08/27/2011 2:37 AM

Engineers,

One of our client is interested to replace the existing standard induction motor driven centrifugal fans and pumps of their plant. They want to know option 1. VFDs or option 2. Mechanically. Adjusted speed drive, will be beneficial.

They are preferring to go for option 2. As they thank it has benefits and advantages over VFDs few of them are:-

  • Substantial energy savings with all variable torque loads.
  • No power quality issues, Zero harmonics
  • No special filters, reactors, or expensive three phase isolation transformers
  • Does not cause additional motor heating, even at continuous low speed requirements (no speed range limitations)
  • Does not harm motor windings
  • Does not cause electrically induced pitting of the motor bearings
  • Does not require expensive inverter duty motors
  • Controller can be located any reasonable distance from the motor/drive without fear of motor damage.

Your comments will help us out.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Magnetic-Coupled Variable Speed Belt Drive

08/27/2011 3:10 AM

There is too little information here, and too many possible variations, to give one-size-fits-all advice.

VFDs can be interfaced with pressure or flow sensors so as to respond automatically to changing process conditions. I'm not sure how many mechanical devices can do this, though they may be manually adjusted from time to time if the process conditions do not fluctuate continuously.

Mechanical devices may have belts, friction cones or disks, etc.; any of which will be subject to wear, and which also have efficiency losses of a few per cent.

Out of a suite of pumps or fans, one might have variable speed, while the rest are either on or off.

Etc.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Magnetic-Coupled Variable Speed Belt Drive

08/27/2011 5:17 AM

There's only two things to be considered to my mind the efficiency of a VFD as against some mechanical contrivance, I know which I'd put my money on!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Magnetic-Coupled Variable Speed Belt Drive

08/27/2011 12:10 PM

What has any of this to do with "magnetic coupled" drives?

Register to Reply
Guru
Hobbies - Musician - New Member United Kingdom - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Transportation Engineering - New Member

Join Date: Mar 2007
Location: England
Posts: 951
Good Answers: 48
#4
In reply to #3

Re: Magnetic-Coupled Variable Speed Belt Drive

08/27/2011 2:05 PM

It is the thread title that tries to encompass all, but misses the crux of the biscuit. Like na former business associate who suggested that a mag-drive peristaltic pump might be a good idea!

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: Magnetic-Coupled Variable Speed Belt Drive

08/27/2011 2:09 PM

Belt and suspenders?

Register to Reply
Guru
Hobbies - Musician - New Member United Kingdom - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Transportation Engineering - New Member

Join Date: Mar 2007
Location: England
Posts: 951
Good Answers: 48
#6
In reply to #5

Re: Magnetic-Coupled Variable Speed Belt Drive

08/27/2011 4:50 PM

Maybe less elegant!

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Magnetic-Coupled Variable Speed Belt Drive

08/27/2011 11:40 PM

It looks as though someone has been reading the sales literature for a Magnadrive (or another similar brand). For those unfamiliar, they are a magnetically coupled Variable Speed Drive that controls speed by varying the magnetic field force in a slip coupling, essentially allowing more or less of the motor speed to be slipped in the coupling as a way of controlling speed.

What their sales literature always leaves out is their main detractor, they are much less efficient than VFDs. So you can vary the speed without some of the problems that VFDs represent, but also without the main benefit, the additional energy savings. Mag Drives are useful for applications where you will not get the additional energy savings anyway, i.e. constant torque loads, but they are almost pointless on a variable torque (quadratic) load. Most of the truly successful applications are very large high torque applications, such as a disc refiner in the pulp making industry or centrifuges (where energy recovery raking is not used).

They are also more expensive than a VFD, and in many cases you STILL need to use a soft starter for the motor, another cost factor they almost always leave out of the sales literature.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#8

Re: Magnetic-Coupled Variable Speed Belt Drive

08/28/2011 12:12 AM

While I have no dogs in this race (meaning I do not presently work in it), I much rather understand and work on a supposed bearing spalling issue in software. Sorry, it is quicker, better, more enduring solution, than mechanical hardware. Yes, it is requiring hardware solutions, sometimes, but not now.

Register to Reply Score 2 for Off Topic
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#9

Re: Magnetic-Coupled Variable Speed Belt Drive

08/28/2011 4:23 AM

Substantial energy savings with all variable torque loads.

Maybe.. but you need to say if its a mag coupling or belt drive

No power quality issues, Zero harmonics

Slightly wrong.. every induction motor generate Harmonics... and if you are using lots of them you have harmonics in your system. However by NOT using a VSD, you are not increasing your harmonic levels

No special filters, reactors, or expensive three phase isolation transformers

If you motors are 3phase 415v, the you can obtain a drive for that motor and there is no need for the step up and step down transformers. They are not isolation transformers, if your supply is not 480v or 415v then you ned to step down and if your motor NP voltage is above 480, then you need to step up the drive output, which possibly be 480v

Does not cause additional motor heating, even at continuous low speed requirements (no speed range limitations)

That would be because of the harmonics but you can get drives with THD of less than 5%, therefore no need for those expensive filters and reactors

Does not harm motor windings

Just starting the motor..DOL... stresses the windings each and every time.. the additional heat from harmonics can harm motor windings but with drives THD <5% not a problem and you have the ramp up time, another bonus feature of a drive

Does not cause electrically induced pitting of the motor bearings

New one on me.. but always wiling to learn.. could you explain please.

