Anonymous Poster #1

Cascading Of Incoming & Outgoing Breakers

08/14/2011 2:26 AM

I am designing a MDB with 4000A ACB as the incomer . the415v 3 phase supply is coming from a distribution transformer with a short circuit level of 95KA. so when selecting the ACB i maintained its Icu @100KA. the busbar selected has a withstanding capacity of 100KA for 1second.there are 21 outgoing feeders.

2->1000A ACB , 1->500A MCCB, 1->400A MCCB, 3->250A MCCB, 1->200A MCCB, 10->100A MCCB, 2->50A MCCB & 1->32A MCCB.

now while selecting the Icu for the outgoing MCCB, do i have to maintain 100KA ? or selecting 50KA is ok?

i looked into the cascading of breakers but still couldnt get 100KA for 50A , 32A & 100A MCCB.

can u give me a solution.

thank u

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: cascading of incoming & outgoing breakers

08/14/2011 5:04 AM

This is just personal preference, but for the smaller MCCB's I'd be inclined to split the board with a section for smaller feeders protected by a suitably rated ACB.

I've had to do this when modifying older boards to accept small feeds.

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster #1
#4
In reply to #1

Re: cascading of incoming & outgoing breakers

08/14/2011 6:03 AM

but my client insists on a single 4000A acb and using another ACB just for smaller feeders will increase the cost too and the market is pretty hectic these days ......

Reply
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: cascading of incoming & outgoing breakers

08/14/2011 5:18 AM

The word 'cascading' implies, to me at least, that the incoming circuit breaker is a current-limiter, and all downstream CBs are conventional ones without current limiting. Consequently, the Incomer will NOT have a 1 sec rating ! At 95kA, it should probably clear the fault in 3 to 6 milliseconds. The downstream breakers will not even react in this time. Here is an extract from a paper from Schneider Electric....

Pardon my asking, but don't you mean 'discrimination' and not 'cascading' ? If you are looking at 1 sec ratings, you are.....

There are many good papers on Discrimination (time-based, energy-based etc) and Cascading on the web. Many manufacturers publsh exhaustive data to enable selection of appropriate CBs. There are even custom software to help you in this. Please google using "discrimination cascading"

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Good Answer (Score 2)
Anonymous Poster #1
#3
In reply to #2

Re: cascading of incoming & outgoing breakers

08/14/2011 5:59 AM

ya the discrimination is time based right. i mean if fault occurs at the load side of a 100A breaker thn the 100A breaker must trip before the incomer ACB so tht there s power flowing through other feeders . this is what discrimination means right?

and cascading is like say for a 70 kA fault at the busbars (after the incomer) ,the incomer must trip before the fault affects the outgoing circuits which are of 50KA Icu..am i right?

i have taken schneider electric acb masterpact nw40bH1 as the incomer. and outgoing are nsx N type..........

Reply
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #3

Re: cascading of incoming & outgoing breakers

08/14/2011 7:07 AM

The NSX breaker is a current-limiting type i think, using the double-break-rotary contact system first seen in their Compact NS MCCB (arguably the most copied contact system in the world !!!). Here is an extract from the 44MB catalog of Compact NSX.

Rather difficult to read, but you must be having the catalog already. You get the idea. At >2400A the famous "reflex trip" acts to clear the fault in milliseconds.

The NSX does have a 150kA version as per this catalog.

Why time-based discrimination? Since you are using Schneider CBs. why not 'Sellim' or 'energy based' discrimination which are better? Please download and study Schneider's ECT167 which describes these systems.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Good Answer (Score 2)
Anonymous Poster #1
#8
In reply to #5

Re: cascading of incoming & outgoing breakers

08/15/2011 6:15 AM

yes sir, it is available but it is very very costly and the delivery time is more thn 12 weeks. so i cant use 150KA breakers. thats y i was talking about cascading. and yes total discrimination is provided between masterpact NW (current limiting type) and masterpact nt ,nsx breakers.

so the breaker sc rating posted on my question is that ok or do i have to go to one further level , say 70KA.

i mailed schneider customer care and they told me they ll come back with a solution..its been 2 days and yet no sign from them.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: cascading of incoming & outgoing breakers

08/15/2011 7:35 AM

You don't seem to have studied ECT 167 which describes various systems of coordination.

