Selection of Motor Starter

09/02/2011 11:33 AM

am seen the plant and they are using for all motors from lower to higher HP level only DOL starter. But i studied higher capacity motors start through only Star delta starter.. i dont know why? can explain any one???

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: Mar 2011
Posts: 48
#1

Re: selection of motor starter

09/02/2011 12:34 PM

this is depends on their requirment.if they need higher staring torque,and the direct starting is not making any voltage dip in the system its no problem.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: selection of motor starter

09/03/2011 2:50 AM

Various types of reduced voltage motor starters (part winding, star-delta, stepped resistance, autotransformer, solid state) can reduce the motor starting current. This minimizes voltage dip in the network.

A robust network can support DOL starting of large motors, but smaller networks might not be able to do this; in which case they may require reduced voltage starting for motors above a specified size.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: selection of motor starter

09/04/2011 5:44 AM

The stipulation of limiting the power rating of motors that ca be started DOL applies only to those customers who draw power from LT Lines. This is because, if an LV customer starts his high capacity motor DOL, the line voltage drop caused in the main LV lines would affect the neighbouring LV customer connected to the same LV mains. And, this could be a flip-flop action. So, to avoid this social problem, regulatory authorities have imposed that DOL starting be limited to motors of capacity upto, say, 7.5HP or 10HP.

But, if a customer is drawing power from a HT mains, he would have a transformer and as such any voltage drop created by starting any of his high capacity motors would not affect his neighbouring HT customer. May be, in his own plant some smaller motors may get affected, but, then that is his "own" problem and NOT a social problem. So, for a HT customer, there are no stipulations as to the size of the motor that can be started DOL. The decision is made based on starting torque requirements, which is good with DOL and, of course, economic considerations.

Register to Reply
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#4

Re: selection of motor starter

09/04/2011 7:43 AM

Star delta starter are for motors that require high Starting torque to more a stationary machine, then once running the requirement for the high torque, high current is reduced, mainly because some machines have the (inbuilt) kinetic energy to overcome that little bit of extra load, for example, car crushers/shredders, conveyor belts.[/p]

Am I right in assuming that you have just got this job straight out of school?

don't try to apply all you've been taught in one afternoon... apply logic and study the principals not the absolute theory.

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Selection of Motor Starter

01/10/2023 7:02 AM

Ask the <...they...>.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard