Proper Earthing

08/17/2011 2:28 AM

What should be a proper way of Earthing for motor, devices or equipment.

I have seen installation where equipments earth linen was tapped to steel structures of the building. Does this comply to the standard of earthing or Earth lines should be made insulated or unexposed to conductors and public?

I will appreciate your rightful answer. Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Proper Earthing

08/17/2011 4:03 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#2

Re: Proper Earthing

08/17/2011 1:17 PM

As our British friend has replied (succinctly)...use your local code authority.

I would refer to:
NEC (NFPA 70)

IEEE Std 100

IEEE Std 142

Reply
Active Contributor

Join Date: Aug 2011
Posts: 12
#3

Re: Proper Earthing

08/17/2011 2:12 PM

Usually its would be considered very recommended to grounding the motor directly to the steel structural ,but you still need to connect the motor to the grounding conductor along with the power cable to provide the motor with particular protection required.

Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#4
In reply to #3

Re: Proper Earthing

08/17/2011 8:21 PM

I bet if some motors located at the higher floors of the building with power supply 440V, 3 phase leaks, and some of the structures gets wet by the rain and get into the cold water line, then the water gets, a really a nutty and refreshing flavor. The last time you would see yourself into, is looking in the mirror at the lavatory and getting attracted with the faucet.

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#5
In reply to #3

Re: Proper Earthing

08/18/2011 3:58 AM

Hi MegaThink, you are part of the way right, the electrical earth should be connected directly to the supply distribution board, but bonding of other metallic structures may be bonded directly to the main motor earth. This is for earthing the metallic structure that is connected to the motor, bonding of all metal is important in an electrical installation. It is also required that an additional earth wire is used to earth structures that are metal, but sometimes installation teams do not follow this rule, due to them being lazy.

Cheers

Joe

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6
In reply to #5

Re: Proper Earthing

08/18/2011 1:34 PM

Joe you said..bonding of all metal is important in an electrical installation. It is also required that an additional earth wire is used to earth structures that are metal, but sometimes installation teams do not follow this rule, due to them being lazy.

Very true, but that's where the inspectors and commissioning people play their part in identifying this failing, and getting it rectified to ensure the installation complies with local codes, BEFORE the installation is signed off.

to the OP...

Yes in the UK we have BS 7671 plus other on site guides etc, etc... Yes, use your local electrical guides and standards, but common sense together with a high degree of experience will tell you if and when something is right or wrong. It's simple really, if it doesn't have an earth, then put one in.

you have asked a good question, but cannot be answered fully as we don't know where you are in the world and we don't know your local electrical codes.

__________________
The square root of nothing is what you make it!
Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#7
In reply to #6

Re: Proper Earthing

08/19/2011 4:31 AM

Hi Brich, I have to agree with what you have said, but sometimes inspectors can be a bit to casual in their testing, they only on some occasions check that there is continuity on the earth connections, and not investigate where this earth connection comes from.

You also said: That I had asked a good question, I don't think that I have asked any questions in this forum, I only made a statement. I think that you may be referring to the AP.

Anyway Very Best Regards

Joe

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#8
In reply to #7

Re: Proper Earthing

08/19/2011 12:09 PM

the "good question" comment was to the OP...

__________________
The square root of nothing is what you make it!
Reply