Short Circuit Device

08/22/2011 3:23 AM

If we put 2 protective devices (MCCBs) having short ckt protection in series, can it will create any problem during short circuit fault??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Short Circuit Device

08/22/2011 3:40 AM

Please check out this recent thread....

http://cr4.globalspec.com/thread/71318

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Short Circuit Device

08/22/2011 3:46 AM

It will offer no better protection than the lowest-tripping-rated device.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Short Circuit Device

08/22/2011 8:54 AM

What is the setting of the short circuit release in each MCCB?

Register to Reply
Commentator

Join Date: Apr 2009
Location: CG
Posts: 64
#5
In reply to #3

Re: Short Circuit Device

08/23/2011 7:06 AM

Both having Icu=Ics=50kA .

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: Short Circuit Device

08/23/2011 8:48 AM

I am not asking the Breaking Capacity. I am asking the setting made in the Instantaneous (Short Circuit Magnetic) Release made in these MCCBs.

Register to Reply
Commentator

Join Date: Apr 2009
Location: CG
Posts: 64
#8
In reply to #6

Re: Short Circuit Device

08/25/2011 8:04 AM

The upstream MCCB setting is 100% & downstream have 80%.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: Short Circuit Device

08/25/2011 8:28 AM

1. EE65 has asked about the Instantaneous (Short Circuit Magnetic) Release setting..i think you are talking about the overload. Yes?

2. Like most people, you don't seem to have checked out the earlier thread on Cascading and Discrimination that i gave ... you would have learnt something i think.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Commentator

Join Date: Apr 2009
Location: CG
Posts: 64
#10
In reply to #9

Re: Short Circuit Device

08/25/2011 12:02 PM

WE have a PCC having 2000A incomer & 4 NOS. 650 A MCCB outgoing feeder & one of these outgoing we connect a MCC having 650A MCCB INCOMER.......

both MCCB having fixed type thermal magnetic short circuit setting = 6xIn.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#11
In reply to #10

Re: Short Circuit Device

08/25/2011 12:25 PM

Then, you will have co-ordination problems, for sure! If there is a short circuit fault beneath the MCC Incomer 650A MCCB, then there is every possibility that the PCC Outgoing Feeder 650A MCCB might trip first. And, you are not sure if the probelm was in the MCC or in the feeding cable, unless you make necessary testing & fault finding exercise.

Register to Reply
Commentator

Join Date: Apr 2009
Location: CG
Posts: 64
#12
In reply to #11

Re: Short Circuit Device

08/25/2011 9:26 PM

In this case what is the correct co-ordination according to you?

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#13
In reply to #12

Re: Short Circuit Device

08/25/2011 9:51 PM

With MCCBs, one cannot have time discrimination as MCCBs are Utilisation category 'A' breakers and hence would not have an Icw (Short Time Withstand Current) rating. You can try current discrimination, but for that the upstream breaker instantaneous setting has to be set above the fault level beneath the downstream breaker. The danger is that there is no back-up, in case the downstream breaker does not trip for a fault beneath it.

There are talks of energy discrimination among some switchgear manufacturers, but I have my own set of doubts on the effective functioning of the same.

In a nutshell, with MCCBs in series you cannot have an effective co-ordination. If possible, change the PCC feeder breaker to an ACB and set a time delay in its short time release (of course, after due calculations).

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Short Circuit Device

08/22/2011 9:10 AM

Worst case, you have increased the time it will take to troubleshoot a problem because you will not immediately know which one tripped. Not a big issue, but one that is better to be avoided if possible.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 10
#7

Re: Short Circuit Device

08/25/2011 7:03 AM

In this application it not clear that how you are using these MCCB . In series means MCCB in MAin Panel and second in next panel then you have to set the MCCB for Overload and Shortcircuit protections to achive cascading and discrimination , then MCCB near to fault will clear the fault and trip. If setting are not proper both may trip in case of Shortcircuit

Register to Reply
Register to Reply 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (4); JRaef (1); kvsridhar (2); lalit_nawada (4); PSB (1); PWSlack (1)