Earthing Conductor Sizing

09/02/2011 11:10 AM

Dear All,

I have done electrical design for a 7 apartment block. A 400A panel boad fitted with 250/400A adjustable MCCB incomer, TT earthing system. The main suppy cable is 4*185mmsq pvc/swa/pvc.
No earthbar, so the protective cable, in this case earhing cable, by the IEE reg. should be 95mmsq to the earthrod.


Is this too big or ok, as one would argue it doesn't matter much since it is path of least resistance and that the fault current would be conducted to ground in some microsecs.

Also, the same specs as above runs for the genset standby supply.
Is it imperative to bond their earths together?

I look forward to your responses soon.

regards,
kebian

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Earhing Conductor Sizing

09/02/2011 11:17 AM

Follow British Standard 7671 to the letter.

The bond between the supply earth and the building earth, in a TT system, is the Earth itself.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2

Re: Earhing Conductor Sizing

09/02/2011 11:44 PM

TT system supply do not have earth wire or cpc,the consumer should provide an earth. Is there a transformer provided by the utility for this installation?. If you calculate or obtain from the utility the value of SC/Fault current you can select the size of Earth rod/plate/cable taking into account the tripping time of the breaker. NEC has provided a table for sizing CPC depending(proportional) on the size/rating of the main CB.

__________________
pnaban
Register to Reply
Associate

Join Date: May 2011
Posts: 28
#3
In reply to #2

Re: Earhing Conductor Sizing

09/08/2011 5:07 AM

Pnaban,

Thanks. Please can u help me with the NEC table for sizing cpc wrt size/rating of the main CB.

Regards,

Kebian