Info Needed

08/17/2011 2:16 PM

If there are 30 (15amp outlets) ,how to feed theme (i.e groups, conductors and main cond and C.B)

THANK YOU

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: INFO NEEDED

08/17/2011 2:36 PM

2 - #14 daisy chained to each recept.

1 - 30X15A=450 - 450A CB

Register to Reply Score 1 for Off Topic
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#5
In reply to #1

Re: INFO NEEDED

08/17/2011 4:07 PM

Might I interest you in some homeowner's insurance?

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: INFO NEEDED

08/17/2011 2:40 PM

I'd make them all home runs and size everything to your local code. Since we have no clue where you live, how can we help you?

Wait, let me polish up my crystal ball:

Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 12
#7
In reply to #2

Re: INFO NEEDED

08/17/2011 6:23 PM

sorry. know if i said it is an industrial shop and folow the CEC,would that help?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #7

Re: INFO NEEDED

08/18/2011 3:55 AM

British Standard 7671 applies, however the 15A round-pin socket is usually only found in special applications these days, like in theatres.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Info Needed

08/17/2011 3:47 PM

If this is a residence, you can put them all on one circuit. 1 20 amp breaker using #12 conductor. I would not do it that way. Suggest maybe 10 on a circuit. Come back and tell me if is is a residence.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Info Needed

08/17/2011 3:54 PM

Quote AP#1 " 2 - #14 daisy chained to each recept.

1 - 30X15A=450 - 450A CB"

Surely you jest. I can see it now. A 450 amp breaker with 2 #14 conductors connected. I don't believe that would work. I don't think the set screw on the breaker would tighten down enough on the #14 conductor to make a connection.

Better check this idea again.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#6

Re: Info Needed

08/17/2011 4:57 PM

You need to determine the anticipated loading on each of the receptacles and then go from there. Without the loading you expect per receptacle, you can not decide how to power these receptacles.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Active Contributor

Join Date: Aug 2011
Posts: 12
#8
In reply to #6

Re: Info Needed

08/17/2011 6:24 PM

sorry. know if i said it is an industrial shop and folow the CEC,would that help?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #8

Re: Info Needed

08/17/2011 10:45 PM

As described so far, I don't think this will satisfy the CEC, or any other Code worthy of the name.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#9

Re: Info Needed

08/17/2011 8:15 PM

Tell ya what. Draw up the dimensions of where you want them, the location of your panel. The size of the panel. The rating of the panel, AMPS. How many open CB spots you have and we can take it from there. 10:1 says you're going to be installing a sub panel and several breakers.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11

Re: Info Needed

08/17/2011 11:03 PM

You can arrange either in radial or ring circuits depending on load connected. group of small loads could be connected in ring. Larger loads should be connected radially with CB for each item. Consider diversity when sizing cable and CB.

__________________
pnaban
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Posts: 989
Good Answers: 14
#12

Re: Info Needed

08/17/2011 11:54 PM

Southern Building Code sez 12 fixtures per breaker circuit and a dual plug outlet counts for 2 so you need to know whether you mean 30 single outlets or 30 dual outlets.

Outlets come in two amperages, 15 and 20. For 12 individual outlets of the 15 amp variety use all 14 guage wire hooked into a 15 amp circuit breaker.

For 12 individual outlets of the 20 amp variety use all 12 guage wire and hook them into a 20 amp outlet.

You're not allowed to mix wire sizes, outlet sizes or breaker sizes anymore in the US.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13

Re: Info Needed

08/18/2011 3:44 AM

Thank god I'm in the UK.

BS1363 fused plugs have served us well since 1942. 30 outlets would, using common sense be split in two rings each with a 32A MCB.

According to BS7671-2008 they all could go on the same ring so long as the area covered doesn't exceed a certain area (can't remember what it is at the moment).

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #13

Re: Info Needed

08/18/2011 3:57 AM

100m2.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#16
In reply to #15

Re: Info Needed

08/18/2011 4:24 AM

Thought it was, but didn't want to say so in case you shot me down in flames

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#17

Re: Info Needed

08/18/2011 8:21 AM

Okay unless you know what each one of those outlets will have plugged into them to dedicate circuits for. Then you use averages. The average is about 1.5 amps for most general devices. So that 6 duplex receptacles on one 20 amp breaker ran with #12 wire. There are some that you may want to run dedicated. Those by sinks or faucets on ground fault circuits. Those that are on kitchen cabinets that may have microwave plugged into them. Microwave draw more then the average current. Receptacle under the sink for garbage disposal. One that may appear to be for a frig in a kitchen area. Those to the exterior of the building never know what current the device plugged into them will draw. Any other areas where you may have a device used that generally will pull more then the average.

Unless your local code says different.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#18

Re: Info Needed

08/18/2011 9:32 AM

Under the CEC (Canadian Electrical Code) here is what you need to do.

Determine the load required by what it is you intend to plug into the receptacles.

You really need to understand the demand that the devices you intend on powering present. It will do you no good at all to connect 5 receptacles to a 15 amp breaker if you intend on pulling 1000w (1000w / 120v = 8.3A) from each receptacle.

Once you know the demand expected you can then power the receptacles in groups that make sense for the anticipated load.

If you do not know or can not get the information on the anticipated load, the CEC allows you to group up to 12 outlets (a single duplex receptacle counts as 1 outlet) together on a 15A circuit using 14 gauge copper conductors. This anticipates a maximum loading of 1A (120w) per outlet. See CEC rule 8-304.

The maximum loading on circuits feeding 5-15R receptacles (the standard 120v 15A receptacle) is determined by the rating of the over current devices powering the circuits and by the type of conductors used. Unless you are using 100% rated breakers, go with 12A maximum loading on a 15A circuit. You may not feed 5-15R receptacles with a breaker larger then 15A.

A 5-15R receptacle may NOT be powered by a 20A circuit in Canada. If you wish to use 20A circuits, then you must use a 5-20R "T-Slot" receptacle with 12 gauge copper conductors.

Keep in mind possible voltage drop issues. The CEC allows for no more then 5% voltage drop overall (from supply service demarc point to the point of utilization) and no more then 3% in a feeder or branch circuit. See rule 8-102.

Finally... go get a qualified electrician licensed in Canada to help you with this.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#19
In reply to #18

Re: Info Needed

08/18/2011 11:06 AM

I miss that. Use to running commercial there we always used 5-20R's. He did say it was industrial shop. But never did we max out the circuit with receptacles.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Register to Reply 19 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

129CBRider (1); Anonymous Poster (1); cuba_pete (1); Fredski (1); lyn (1); MegaThink (2); North of 60 (2); ozzb (2); pnaban (1); PWSlack (2); TonyS (2); Tornado (1); wareagle (2)

Previous in Forum: Choice of Cheap n Well Documented MCU to Handle USB and/or RS-232 Interface   Next in Forum: CT Ratio

Advertisement