Does not require expensive inverter duty motors

Not really an issue, as most motors will run on a drive, however you can obtain low cost high efficiency NEMA motor these days

Controller can be located any reasonable distance from the motor/drive without fear of motor damage.

If using a drive the HMI(controller) can be located anywhere. As for the drive, I use drives located 1Km from the motor

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 2)
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#13
In reply to #9

Re: Magnetic-Coupled Variable Speed Belt Drive

08/29/2011 6:13 AM

He Said:...Does not cause electrically induced pitting of the motor bearings

You said:...New one on me.. but always wiling to learn.. could you explain please.

I think the OP is refering to STEEL bearings, that MIGHT be affected by induction! I've never seen it or heard of it, thats not saying it couldn't.. anyone??

Register to Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#10

Re: Magnetic-Coupled Variable Speed Belt Drive

08/28/2011 7:00 AM

Earlier we could buy Variable Speed Pulley drive which consisted of Pulley which could be expanded as its construction was split type and spring loaded. Motor with pulley was mounted on slide to control speed.

You can also try High Torque Magnetic Motor which can give variable speed but is quite expensive.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#11

Re: Magnetic-Coupled Variable Speed Belt Drive

08/28/2011 7:21 AM

Yes, for decades machine tools were built with mechanical variable speed drives. The principle is simple, and they work reliably. You have two cones on the input, two cones on the output. A chain or belt connects them. When the input is moved apart, the output is moved together. Simple, effective, well working. If one cone works in a 1:5 range, the transmission is 1:25. Neat.

There was even a car with this drive, the Daffodil from Netherland. A neat simple car. Today, with modern belt materials it wold be a viable proposition, IMHO.

Register to Reply
Active Contributor

Join Date: Mar 2009
Location: Abu Dhabi - UAE
Posts: 20
#12

Re: Magnetic-Coupled Variable Speed Belt Drive

08/28/2011 3:58 PM

The reply you have got from Brich is very good one, just I would like to add the following:-

-Magnetic Coupling drives usually have heating problems, as it depends on the Eddy current phenomena, and the larger the coupling the more heat will be generated.

- Magnetic coupling drives are point to point assignment, which means you can't utilize one motor's coupling with other motor, while in VFDs you can use assignment switch to connect one VFD to different motors this will increase the reliability of your system.

- You can use one VFD to run 2 motors that are sharing a load, like Mud Pumps in drilling rigs, and can easily control the load sharing between them, the thing that you can't do it by using the Magnetic coupling drives.

- VFDs give smoother torque and speed control than Mag Drives, as in VFDs the speed feedback always tracking the speed reference at any time.

- By using HMI the troubleshooting of VFDs is very easy.

- THD can be reduced by using only suitable line reactors at the input of the converters , and L-C filters at the DC bus of the VFDs, and no need to use expensive Harmonics filters for that.

I recommend VFDs

Regards

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#15
In reply to #12

Re: Magnetic-Coupled Variable Speed Belt Drive

08/29/2011 7:41 PM

Thanks to all my technical experts.I have passed on the Forum suggestions and guidence to the concerned plant technical manager.

Register to Reply
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#14

Re: Magnetic-Coupled Variable Speed Belt Drive

08/29/2011 9:16 AM

follow this to a previous topic ref VSD's

http://cr4.globalspec.com/thread/70575#comment754304

and look for answer 3

Register to Reply
Participant

Join Date: Dec 2006
Location: Illinois USA
Posts: 2
#16

Re: Magnetic-Coupled Variable Speed Belt Drive

09/01/2011 1:01 PM

If you are in the United States, another advantage to the VFD's is you also may be eligible to receive additional funding via the utility companies grant program (http://www.dsireusa.org/).

__________________
Joliet Technologies - Variable Speed Drives and Controls
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#17
In reply to #16

Re: Magnetic-Coupled Variable Speed Belt Drive

09/02/2011 4:11 AM

We are stationed in Pakistan,but thanks for the reply.

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#18

Re: Magnetic-Coupled Variable Speed Belt Drive

09/02/2011 11:41 AM

In the early days of the VFD technology the listed concerns were valid. The fix to avoid the transient currents problem is now easy and inexpensive. The power savings of VFDs that are correctly applied are very attractive and the payback is quick.

Lou Bindner

Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

brich (1); Holzfeller (2); joliettech (1); JRaef (1); leveles (2); Lou Bindner (1); lyn (2); M-salem (1); salahuddin zia (2); suresh sharma (1); thccontrols (2); TonyS (1); Tornado (1)

Previous in Forum: Phase Conversion   Next in Forum: Neutral Bushing Rating Of 220/33Kv Transformer

Advertisement