Imbalance

07/26/2011 11:21 PM

Hi

I have several 415V 3ph motors on my site and when i check the at the motor terminals R/B 413V R/Y 406V Y/B 410V. Now when i disconnect the cable from the motor and do the same check the voltage readings are 414.2V, 414V, 414.4V. I have tested the motor windings individually and the readings are U1-U2= 12.8Ω. V1-V2=13Ω, W1-W2=12.8Ω. This is a small motor .12KW and low power factor of 0.37 and FLC of 0.8A. So can someone please tell me why i have this imbalance when i connect to the motor. The 5 motors are all from the same manufacturer and their serial numbers are consecutive which looks like they have come from the same batch at the manufacturing stage.

Best regards

Duncan Cowan

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#1

Re: Imbalance

07/26/2011 11:41 PM

If the motor is defect free, then Your powering cables for all phases may not have equal lengths or equal conductor diameters or equal number of strands.or combinations of all these three. in other words input impedance for all three phases is not equal. You should check the current drawn by motor instead of resistances.

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Imbalance

07/27/2011 1:16 AM

413 vs 406 ≈ 1.7% imbalance. This does not seem very severe, and might even be due to a loose wire nut or the like.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Apr 2011
Posts: 3
#5
In reply to #2

Re: Imbalance

07/27/2011 6:17 AM

We did find loose wires under the termination block but this did not cure the imbalance. I am not worried about the level of imbalance but why we only have it when i connect to the motor and only on the yellow phase. The motor still runs no problem it is just a general enquiry to see if someone else has ever had this problem. The core lengths are all the same and the core diameters are all the same. When the cable is not connected i have 1V of a drop between Red/Yellow but when i connect the cable to the motor that reading increases to 7V. It is the same on the other 4 motors the Red/Yellow voltage reading is about 7V lower than the other 2 readings. I just think this is strange and was just trying to understand why this should happen.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6
In reply to #5

Re: Imbalance

07/27/2011 6:43 AM

the answer is "back to basics"

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#7
In reply to #2

Re: Imbalance

07/27/2011 11:28 AM

I'm with you...I wouldn't even notice a small difference like that. It doesn't seem like a "problem" at all.

I wonder what the mfr's specs are? I bet this motor is within tolerance.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#3

Re: Imbalance

07/27/2011 3:05 AM

are you using flat cables or single core cables to your motors?

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Imbalance

07/27/2011 4:08 AM

Imbalance is a fact of life.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #4

Re: Imbalance

07/27/2011 12:11 PM

"Imbalance is a fact of life."

Bingo. Although I like to say it as "Imbalance happens."

Nothing on this planet is perfect, there are always small differences in two things, exponentially more in 3 things, such as 3 phases and 3 motor windings. What you have discovered is a phenomenon that motor people often take advantage of in helping to get the most balanced voltages possible. It's called "rolling" the conductors and is used when you find yourself in the exact situation you described, a slight imbalance: move A to B, B to C, C to A. It doesn't change the rotation but it takes advantage of slight variations in conductor resistance, impedance irregularities etc. between the three windings and the three motor leads.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9

Re: Imbalance

07/27/2011 11:02 PM

Please measure the harmonics in voltage before and after energising.

__________________
pnaban
Register to Reply Score 1 for Off Topic
Member

Join Date: Jul 2011
Posts: 5
#10

Re: Imbalance

07/27/2011 11:19 PM

you can check the voltage and power between L1,L2,L3 phase when the moto is working

__________________
Blue Jay Electronic provide high performance power meter, energy meter, and industry automatic solution.
Register to Reply
Power-User
Popular Science - Weaponology - New Member

Join Date: Jun 2011
Location: Berkeley, CA USA
Posts: 128
Good Answers: 4
#11

Re: Imbalance

07/28/2011 12:34 AM

The problem may also be in the source to your factory. If the distribution line to your factory has a PF imbalance the resistance on that phase may be higher IE higher source resistance on that phase due to differential heating. Try taking the measurement again on the weekend or after business hours and see if it is different.

__________________
Working to end the use of carbon for energy
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#12

Re: Imbalance

07/28/2011 1:01 AM

What is your supply transformer kva, and length and gauge of cable runs? With such a small load I am surprised you notice it connected at all. What happens if you connect a balanced three phase resistive load such as an incandescent lamp load?

Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 10
#13

Re: Imbalance

07/28/2011 1:53 AM

Good day Bali Boy

I think Rakesh Semwal has the answer. Check the current drawn by each phase, the excitation currents may have a typical H-L-H pattern causing the perceived imbalance. This is typical of transformers as well.

Register to Reply
Active Contributor

Join Date: May 2011
Posts: 18
#14

Re: Imbalance

07/28/2011 1:54 AM

Your source power without load is excellent.

