Problem With Valve Actuator

07/24/2011 5:48 AM

Presently we are using a steam line electric actuator modulating control valve and actuator Model No.: EK60.908M (VALPES).

We have already changed this valves two times in last six months, then we check the details specification of the valves actuator and found operating temperature -10 Deg C to 55 deg C. My question is this temperature is for the environmental temp. or steam temperature that the valve is controlling?

If we want to change this valve brand with similar specification which brand is available in ASIA region? I am from Bangladesh.

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#1

Re: Problem with valve actuator

07/24/2011 6:06 AM

Those are ambient temp values, BTW you have clue in your hand, steam can not have -100C. and even at 550C you will hardly get any usable amount of steam.

Are you sure the valve is designed for the operation of steam. If Yes,then there must be an another specification that tells about max steam temp that is passing through valve.

Register to Reply
Commentator

Join Date: Oct 2010
Location: Bangladesh
Posts: 91
Good Answers: 2
#2
In reply to #1

Re: Problem with valve actuator

07/24/2011 6:55 AM

Thanks....

Actually its come with an Air Handling Unit, and that valve purpose is to control steam and steam purpose is to control dehumidification of the unit accurately.

As it come with a big unit we do not have enough idea about the valve or actuator its out of our URS.

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#3

Re: Problem With Valve Actuator

07/24/2011 11:49 PM

Do you have the orginals valves you removed ?

Check and see if they are made of the same material.

Then check you system for sand or sediment when high temp equipment has been setting any lenght of time it must be cleaned expertly before it will operate properly.

As you said it came with the system.

__________________
If you never do anything you never have problems.
Register to Reply
Commentator

Join Date: Oct 2010
Location: Bangladesh
Posts: 91
Good Answers: 2
#4
In reply to #3

Re: Problem With Valve Actuator

07/25/2011 12:50 AM

We have only changed the actuator portion with same specification not the valve. No sand or something like this. Only problem we found is the actuator motor damage.

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Problem With Valve Actuator

07/25/2011 1:14 AM

Heat from the steam line may be conducting into the valve actuator motor, damaging it in the same way a too-high ambient temperature would.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Jul 2010
Location: Europe Netherlands
Posts: 28
#6
In reply to #5

Re: Problem With Valve Actuator

07/25/2011 2:14 AM

Bashir,

you mention Valpes actuator type EK, I only know type ER. using the third actuator in 6 months is no good. You use this valve in a modulating mode, some of the Valpes actuators can not be used constantly, check if the valve actuator gets any rest for cooling down.

__________________
Only if it's impossible, it will never happen
Register to Reply
Commentator

Join Date: Oct 2010
Location: Bangladesh
Posts: 91
Good Answers: 2
#7
In reply to #6

Re: Problem With Valve Actuator

07/25/2011 4:25 AM

thanks,

No cooling or rest

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Problem With Valve Actuator

07/25/2011 8:12 AM

Choose an alternative actuator that is rated for the steam temperatures in question.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Oct 2010
Location: Bangladesh
Posts: 91
Good Answers: 2
#9
In reply to #8

Re: Problem With Valve Actuator

07/25/2011 8:23 AM

it should match with the valve!

We are looking for that.......

__________________
Experiance will come with time, but you have to manage quality time. Bad management always leads us bad experiance.
Register to Reply