If you understand and use cascading, you need a current-limiting circuit breaker as the incomer, and cheaper, normal MCCBs in the outgoing feeders. The Masterpact ACB also has a current-limiting version with (i think) 200kA capacity. Once you select this as the incomer, the rest of the downstream MCCB can be of lower capacity ... that is what 'cascading' or 'series rating' is all about.

Remember, proper selection of circuit breakers depends on ensuring that as far as possible, only the faulty section is isolated, and continuity of power is maintained to healthy feeders. Cascading may look like a compromise, but is it ? How likely is a 100kA fault ? Only the SC labs of CPRI and ERDA can deliver such a fault...that too to a solidly bolted short-circuit. So, you need to check whether your conditions are met at all levels - from overloads to high impedance short-circuits to Icu.

Coordination is an interesting but complex subject. i would urge you to read that paper, study the coordination tables available on Schneider website, sit with their engineers and discuss in depth. You will learn a lot.

Isn't it time you registered on CR4 ? Many people (including me ) do not reply to anonymous posters.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster #1
#10
In reply to #9

Re: cascading of incoming & outgoing breakers

08/21/2011 5:06 AM

i have studied ect 167 one time and i must say its pretty complex. but still i know some thing about discrimination. yes i am young man with just 10 months experience in lv design & working under a senior designer . my designer has gone out of country for his vacation and now its all upon me to design. since this s a tendering stage, i want to be little careful ........i had called the client regarding the short circuit rating & he said "hmm, i donot know, current, i ask my engineer and come ". His electric engineer told me that "the supply is from a 11kv/415v 2.5MVA step down transformer with secondary impedance of 6.25% and so from the calculation it is coming around 90-100k, so design accordingly".

i have seen the discrimination tables .if i want to use nw40bH1 there s no total discrimination between incomer n outgoing nw1000A acb. if i use NT acb i will get total discrimination.

but i dont know about the KA rating. NTH2 is 50KA & NTH1 42 KA. NTL1 which is a current limiting breaker is of 130KA.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#11
In reply to #10

Re: cascading of incoming & outgoing breakers

08/21/2011 7:39 AM

The fault level at the outgoing terminals of the transformer may be 100kA, but will it not reduce at the outgoing of each feeder ? Something like this ....

This is on page 101 of this document from Schneider, cascading_2009_EN-2.pdf

You can select downstream MCCBs with lower Icu/Ics after calculating the various fault levels (using ETAP or some such software maybe?)

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Cascading Of Incoming & Outgoing Breakers

08/14/2011 11:44 AM

Here in the US, we call it "Series Ratings" when you want to use a system of protective devices down stream that have a lower interrupt capacity than the main ahead of them and rely upon the current limiting capability of the upstream device to keep the fault current levels below the levels of the lower rated devices. But for us, this can only be done if there has been some very expensive testing and third party approvals performed, you cannot do it in the field. So if you were constructing this as a one-off, you would either have to use a listed series combination, usually all from the same mfr., or be willing to sacrifice a test system at an approved lab. I'm not sure if IEC requires the same thing though, but is appears as though they do not. Still, it might be worth checking to see if a manufacturer has already done this testing for the US market on their components, because that would be an excellent argument that the combination of devices is sound.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: Cascading Of Incoming & Outgoing Breakers

08/14/2011 12:07 PM

Exactly JRaef

i remember a super designer from Westinghouse describing the logic of the "Series Rating"way back in 1984. i remember thinkig then 'What a nice concept! We need this in India, not that awful expensive discrimination system"

Nothing came out of that i regret, since my company was a 96 pound weakling against several 500 pound gorillas....

i will never forget what my illustrious American friend told me two years later.... "You really are a RICH country ! You don't want series rating ! You can afford full discrimination !!! "

Not really. Just too much CYA(cover your a$$)and NMJ (not My job) syndromes

Schneider, ABB, Siemens and many others have full discrimination and cascading ratings for their equipment on their websites...fully tested and certified by independant labs like KEMA and CESI.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Reply to Forum Thread 11 comments