08/11/2011 4:38 AM
Re: Fuel gas Pipe size & flange rating
08/11/2011 4:46 AM
Er, all the information needed is on the drawing.
Good Answers: 19
08/12/2011 1:15 AM
Re: Fuel Gas Pipe size & Flange Rating
08/11/2011 12:17 PM
Homework? Some of the pipe sizes seem odd.
08/11/2011 10:14 PM
Dear JBK
1. Line size - it depends on the future demand, the length of pipe and the pressure at the terminal. However, I believe that this info is not currently available, then my suggestion is for you to use the same diameter as the main header.
2. Flange rating - for C.S at 16 bara and 65 C, 150# just meet your requirement. However, I propose that you use 300# rating to be on the safe side.
Hope the above helps.
Sabri Ahmad
Good Answers: 11
08/13/2011 7:23 AM
Gas velocity as per the data is around 25 m/s, which is in order for fuel gas. Every thing looks like for future connections, except the last one. You should decide the pipe size & flange ratings for future connections 1,2,3 in the same way as present. Follow the same velocity limit of 25 m/s and calculate the pipe size. Rating shall be same as present because pressure is the same.
Different flow units for future connection 180 MMSCF/d is not understood.
When there is smoke, there must be fire.