak flow, the pumps are over-sized for the inflow, so they will slam on, run flat out for 30 seconds then stop. Each time they start, the inrush currents and energy required to start physically moving the liquids in the pipes will be very significant relative to the energy used for the rest of the pump cycle.

Now, what if we were to run the pump at half speed? (Start it at 100% for 5 seconds to flush the pipes and run the mix/flush valves, then return to a calculated speed). You will get much longer pump run times, so less energy-consuming starts. Include an algorithm that will increase the speed of the VSD proportional to the level in the well and the number of pumps running (http://www.multitrode.com/pump-station-manager/vfd.html), and you have a system that matches the inflow, to only use as much energy as it needs.

Longer, slower run-times are not only more energy-efficient (Energy = Money, so hence they are also cost-saving), they are better for the pumps, and steady inflow is much preferred by the treatment works in terms of system stability, instead of pulsed inflow that a normal headworks lift station would provide.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#12

Re: How Often do VSD's Save Money

07/21/2011 8:53 PM

Contrary to popular belief, "inrush current" (really Starting current, inrush is something different) does NOT represent additional energy use. No matter what you use, the amount of ENERGY it requires to accelerate a load is a physics constant; nothing you do (within the laws of physics that so far govern our existence), will alter that amount of ENERGY. All a VFD does is lower the beak and lengthen the time. But if you plot it on a curve, the area of the curve is constant.

Note that I use the term energy. Current is not energy, it is a component of power (or watts). Watts are not energy either, energy in electrical terms is watts and time together.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#15

Re: How Often do VSD's Save Money

07/23/2011 3:56 AM
__________________
shamith gambhir, electrical engineer
Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

brich (2); Critcho (1); dthomas16 (2); ffej (1); Holzfeller (1); Jimh77 (3); JRaef (3); PWSlack (1); SHAMITHGAMBHIR1 (1)

Previous in Forum: Identification of Magnets   Next in Forum: Problem with Danfoss Inverter VLT-5000

Advertisement