AC Cable for use in DC

08/24/2011 8:45 PM

1.1 KV rated LT cable can be used for how much DC voltage (continuous duty) ? any impirical relation or ref. book you can suggest?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Petroleum Engineering - New Member Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Location: Spring, Texas
Posts: 3403
Good Answers: 150
#1

Re: AC Cable for use in DC

08/24/2011 9:11 PM

1.1KV obviously. the limitation will be the breakdown voltage of the insulation which is pretty much agnostic towards the direction of the current. (the exception being high frequencies where it does matter.).

__________________
Who is John Galt?
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#2

Re: AC Cable for use in DC

08/24/2011 9:28 PM

Contact the cable manufacture.
The DC rating should be higher than the peak AC rating, but it could also be lower in some cases.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: AC Cable for use in DC

08/25/2011 1:31 AM

Though this Wiki extract refers to HVDC, it should be even more valid for 1.1kV ?

HVDC can carry more power per conductor because, for a given power rating, the constant voltage in a DC line is the same as the peak voltage in an AC line. The power delivered in an AC system is defined by the root mean square (RMS) of an AC voltage, but RMS is only about 71% of the peak voltage. The peak voltage of AC determines the actual insulation thickness and conductor spacing. Because DC operates at a constant maximum voltage, this allows existing transmission line corridors with equally sized conductors and insulation to carry more power into an area of high power consumption than AC, which can lower costs

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: AC Cable for use in DC

08/25/2011 2:02 AM

The one time I could see this causing a problem is if you used 1100V + or - to a grounded 0V. The voltage to earth may be too high.

__________________
The reports of my death are greatly exaggerated.