Your voltage drop is due to load activated and doing work.

Your voltage imbalance can lead to current imbalance which is the major issue, but, in this case, the voltage without load is very good from the source, so, the "loading" is coming from the motor and or what it is connected to, or the work it is performing.

As long as your current is on or about the FLA on the nameplate data, its OK. If your over but not over by more than SFA, your imbalance is still OK if imbalance is less than 5%. More than that and you need to perform rotations to find the best balance.

The reasons for loading on just one leg/winding of the motor is multiple. could be dirt, bearing, wear, or aging. monitor for heat build up only if running amps higher than FLA nameplate data.

IF all within parameters, just basic PM, keep circulation area clean. No one gets out alive and all things come to an end. Motors included.

Register to Reply
Participant

Join Date: May 2011
Posts: 2
Good Answers: 1
#15

Re: Imbalance

07/28/2011 2:24 AM

What 'Cable' do you disconnect and still get Voltage readings on your motor terminals? Also are you concerned about the resistance imbalance or the voltage imbalance? Remember a 1% voltage imbalance can cause a 6-7% current imbalance try taking current readings while the motor is under load. Is this a AC Induction motor?

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#16

Re: Imbalance

07/28/2011 5:40 AM

If you interchange the cables on the motor terminals, and still have the same imbalance but related to the same terminals and not the phase colours, AND this happens on all the motors of this same batch, then maybe the imbalance is due to the slight differences in the iron works (Stamped laminated stator and rotor make up. i.e. the magnetic fields. Since it is the same batch, they will exhibit almost the same imbalance due to the fields imbalances. (Lw is more important than the resistance of the windings).

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#17

Re: Imbalance

07/28/2011 8:52 AM

Generally,2% voltage imbalance is allowed without derating of motor Kw capacity. You have mentioned that you have measured motor winding resistances and the figures indicated are also found normal. But which method was adopted for this measurements? You must use Electric motor checker instrument for measurements of % inductances( L-L/ L-N ) and resistances of motor coils . Most probably you may observe that there is a variation in & indutance values and this may be the reason for the voltage imbalance.

Manindra.

__________________
Manindra
Register to Reply
Active Contributor

Join Date: Jan 2010
Posts: 10
#18

Re: Imbalance

07/28/2011 9:34 AM

I agree with LA LUKE. If you rotate the location of the power leads and the motor terminals keep the same voltage imbalance, the motors are the source of the imbalance, if the power lines keep the imbalance your power supply is the source of variation.

Resistance is only a minor part of the impedance (Z=R+jXl) . The inductive reactance is the main factor that affects the total impedance of each phase. What about currents? (Z=V/I). Note that line to line voltages and phase voltages are not nesessarily the same.

Although motor manufacturers goal is to construct the three phases identical, even shape variations on the windings if not different length or a missing turn, could result on different motor reactances.

Certainlly there are standards that manufactures shall comply with.

Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#19

Re: Imbalance

07/28/2011 9:59 AM

I would tend to agree with the following comments:

1.- Less than 2% is nothing to worry about and maybe inherent to the system

2.- The length difference of the cables may also be giving you the discrepancies once the motor is connected.

3.-The power distribution in your plant maybe imbalanced.

4.- Biggest truth in the world "Imbalance exists"

Register to Reply
Guru

Join Date: Sep 2008
Posts: 706
Good Answers: 32
#20

Re: Imbalance

07/28/2011 10:23 AM

I'm assuming that this motor is being run through a starter. Have you checked line voltage before and after the contacts right in the starter box itself or or you checking at the motor terminal box? Did you remove and check the contacts for signs of arcing or erosion? Additional resistance at the contacts could explain why you're having a slight voltage drop at the motor terminal block or even on the load side of the contacts.

__________________
Spinco
Register to Reply
Commentator

Join Date: Jun 2011
Location: Hyderabad, India.
Posts: 92
Good Answers: 2
#21

Re: Imbalance

07/28/2011 5:06 PM

I agree fully with Vargaalex explanation, additionally I recommend you to touch the motor after half an hour running if you can do that then you need not worry and stop thinking about unbalance of voltage.

__________________
B.E, M.I.E, M.S
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#22
In reply to #21

Re: Imbalance

07/28/2011 5:19 PM

For the heat? Yeah, that's a good hourly/daily rounds kind of check.

Register to Reply
Register to Reply 22 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bali Boy (1); brich (2); cqbluejay (1); cuba_pete (2); cyoung (1); Forbes (1); Gibson81 (1); GW (1); JRaef (1); LAA_Lucke (1); manindra (1); Mushtaq Hussainh (1); pnaban (1); PWSlack (1); rakesh_semwal (1); regsoft (1); Spinco (1); Tawinc440 (1); Tornado (1); vargaalex (1)